Four winters ago, we had a direct vent furnace installed. The only thing left on the chimney is the water heater. At that time I had the installer check the existing chimney liner to be sure it was in good shape. The vent pipe for the old furnace was capped off. I just noticed tonight that the capped off furnace vent is dripping water when the WH is running. I think it has been dripping for most of this winter because there is a lot of paint peeled off the wall underneath it. What’s going on here? I know that a WH by itself will cause some condensation, but I don’t understand why is it so much now that it’s running out the bottom of the chimney? And what I should do about it? Thanks.
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story

Learn more about the pros and cons of single-room ERVs.
Highlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
When the chimney was shared with a furnace, it stayed warmeer so much of the moisture by-product of the water heater combustion remaned in vapourous state and left the stack .
Now you have very little heat going up the chimney so the mass of masonry stays cold. That means that most of the moisture in the exhaust is now condensing on the walls of the flue and driping/running back down and in. Lining it with a class b flue of the right size - probably 4" will help it exhaust to the exterior faster before it condenses.
There is another feature you now employ in this setup which can be unhealthy. Since the flue is so large re the size required and the gasses cool down so fast, they sit there drigitn around, and there is an increased chance that they can leak back into th ehouse. That is not a good place to have carbon monoxide. I would suggest a tester
Welcome to the
Taunton University of Knowledge FHB Campus at Breaktime.
where ...
Excellence is its own reward!
Thanks, I do have a CO2 detector in the kids' bedrooms and in the furnace room where the WH and chimney are located. Guess I'll have to look into getting the liner replaced. Last time I did that on another house it was $500. Might be money well spent to just change out the 4 year old WH for a direct vent.
A water heater by itself in a large chimney flue is a BAAAAD idea. Take it from me, the rear chimney in our home was waterlogged to 90+% due to being abandoned to nothing more than a gas water heater. The basement brick chimney foundation had holes large enough to stick a fist through and the stuff was spalling everywhere. That chimney came down rather easily.
Between the oversized flue (reducing the air speed) and the large surface area, that masonary chimney of yours is never going to come to temperature unless you draw hot water 24/7 slowly but continuously. And if you're heating with natural gas, once the surface temperature drops below 140°F, it'll start condensing in there. And remember, the whole chimney has to make it to 140°F, not just the flue gases entering at the bottom. LP and oil have slightly lower condensing temperatures.
As I see it, you have a couple options...