In installing the main appliance receptacles in my kitchen I used a 3 wire cable and alternated the two hot wires on the 9 receptacles.. My plan was to install the protective GFCI receptacles(one on each of the hot wires) but I found out that it is not possible to do so with the 3 wires (evidently because of the common neutral). My question is: Will it work to use GFCI breakers on each of the two circuits (even tho there is a common neutral) or do I ditch the idea of the two wire alternating idea? If this is not clear let me know. Thanks!
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
The FHB Podcast crew takes a closer look at an interesting roof.
Featured Video
Builder’s Advocate: An Interview With ViewrailHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
Bad idea from the start.
Use 9 GFI receptacles all wired to LINE
OR
Depending on the brand of panel/availability .....
....a two pole 20 amp GFCI Breaker
Thanks for your help.
If it is practical to rewire the rectacles you leave the multi-wire to the first box.
Then run 2 separately 2 wire circuit to different boxes. Then you could get by with just 2 GFCI receptacles.
Or GFCI's at each postion.
Or install a TWO POLE GFCI breaker in the panel.
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
Thanks for your helpful word.
What you have to do is install a 240V (double-pole) GFCI breaker. Not cheap.