4lorn- electrical ?

brownbagg | Posted in Construction Techniques on July 1, 2005 05:50am

running 100 amp service to shop through 2 inch pvc conduit. I have the correct size wire, just cant think of it. 4 copper wires. 120 feet (2) 90’s. i got a 150 foot snake and will pull rope with it. The question is.
How much of the lubicate soap do I need to pour in the pipe. I,m ready to use a five gallon bucket full.

(3) 4 awg and (1) 6 awg

Reply

Replies

  1. junkhound | Jul 01, 2005 06:56am | #1

    4 little wires in 2" and only 2 bends doesn't sound like any lube is needed, esp if DW pushes the wire from the feed end.

    1. 4Lorn1 | Jul 02, 2005 03:54am | #5

      Re: "4 little wires in 2" and only 2 bends doesn't sound like any lube is needed"...Been down that road too many times. About the time I figure a pull will be dead easy the Murphoid nature of plastics, cables and conduits raises its ugly head. Once saw a 40' straight run defy a crew for over an hour. You could look down the conduit and see the other end. And yet the conductors refused to go in. They figured it would go in so easily they could just push it in dry. It bound up at around 20'. So they ran a fish tape and made up a quick and dirty head. This too bound up and refused to move. They pulled the hook out of the tape. The conduit was wet and they assumed that it would slide right in.About this time my crew got involved and we reran the tape and pulled in a rope. To this we made up a real head and broke out the lube. Even then it didn't go in easily. Had two helpers and a journeyman grunting like they were giving birth pulling it in. We never did find out why it was so hard. Joke was that the head was afraid of the light. Once it got into a warm, dark spot it wanted to stay. We debated rerunning the conduit but the cables were, and remain to this day, almost twenty years later, from what I hear, electrically sound. The lesson being that: Shy of someone holding a loaded gun to my head I will never go to a site without some sort of pulling lube. I seldom stuff anything bigger than a #12 down a 2' section of 4" without lube. Every pull has to be assumed to be a difficult one. Use any reasonable methods that will make it easier. If it slides in like it wanted to to be there then no big deal. Your out a few bucks for lube. The larger and longer the pull the more I try to overestimate the difficulty. Having a pull jam often means backing the pull out. And that can easily multiply the time involved and can damage the insulation. Once saw three pulling crews, each of which would normally do two or so major pulls a day, spend a day backing a pull out, inspecting the cable an inch at a time, and pulling it back in. While we were busy inspecting the cables a labor crew did yeoman labor digging out the broken conduit connection and fixing it.I will add that on any pull a pair or two of those latex smeared gloves and a couple of old towels makes things easier. The former help to grip the slick cables and the later in clean-up and getting the lube off the hands and tools. On the up side Yellow 77 does keep the hands soft and smooth.

      1. junkhound | Jul 02, 2005 06:26am | #8

        Good points, I defer to your extensive commercial experience.

        FWIW:  The hardest pull I was ever involved with was in 1970, pulling a 100% full** 4" 2024 T3 aluminum conduit 110 ft long with one about 90 degree and 2ea approx 45 degree bends. Obviously, this was NOT NEC, it was on the SST prototype airplane for test flight  (cancelled in 1971). All of the wiring was teflon sleave shielded pairs for instrumentation, minimum size was critical as there were penetrations thru wing spars, etc.  Used a 3 ft long, thin nylon chinese finger for a pull attachment, totally saturated cables and conduit with commercial lube, 10,000 pound winch to pull and ten guys on the push end.  NO GO!  Finally sprayed the inside of the conduit with PAM vegatable spray for cooking and got it pulled thru. Probably 20 people involved for most of a full day, at aerospace labor rates, could have wired ten houses for the same $$$.

        Everybody knows I'm cheap (but dont rat to the local code authorities about this), but once pulled 3 ea 8 MTW wires  and a 10 AWG THHN plus a TSP 16 AWG thru 130 ft of abandoned underground 1" polyethelene water pipe for a 'bootleg' conduit run with no problem, no lube.

        ** 100% full means here that you could not even fit a 1/4" dia rod into the conduit with the wire inplace

        1. User avater
          BillHartmann | Jul 02, 2005 07:08am | #11

          "Everybody knows I'm cheap (but dont rat to the local code authorities about this), but once pulled 3 ea 8 MTW wires and a 10 AWG THHN plus a TSP 16 AWG thru 130 ft of abandoned underground 1" polyethelene water pipe for a 'bootleg' conduit run with no problem, no lube."That is now "legal".There is a new type of conduit, HDPE.I suspect that it is fairly close to PE water line.

          1. 4Lorn1 | Jul 02, 2005 12:33pm | #12

            Actually my rough guess is that other than your choice of conduit your installation would be alright.As I remember it 3 - #8 THHNs are OK in 1/2" trade size conduit. Less than 40% fill.

  2. 4Lorn1 | Jul 01, 2005 09:10am | #2

    I would figure two quarts. A gallon at most. I would use Yellow 77 as it is easier to handle and clean up.

    This, in the scale of things, is a short pull. 'Soap' a bit a a time and pull it in. Try to develop a rhythm. Try to get the lube spread fairly evenly. A thinner even coat does more than large gobs with sections left dry.

  3. BarryO | Jul 01, 2005 09:56am | #3

    FYI, 4 AWG with 90 degree C insulation is rated for 95 amps, and that's before any ambient temperature correction factors.

    120 foot run => 240 feet of wire => 7.4 volts drop @ 100 amp, or 3% of 240V, for this feeder.

    I'd bump the conductor size up, if it were me, especially if you're supplying single phase motors with big startup currents.

    And yes, I'd think this would be an easy pull.  If you want to use lube, just have the person at the feeding end lather some on the wires as they're going in.

    1. brownbagg | Jul 02, 2005 03:04am | #4

      Its a 100 amp subpanel to the shop but never will ever come close to running 100 amp at once. maybe 60 amp at best.

    2. RyanBrant | Jul 02, 2005 04:26am | #6

      This type of pull is in my future, so out of curiousity, how does 120' become 240'?  If it were only an outlet 120' away, the run would be just that, right?  And for a 240V sub-panel, each hot carries 120 volts over 120', so hence my confusion.

      1. BarryO | Jul 03, 2005 08:31pm | #19

        This type of pull is in my future, so out of curiousity, how does 120' become 240'?  If it were only an outlet 120' away, the run would be just that, right?  And for a 240V sub-panel, each hot carries 120 volts over 120', so hence my confusion.

        It becomes 240' when figuring voltage drop because, for 240V, each hot conductor is carrying current, therefore there is voltage drop across each of them.  The percentage drop is then:

        [(current in amps)*(2*120 ft.)*(resistance per foot)/(240V)] * 100

        120V circuits will see the same percentage drop; if you assume balanced current in the neutral there will be no voltage drop through it, but the denominator is now 120V instead of 240V.   Conceivably it could be worse if the load were so imbalanced that the other pole had little current draw while the pole in question was drawing close to 100, but that shouldn't happen with the big loads on 240V and proper panel layout.

  4. piko | Jul 02, 2005 05:12am | #7

    My sparky yelled at me as I was abt to glue up. He chose to run the wire thru separate  lengths of conduit BEFORE he glued them together. Made sense to me.

    cheers

    ***I'm a contractor - but I'm trying to go straight!***

    1. pm22 | Jul 02, 2005 06:30am | #9

      This is not kosher. "He chose to run the wire thru separate  lengths of conduit BEFORE he glued them together." There is an entire sentence in the Code which says the wires must be pulled into a complete conduit system.

      As for the pullong and lube, perhaps you could lube the conduit before pulling the wires in. This will coat your pull rope making it slippery to pull on. An alternative is polywater if you want to get technical.

      Perhaps Mr. Lorn's proplem could have been solved had he tried feeding from the other end. Perhaps one of the conduits [assuming PVC] was not fully inserted into its socket.

      The head should be minimum diameter -- no wider than the total diameter of the entire bunch of cables.

      ~Peter

      1. piko | Jul 02, 2005 04:49pm | #16

        As I posted to 4lorn1, this was the only time I saw that happen. I don't know why that particular sparky chose to do it. A responsible reply - thankyoucheers

        ***I'm a contractor - but I'm trying to go straight!***

        1. brownbagg | Jul 03, 2005 05:05am | #17

          O.K. got the wire pulled, no problem. had to do it by myself. you know how friends are on the weekend, especally if the beach is close by. Had to keep walking to the beginning to give it some slack so I could pull. you be amaze how much 150 of wire laying on the ground weighs. I use about a gallon of lubicate, talk about a mess. I got another gallon left over, wonder what type of practical joke I could use it for.

          1. 4Lorn1 | Jul 03, 2005 07:37am | #18

            If it is Yellow 77 it makes a decent anti-rust agent. Slather it of the steel with a course bristled brush and let the tools lay out in the hot summer sun. On a piece of tar paper or roofing iron is best. As the metal warms the water and solvents evaporate and the wax melts into the grain of the metal. Lay them out late morning and by mid-afternoon they are good to go. Wipe off the remainder with a terry cloth towel.Hydrogel, or was it one of the other gels, is reported, by a manufacturers reps in a supply house, or so the gentleman said, in the gay community. A mystery what they do with it but I understand that they pay something like $20 a quart for a tub of it.Some of the lubricants make for great oil parties and adult 'slip-n-slide's. Run plastic down a slope and smear on the lube. Mist lightly to make it extra slick. Great fun. When the slide runs down to the lake, the BBQ is cooking, a bonfire is going, the beer is flowing and the music is good. Once rigged a slide into the surf seaside. A fun time was had by all.

    2. 4Lorn1 | Jul 02, 2005 06:54am | #10

      Running the conductors before the conduit is assembled is a poor technique. Usually you see this sort of thing with amateurs who don't know much about, and are afraid of, pulling wire. Or one-man crews that are too cheap to hire the help necessary to pull some runs. Rare to find a situation where it is any easier than doing it correctly.Actually a violation of code. One of the few articles that deals with methods instead of a requirement when finished. Good chance he damages the insulation, a problem that may take years to show up, and/or glues the wires into the conduit, making removal or replacement a PITA. When done in a ditch it often means that the conduit has a lot of dirt in it. dirt, crud, and especially stones, can make pulling wires, in or out, a real joy.Any luck at all and he will end up doing both. Which could require a replacement of the conduit run when a problem shows up. Possibly better if he had run direct burial.

      1. piko | Jul 02, 2005 04:46pm | #15

        An informative reply - thankyou. This was the only occasion I've seen thqt happen, and for what reason I know not.

        By the way - where've you been? HAven't seen you posted much in the last 3 weeks (since I stated posting). Used to be that your nickname cropped up in FHB pages some years ago, and I thought then, as I think now - what a wonderful nickname!!!cheers

        ***I'm a contractor - but I'm trying to go straight!***

  5. paulc1 | Jul 02, 2005 12:54pm | #13

    The way I would do it would be to string the wire through the sections of pipe then glue them together as you go (put through pipe then through elbow then glue those pieces together) makes it easier, that wire doesn't bend very easy

    1. brownbagg | Jul 02, 2005 03:35pm | #14

      problem is: they was buried a couple years ago when I trench for the house. they are at least three foot down and part of it has concrete slab poured over.

    2. BarryO | Jul 03, 2005 08:47pm | #20

       

      The way I would do it would be to string the wire through the sections of pipe then glue them together as you go (put through pipe then through elbow then glue those pieces together) makes it easier, that wire doesn't bend very easy

      yes, it sounds easy.  In reality, this is extremely slow, and a real PITA.  After gluing on each section, you'd have to wait for the glue to dry before pulling the string past the joint.  If you don't wait, and do this too hastily, you get some cement from the inevitable little bit of squeeze-out on the string.  the string ends up getting welded to the inside of the conduit.  Now the pull gets harder rather than easier, because you have this length of string attached to the inside of the conduit interfering with the pull.

      Sucking a string through a conduit run after it's completed is easy, so there's no reason to try to install it during glue-up.

    3. 4Lorn1 | Jul 04, 2005 03:51am | #21

      You would be surprised how fast you can blow or suck a rat or parachute through even a long run of conduit. Long time ago we had to pull in strings for future needs in existing runs. They were around 400' foot runs. We used a vacuum. The rat, a foam rubber plug, came through so fast that at first we thought that someone had left one in the conduit near the end. Or at least that ours had come off the line. Even at around 400' it took only seconds to get there.Also don't worry too much about the stiffness of the wire. Electrical fittings have a radius that smoothly handles the bending process as long as a bit of lube is used. Of course all bets are off if you are silly enough to use plumbing fittings or make non-standard bends in the conduit.A standard 'shop vac' will pull the line in easily. Remember that most vacuums will also blow. Something to remember when dealing with water filled underground conduits. Which is to say most conduits if they have been underground for long and there is rain or groundwater present.Lacking power at a site a gasoline leaf blower make a handy, if a bit loud, tool for the same job. Just be sure to screen the entrance because your average blower, rigged as a vacuum, will such up the parachute and about a thousand feet of line faster than the average human can react and sucking a hundred gallons of water, which keeps coming for a few seconds after you stop pulling, doesn't do them a bit of good.Water filled conduits are great for initiating your young and gullible apprentices. Stuff them into a manhole and tell them to look down the conduit to spot the rat. Have the man on the other end use the vacuum to blow into the conduit. A conduit full of water, water that has lain stagnant for a few months so it is both florid and fragrant makes for an unholy, and memorable, baptism. Welcome to the electrical trade.Best be prepared to sooth, comfort and possible break up a fight. Having towels, a change of cloths and libations ready helps. As does a sense of humor. Unless your attempting to precipitate a confrontation avoid this sort of thing first thing in the morning, in cold weather, and with help that lacks humor. Ten minutes before quitting time with a bar nearby it goes over more smoothly.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Tool Test: You Need a Drywall Sander

We tried out a range of rotary and random-orbit sanders to compare their dust collection, quality of finish, and user fatigue after hours of sanding.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Sharp-Blade Solution
  • Podcast Episode 684: Masonry Heaters, Whole-House Ventilation, and Porch Flooring
  • FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity
  • Tools and Gear for the Moms Who Get it Done

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in