el water heater for heat/ figure BTUs

Fonzie | Posted in Energy, Heating & Insulation on August 29, 2008 07:19am

We have just installed pex in 560 sq ft concrete on 2 inch starfoam. The walls/ceiling are going to be super insulated (R 13 walls + 1 inch R Board) (R 38 ceiling + 1 inch R board). We have the control setup ordered. The heat figured out to be 11000 BTU/hour. I have tried to use the conversion tables and it looks like about 3500 watts approx.

Well, if this is correct I would like to get this in a 20 gal rather than a 30 gal. I haven’t seen it – though I haven’t looked at the cashy ones.

BTW the guy said the pump didn’t move enough to turn on a “demand” el water heater.

Any counsel would be appreciated. This is our first in floor heat.

Reply

Replies

  1. DanH | Aug 29, 2008 02:02pm | #1

    With an electric water heater you needn't worry about having a unit that is a bit oveersized -- there will be no significant loss of efficiency so long as you buy a quality unit.

    In science it often happens that scientists say, "You know that's a really good argument; my position is mistaken," and then they would actually change their minds and you never hear that old view from them again. They really do it. It doesn't happen as often as it should, because scientists are human and change is sometimes painful. But it happens every day. I cannot recall the last time something like that happened in politics or religion. --Carl Sagan
  2. Clewless1 | Aug 29, 2008 03:15pm | #2

    A larger water heater (gallons) will be OK. Sometimes it may circulate w/out actually kicking on the water heater ... so it will cycle somewhat less. If this is new construction, you could combine the doemestic hot water and floor heat into the same water heater ... it is a 'special' water heater ... readily available. Lots of people use them. A great way to combine the two systems (I did it in my new house).

    IMO, R-13 w/ foam is NOT 'superinsulated nor is R-38 w/ foam. I put R-21 in my new house and I don't consider it super insulated. R-38 walls is probably considered 'superinsulated' and a minimum R-49 ceiling is probably superinsulated. Your ceiling is about average ... maybe slightly above. Your walls IMO are average maybe below. Especially w/ your cold Illinois winters. Not trying to badmouth, just in case someone told you that you have the baddest insulation that side of the Mississippi.

    1. User avater
      Fonzie | Aug 30, 2008 01:57am | #3

      I made a mistake on that. We're building 6 inch walls and putting R 19 in them with 1 inch R Board on top. The ceiling is R 38 with the R board too. We have had great luck with the R board. In my non engineer trained experience it disperses where the heat and cold meet - unlike visqueen which will give you instant water droplets. We don't use visqueen and have seen problems remodeling where they have. Yeah, Illinois weather - we know a good day when we see one. Actually I like Illinois weather and have become fairly oblivious to it. We are using a closed system with antifreeze. I see your point though - if the customer was using it for both it wouldn't make any difference. This figuring the btu / hour must not be a real straighforward thing. I met with an electrical engineer today and she said she would have to look it up. I have used the conversion tables but I want to get some counsel from experience.

      1. Clewless1 | Aug 30, 2008 02:54am | #4

        Ok. Yeah, if you can take care of details with respect to the rigid board added to the wall, it's definately a great way to go. For some it's second nature. Just a process of getting used to a different construction detail like anything else.

        My radiant floor is closed system w/out antifreeze. I use the water heater that has the HX built into it. Works fine.

        Your heat load ... do it piece by piece (walls, windows, ceiling/roof) and you'll be fine. Don't forget about the air leakage ... it is a component just like walls.

  3. Clewless1 | Aug 30, 2008 02:57am | #5

    Your total floor area is 560 sqft?? that ain't much, but if it's just two people, it can be plenty. If it's right 11,000 btuh sounds +/- reasonable w/ insulation levels you have ... and not knowing whether you have designed a glass box or not (assume it isn't as you do imply at least some wall area :)

     

    1. User avater
      Fonzie | Aug 30, 2008 07:54am | #6

      Ha, I looked back and I did forget to mention that this is a sharpening shop being built in an existing 2 car garage. Yeah, 560 sq feet, I know you were feeling sorry there. I didn't aim to do that. Actually this is a very specialized type of sharpening - elaborate carbide cutters and draw dies, etc. Not much room is needed. Plus, there will only be one small window. It will be easy to heat. I didn't understand what you meant about having the HX built into the water heater?

      1. Clewless1 | Aug 30, 2008 04:49pm | #7

        a domestic hot water heater that has a heat exchanger built into it for hydronic heating applications. This keeps the potable water separate from the floor heating system, yet they are one in the same heater.

        Your 11,000 btuh load may be a bit big for your application. I calc a CONDUCTIVE load at 80 deg delta T of only 3,800 btuh ... plus air leakage, but that should be small, I'm guessing. Even if it was double, we are only talking 7,400 Btuh. That is a ROUGH calc, not knowing any specifics of your application. You keeping the garage door? That alone may increase losses significantly it's not insulated and weatherstripped. 

        1. User avater
          Fonzie | Aug 30, 2008 05:02pm | #8

          No garage door. There are going to be 2x6 walls on all sides (including the inside of the L which is adjacent to the house) and there will be a 4 inch partially insulated wall outside of that. The only heat loss will be the steel 3ft door and a small slider window. If your figures are right, do you think it could be heated by a 1500wt 120 vt 20 gal mobile home water heater? Or do you have a recommendation on water heaters?

          1. Clewless1 | Aug 31, 2008 03:57am | #9

            Not sure I understand ... the 'only' heat loss is the door and the window ... you do have exterior walls and a roof, don't you?

            Give me a better idea of the geometry/configuration and I can send you a rough cut heat loss. Is a particular space temp critical for your operation?

            I assumed a square box w/ 8ft ceilings and a 15 sqft window and a 3x7 door. This was exposed to the weather on the 4 sides. Sounds like your config. is quite a bit different (i.e. some exterior walls are common to the house). 1.5 KW sounds like it could easily be in the ballpark ... and for a majority of the time (except the coldest of weather), will likely be.

            If your shop environment is like many, your space temp could easily be set at say 60-65 and be quite comfortable ... but I know zip about the relative level of physical moving around that might justify a lower setpoint. Generally, it doesn't take a lot [of physical exertion] to justify it.

          2. User avater
            Fonzie | Aug 31, 2008 02:42pm | #10

            A guy in this area keeps his floor heat set at 61 and it is amazingly comfortable. It is "L" shaped. It would be a 23 x 32 space except the house cuts out a 19 x 9 rectangle out of the corner. We are building 6 inch walls/R board on those two sides too (sound issue as well). There is only one small window - about 16 x 32, and two 3 ft steel doors to the outside. You're right, 8 ft ceilings. With Illinois weather it is important to keep the machines the same temp and control the humidity - not get a dew point going. I'm not sure if I'm taking a risk by trying to use a 20 gal water heater - less residual hot water as well as smaller element. A 30gal isn't much different in price. Plus, some of these are amazingly expensive. Am I missing something about the equivalent of "ball bearings" in water heaters?

          3. User avater
            jonblakemore | Aug 31, 2008 04:48pm | #11

            The difference between the 20 and 30 gallon heater is likely just the size of the tank. What you really want to check is the wattage of the heating element.A larger tank will provide you with 50% more reserve, but no more "heating" capacity. 

            Jon Blakemore RappahannockINC.com Fredericksburg, VA

          4. Clewless1 | Aug 31, 2008 04:58pm | #12

            So for that, your CONDUCTIVE load at 70 Fdeg delta T (~60 in and minus 10 outside) is about 2,900 Btuh. add an assumed air leakage rate of say 0.35 ACH and it goes up to 4,900 roughly. That is 1.43 KW. Margin of error ... round to say 1.5 KW ... what are your options rated at? Remember the VAST majority of time equipment rated less than this will do the job ... you size for the peak or worst case that will typically have a good chance of occuring.

          5. NRTRob | Aug 31, 2008 06:42pm | #13

            water heaters should be oversized by a good 25% or so in most cases, even if dedicated.their heat transfer ability is rated assuming ground temperature incoming water. we have found in the past that they are often not capable of their rated outputs in heating applications.though their efficiency is much better heating than the EF for water heating would indicate as well, as standby loss remains constant and the total load grows.if the water heater does double duty, a fudge factor is good to account for scale buildup as well. constant introduction of fresh water can diminish outputs over time. and of course you need to add the DHW load to the heating load to figure output requirements.I am not sure, however, that the upsized recommendation would hold true for an electric water heater specifically... not sure how hot those elements get, and the difference between radiant return and ground water temperature may not be significant at the dT to the electric element if it's hot enough. However, since it can't be so hot it would flash water to steam, I would assume that it DOES hold up, but I can't swear to it in a court of law.
            -------------------------------------
            -=Northeast Radiant Technology=-
            Radiant Design, Consultation, Parts Supply
            http://www.NRTradiant.comEdited 8/31/2008 11:43 am ET by NRTRob

            Edited 8/31/2008 11:43 am ET by NRTRob

          6. DanH | Aug 31, 2008 09:32pm | #15

            > their heat transfer ability is rated assuming ground temperature incoming water.True for a gas water heater, but not for an electric.
            In science it often happens that scientists say, "You know that's a really good argument; my position is mistaken," and then they would actually change their minds and you never hear that old view from them again. They really do it. It doesn't happen as often as it should, because scientists are human and change is sometimes painful. But it happens every day. I cannot recall the last time something like that happened in politics or religion. --Carl Sagan

          7. NRTRob | Sep 01, 2008 08:07pm | #16

            what's the rating for an electric based on?and, do you know how hot the elements get?-------------------------------------
            -=Northeast Radiant Technology=-
            Radiant Design, Consultation, Parts Supply
            http://www.NRTradiant.com

          8. DanH | Sep 01, 2008 08:43pm | #17

            The rating for electric is based on watts. Watts convert directly to BTUs. There will generally be a **very slight** rolloff as temps increase due to the increase in resistance of the element (which reduces its actual wattage), but it's pretty negligible.Basically, an electric element will continue to put out its rated watts (or close to the rating) up to the point where it's gets so hot it burns out. This only happens when the unit is run dry.
            In science it often happens that scientists say, "You know that's a really good argument; my position is mistaken," and then they would actually change their minds and you never hear that old view from them again. They really do it. It doesn't happen as often as it should, because scientists are human and change is sometimes painful. But it happens every day. I cannot recall the last time something like that happened in politics or religion. --Carl Sagan

          9. NRTRob | Sep 02, 2008 05:57am | #18

            just to restate to make sure I understand then, the element must be hot enough so that the variance in water temperature across the element from ground to heating temperature ranges is a negligable difference, compared to the delta-T from water at either temperature to the element itself.right?if that is true though, I have to wonder how it's not flashing to steam. If it's not flashing to steam, I have to wonder how that is true ;)ah, how I entertain myself. I can't figure out what the element temperature is, but with some digging around, everything hints at "pretty darn hot".-------------------------------------
            -=Northeast Radiant Technology=-
            Radiant Design, Consultation, Parts Supply
            http://www.NRTradiant.com

          10. DanH | Sep 02, 2008 06:19am | #19

            Sorry, I couldn't parse that statement.The element puts out X watts of heat. The temperature on the outer shell of the element depends simply on how fast the water can carry away that heat. Presumably the calculations have been done to predict (or experience has shown) that "free" water can carry off the heat without flashing, up to some reasonable upper limit.Understand that essentially 100% of the heat from the element goes into the water -- there's only a little loss through the end of the element where it penetrates the tank.
            In science it often happens that scientists say, "You know that's a really good argument; my position is mistaken," and then they would actually change their minds and you never hear that old view from them again. They really do it. It doesn't happen as often as it should, because scientists are human and change is sometimes painful. But it happens every day. I cannot recall the last time something like that happened in politics or religion. --Carl Sagan

  4. Clewless1 | Aug 31, 2008 08:28pm | #14

    also ... think about installing a 3-way valve to adjust output to the floor based on current average weather conditions. You want hotter water for bigger loads (cold weather) and cooler water for light loads. You'll know if it is right if your pump runs a LOT ... the ideal condition IMO (it keeps the heating nice and even ... no frequent on/off operation).

     

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Tall Deck on a Sloped Lot

When deck posts exceed what the prescriptive code tables allow, it's time to consult a structural engineer for post sizing and possible bracing.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • The Unabashed Maximalist
  • A 1980s Condo Goes Retro Vintage
  • Sharp-Blade Solution
  • Podcast Episode 684: Masonry Heaters, Whole-House Ventilation, and Porch Flooring

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in