ANTENNA GROUNDING

wallyo | Posted in Energy, Heating & Insulation on January 5, 2009 07:44am

In order to receive HDTV I needed to move my antenna from attic to exterior roof mount. I am not too worried right now because there are several trees about 30′ away that are taller then the antenna, and if there was a close lightening strike the trees are probably the easier path. Also most lightening happens in summer so I have some time to prep. But what is the correct way according to code to ground the antenna. Do you tie into the electrical grounding system, Locally hardly anyone sells exterior antennas worth any salt (at first I thought I needed a larger antenna, could not find one any where local) let alone things like lightening traps.

Any help or current diagrams would be of great help.

Wallyo

Reply

Replies

  1. DanH | Jan 05, 2009 08:01pm | #1

    First and foremost the antenna mast must be grounded. I'm not sure what the code details are, but electrically the shortest path to a good solid ground rod is to be desired.

    Beyond that, the coax should run through a ground block near where it enters the structure. And to protect your equipment it's best to then run the coax through a surge protector.

    The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel
  2. User avater
    BillHartmann | Jan 05, 2009 08:06pm | #2

    "810.20 Antenna Discharge Units — Receiving Stations
    (A) Where Required Each conductor of a lead-in from an outdoor antenna shall be
    provided with a listed antenna discharge unit.
    Exception: Where the lead-in conductors are enclosed in a continuous metallic shield
    that either is permanently and effectively grounded or is protected by an antenna
    discharge unit.
    (B) Location Antenna discharge units shall be located outside the building or inside the
    building between the point of entrance of the lead-in and the radio set or transformers and
    as near as practicable to the entrance of the conductors to the building. The antenna
    discharge unit shall not be located near combustible material or in a hazardous
    (classified) location as defined in Article 500.
    An antenna discharge unit (lightning arrester) is not required if the lead-in conductors
    are enclosed in a continuous metal shield, such as rigid or intermediate metal conduit,
    electrical metallic tubing, or any metal raceway or metal-shielded cable that is
    effectively grounded. A lightning discharge will take the path of lower impedance and
    jump from the lead-in conductors to the metal raceway or shield rather than take the
    path through the antenna coil of the receiver.
    (C) Grounding The antenna discharge unit shall be grounded in accordance with 810.21.
    810.21 Grounding Conductors — Receiving Stations
    Grounding conductors shall comply with 810.21(A) through 810.21(K).
    (A) Material The grounding conductor shall be of copper, aluminum, copper-clad steel,
    bronze, or similar corrosion-resistant material. Aluminum or copper-clad aluminum
    grounding conductors shall not be used where in direct contact with masonry or the earth
    or where subject to corrosive conditions. Where used outside, aluminum or copper-clad
    aluminum shall not be installed within 450 mm (18 in.) of the earth.
    (B) Insulation Insulation on grounding conductors shall not be required.
    (C) Supports The grounding conductors shall be securely fastened in place and shall be
    permitted to be directly attached to the surface wired over without the use of insulating
    supports.
    Exception: Where proper support cannot be provided, the size of the grounding
    conductors shall be increased proportionately.
    (D) Mechanical Protection The grounding conductor shall be protected where exposed
    to physical damage, or the size of the grounding conductors shall be increased
    proportionately to compensate for the lack of protection. Where the grounding conductor
    is run in a metal raceway, both ends of the raceway shall be bonded to the grounding
    conductor or to the same terminal or electrode to which the grounding conductor is
    connected.
    If metal enclosures such as steel conduit are used to enclose the grounding conductor,
    bonding must be provided at both ends to ensure an adequate low-impedance current
    path.
    (E) Run in Straight Line The grounding conductor for an antenna mast or antenna
    discharge unit shall be run in as straight a line as practicable from the mast or discharge
    unit to the grounding electrode.
    (F) Electrode The grounding conductor shall be connected as follows:
    See the commentary following 250.52(A)(1).
    (1) To the nearest accessible location on the following:
    a. The building or structure grounding electrode system as covered in 250.50
    b. The grounded interior metal water piping systems, within 1.52 m (5 ft) from
    its point of entrance to the building, as covered in 250.52
    c. The power service accessible means external to the building, as covered in
    250.94
    d. The metallic power service raceway
    e. The service equipment enclosure, or
    f. The grounding electrode conductor or the grounding electrode conductor
    metal enclosures; or
    (2) If the building or structure served has no grounding means, as described in
    810.21(F)(1), to any one of the individual electrodes described in 250.52; or
    (3) If the building or structure served has no grounding means, as described in
    810.21(F)(1) or (F)(2), to an effectively grounded metal structure or to any of the
    individual electrodes described in 250.52
    (G) Inside or Outside Building The grounding conductor shall be permitted to be run
    either inside or outside the building.
    (H) Size The grounding conductor shall not be smaller than 10 AWG copper, 8 AWG
    aluminum, or 17 AWG copper-clad steel or bronze.
    (I) Common Ground A single grounding conductor shall be permitted for both
    protective and operating purposes.
    (J) Bonding of Electrodes A bonding jumper not smaller than 6 AWG copper or
    equivalent shall be connected between the radio and television equipment grounding
    electrode and the power grounding electrode system at the building or structure served
    where separate electrodes are used.
    The requirements for grounding are in accordance with Article 250. Antenna masts
    must be grounded to the same grounding electrode used for the building's electrical
    system, to ensure that all exposed, non–current-carrying metal parts are at the same
    potential. In many cases, masts are connected incorrectly to conveniently located vent
    pipes, metal gutters, or downspouts. Such a connection could create potential
    differences between lead-in conductors and various metal parts located in or on
    buildings, resulting in possible shock and fire hazards. An underground gas piping
    system is not permitted to be used as a grounding electrode.
    Section 810.21(J) clarifies that the bonding requirement applies only to electrodes at
    the same building or structure. The use of separate radio/television grounding
    electrodes is not required.
    (K) Electrode Connection Connections to grounding electrodes shall comply with
    250.70.
    This section is new in the 2005 Code. This requirement is similar to the requirements
    for grounding electrode conductors in Articles 800, 820, and 830."

    Bascially #10 copper and connect it to the grounding electrode system.

    If you have not see it this website gives you info on size and aimming f the antenna.

    http://antennaweb.org/aw/welcome.aspx

    .
    William the Geezer, the sequel to Billy the Kid - Shoe
    1. wallyo | Jan 05, 2009 08:43pm | #3

      Bill if I am reading correctly #10 bare copper ran in the straightest path to the house's electrical system's grounding rod and clamped to it and a clamp at the antenna mast.This can be ran inside the attic space and down the garage wall?Do I need also to attach a grounding block to the coax, or is grounding the mast enough, and if I use a grounding block on the coax does that get tied to the antenna mast ground or is a second ground wire needed?Yes I used antenna web good site, that is where I thought I needed a larger antenna. Turns out when I moved the antenna from attic to roof I never rescanned for the stations so when told I was not receiving 7.1 by the receiver, I thought the antenna system was at fault. The problem was without rescanning the TV did not know what band width 7.1 was at. (as well as a bunch of other stations).May still go with a larger antenna because I am barely in the green according to the built in meter. Tried two in line amps they made little difference.Thanks Wally o

      1. DanH | Jan 05, 2009 08:52pm | #4

        If you don't have an antenna preamp you should get one. Beyond that, other amps should only be needed if you split the signal several ways.On most digital decoders there are ways to add new stations without rescanning everything.
        The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel

        1. wallyo | Jan 05, 2009 09:02pm | #5

          Over the weekend I brought 2; a Radio Shack 10 db and a Philps 18 db they boost the signal a bit but not a whole lot. But here is the question where is the best placement for one.? Closest to the antenna or equipment? Instructions on either don't say.Wallyo

          1. DanH | Jan 05, 2009 09:02pm | #7

            Like I said, a "preamp" -- an amplifier that goes right on the antenna.
            The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel

          2. wallyo | Jan 05, 2009 09:09pm | #9

            Got it now thanks for clearing that up.Wallyo

      2. User avater
        BillHartmann | Jan 05, 2009 09:02pm | #6

        "in the straightest path to the house's electrical system's grounding rod and clamped to it and a clamp at the antenna mast."Yes or other point on the grounding electrode system such as the service entrance or grounding connection to the water supply.The grounding block (arrestor) can be connected to the same ground as the antenna mask or a separate wire run to the same ground electrode system.It is best place either immediately before or after the cable enters the building..
        William the Geezer, the sequel to Billy the Kid - Shoe

        1. wallyo | Jan 05, 2009 09:06pm | #8

          Thanks again Bill as always you are a breath of fresh air! Now to find a good deal on 40' of bare #10.Wallyo

        2. DanH | Jan 05, 2009 09:13pm | #10

          It should be noted that the grounding block isn't technically an "arrester", since it contains no spark gap or MOV to shunt the center conductor to ground in the event of a surge. There are true stand-alone coax arresters, but they're fairly scarce, so it's advisable to route the cable from the grounding block into a surge-suppressor plugstrip which includes a coax suppressor (after first going through the preamp power supply, if there is one).Antenna => Preamp => Downlead => Grounding block => Preamp power supply => Surge suppressor => Splitter or splitter/amp => TV
          The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel

      3. gfretwell | Jan 05, 2009 09:58pm | #11

        I would drive a rod directly under the antenna mast and bond to that, keeping the grounding conductor as straight and short as possible. Then you bond that electrode back to the service electrode system to reduce ground shift.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Fine Homebuilding – July 2023, Issue #316

Find online articles on timber-framed solar canopies; the right footings; the best toilets; choosing insulation; compact cordless routers; and much more.

Featured Video

Video: Build a Fireplace, Brick by Brick

Get an overview of the process of creating a traditional-style fireplace that burns well and meets current building codes from experienced mason Mike Mehaffey.

Related Stories

  • Podcast 569: Bath Fan Installs, Sunroom Trim, and Basement Control Layers
  • Podcast 569: Members-only Aftershow — Rob Yagid’s Addition
  • Fine Homebuilding – July 2023, Issue #316
  • Fine Homebuilding Issue #316 Online Highlights

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • 2022 Fine Homebuilding Archive
    Buy Now
  • Pretty Good House
    Buy Now
  • 2023 Tool Guide
    Buy Now
  • Code Check Building 4th Edition
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 316 - July
    • Timber-Framed Solar Canopies
    • Build a Transom Above a Stock Door
    • Understanding Toilet Design and Efficiency
  • Issue 315 - June 2023
    • How to Craft a Copper Roof
    • 5 Lessons from Building in a Cold Climate
    • The Advantages of Cellular PVC Siding
  • Issue 314 - April/May 2023
    • 7 Options for Countertops
    • Tool Test: Wood-Boring Bits
    • Critical Details for Ductless Heat Pumps
  • Issue 313 - Feb/March 2023
    • Practical System for a Seismic Retrofit
    • Fine Homebuilding Issue #313 Online Highlights
    • Practical System for a Seismic Retrofit
  • Issue 312 - Dec 2022/Jan 2023
    • Tool Test: Cordless Tablesaws
    • Gray-Water System for a Sustainable Home
    • Insulate a Cape Roof to Avoid Ice Dams

Fine Homebuilding

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in