I own a restaurant that has a walk-in refrigerator approx. 6’x9’x7′ high.
The refer is built in the back room. 2 walls are on outside walls and 2 inside walls. The ceiling of the walk-in is built with 2×4’s and butts the ceiling. The walls of the walkin are 1/4″ plywood covered with white fiberglas foodservice grade panels. The ceiling as far as I know has no vapor barrier and in the summer “sweats” real bad and water puddles on the floor. What can I do to stop this? Do I need to remove the panels and put plastic or something else on the walls and ceiling to stop this?? The walkin is 38° and the attic will reach over 100° in the summer.
Thanks Gary
Replies
*
Gray,
Joseph Fusco
View Image
"The price of apathy towards public affairs is to be ruled by evil men." -- Plato
*
The water is leaking into the box through the ceiling and accumulating on the floor.
*
Gary,
Joseph Fusco
View Image
© 1999
"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it."
Aristotle
*Gary, I am reading your posts as "water is coming THROUGH the ceiling in the walk-in" Something in the attic is cold enough to be a condensing surface. You make no mention of any insulation in your discription of the walls or ceiling, but there must be something other than 1/4" plywood and fiberglass panels.Is the ceiling insulation open to view in the attic? What is up there? Sounds like a bacterial breeding ground, with direct access to your food storage. Joe H
*Fred,
Gary,
Joseph Fusco View Image© 1999 "The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it." Aristotle
*Fred,
Joseph Fusco View Image© 1999"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it." Aristotle
*Fred,
Hidden Heat
Melting or Fusion
Heat of Fusion
Vaporization
Condensation a Heating Process
Evaporation a Cooling Process
Joseph Fusco View Image© 1999"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it." Aristotle
*Fred & Gary, I think someone at some time has opened the outer shell of the reefer to repair the refrigeration unit or possibly install new lighting? The moist outside air is now getting inside the formerly sealed shell (think of a thermos, with it's vacuum chamber) and is condensing on the cold surface and running out through openings in the ceiling. How long this has been going on probably will affect the amount of damage done inner structure. How to repair? Find the leak and seal it will probably stop the immediate rain, but there could be a real mess hidden in the ceiling and walls.Gary, what can you see in the attic? Is the top of the cooler hidden, or fairly visible? Anything to be seen in the way of plumbing? Has someone installed a medicine cabinet or anything into one of the walls in the resturant? Installed a sign on one of the outside walls and poked some holes through the wall? What do you think, Fred? Am I on the right trail? Joe H
*Fred,
Joseph FuscoView Image© 1999"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it." Aristotle
*Dear Joe,You're very warm. Consider now what could force huge volumes of warm, humid outdoor air to flow downward from a vented attic to contact the refer shell. And what Gary could do to stop that.Impressed, Fred
*Fred, I see you've given me the clue that I should have thought of myself. Every time the door opens the kitchen exhaust fans suck a new batch of moist attic air into the unintentionally vented shell of the reefer, the now de-humidified previously attic air goes through the ceiling leaks into the box & out the door. Since the attic is vented to the outside, there is an inexhaustible supply of soggy air waiting to be dried by the refrigeration system. What has happened to the electric bill and repairs to the overloaded refrigeration system since this problem started? And what sort of damage to the outer shell caused it? Did some damage occur to an outside wall that was repaired without considering that it had caused a breach in an interior vapor barrier? As to what Gary could do to cure the problem, first choice would be to find the holes in the cooler's outer envelope. I suspect that the interior of the walls & ceiling will probably need some repairs due to water damage, maybe mold growth since this has been going on through at least one summer. In order to contine the "Vent-no-Vent" battle, he could seal the attic vents instead. It certainly would be a round about means to an end, but it might work if he could find every tiny crack. Might also hook a door switch to the vent fan, or open another bigger hole in the kitchen space. Something makes me think you have a better answer, but I don't see it right now. More clues please?Mystery stuff from long distance......Joe H
*
Joseph Fusco View Image "The price of apathy towards public affairs is to be ruled by evil men." -- Plato
*Reality Check.I didn't hear Fred prescribe that for this situation any more than I heard you prescribe wrapping the box in saran wrap and punching some holes in the roof.At least Fred and Joe are trying to figure out WHY there is too much moisture in the box. Maybe you could lend a little insight into that.Most little boys grow up and stop throwing rocks at people.Steve
*
My problem started 2 years ago when the state told me that all walls had to be finished. I put up the fiberglas board that Home Depot sells for $28.50 a sheet.
As the weather got more humid that is when the water problem started.
Here is a cross section on how the box is built.
============== attic space with 4-6" blownin insulation
============== some sort of paper type board 1/2" thick
xxxxxxxxxxxxxx 2x3"s witn reg. fiberglas insulation
-------------- 1/4" a/c plywood
-------------- 2nd layer of 1/4" plywood
After my season was over I pulled the fiberglas from the ceiling thinking the moisture was condensating between the plywood and fiberglas.
Problem started again when the warm weather hit and water started dripping from a seam in the ceiling.
I never had problems before 2 years ago so I am baffled as to why this started.
As far as I can tell there is no vapor barrier around the box.
Gary
*Sorry the ascii graphis didn't post like I wanted them toBut I think you can figure out what I drew.Gary
*
Steve,
Joseph Fusco
View Image
© 1999
"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it."
Aristotle
*Gary,
Joseph FuscoView Image© 1999"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it." Aristotle
*Fred, alternate scenario....Gary's place is a dive. Rats the size of cats have pilfered all the insulation to line their rat condos. They have also gnawed large holes through the walls behind the groceries for easy access to after hours meals. Gary is cooling the entire attic now, and the whole place is draining into the reefer?Nah, that's probably not it either. Is Global Warming a possibility? What makes you think there is something besides the usual kitchen ventilation system that would cause additional negative pressure? Or are you implying that the, Oh! Hot damn! Just flashed on the word "WAS" in your description of the make-up air system. Are you implying that the kitchen has become semi sealed and the ventilators are now pulling air through whatever openings are available? Back to those big rats, must be a big fat one stuck in one of the fresh air vents? That's it, I'm out of ideas again. Joe H
* Fred,
Joseph Fusco View Image "The price of apathy towards public affairs is to be ruled by evil men." -- Plato
*Hey Joe, you can't post to this thread any more, Fred says it's solved and over.Vince
*Get a life Joe.
* Steve,
Joseph Fusco View Image "The price of apathy towards public affairs is to be ruled by evil men." -- Plato
*Fred,
Joseph FuscoView Image© 1999"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it." Aristotle
*Fred,
Joseph FuscoView Image© 1999"The first step towards vice is to shroud innocent actions in mystery, and whoever likes to conceal something sooner or later has reason to conceal it." Aristotle
*I like my life a lot, Joe. I hope you like yours too. But for someone who has it so good, you carry around an awful lot of anger. I feel sorry for you.Maybe you'll get right in your next incarnation. Or at least move up the ladder a little bit.Steve
*Excellent analysis Fred, I hope Gary will do the tests and post the results. As I read through all the messages in this thread, the following quote from Robert Burns came often to mind (well actually the gist of it, I had to look the actual quote up). Oh wad some power the giftie gie us To see oursel's as others see us! It wad frae monie a blunder free us,And foolish notion.
*
I own a restaurant that has a walk-in refrigerator approx. 6'x9'x7' high.
The refer is built in the back room. 2 walls are on outside walls and 2 inside walls. The ceiling of the walk-in is built with 2x4's and butts the ceiling. The walls of the walkin are 1/4" plywood covered with white fiberglas foodservice grade panels. The ceiling as far as I know has no vapor barrier and in the summer "sweats" real bad and water puddles on the floor. What can I do to stop this? Do I need to remove the panels and put plastic or something else on the walls and ceiling to stop this?? The walkin is 38° and the attic will reach over 100° in the summer.
Thanks Gary