I can’t find my NEC books, new and old. I don’t want to spend the next 6 hours tearing up the place looking for the books. I know where “I” left them, not where “she” put them. AUGH!!!
sooo… can some one tell me the number of wires for
#6THHN in 3/4″ and 1″ flex metalic conduit
#8THHN in 3/4″ and 1″ flex metalic conduit
basically I need to pull 3feeds(2hots,1 neutral) plus one ground wire
I haven’t pulled wire in about 4 years and I’m having a real brain fart right now. I’m pretty sure that #8 in 3/4 in ok and #6 in 1″ is ok but I’m not sure about #6 in 3/4″.
As always, Thank you.
In the mean time, back to tracing/toning wires
Replies
THHN #6: 4 in 3/4", 6 in 1" FMC
THHN #8: 6 in 3/4", 9 in 1" FMC
What you want to do is OK, but #6 in 3/4" won't be any fun at all to pull.
-- J.S.
My long term memory said yes, but the short term said "Duhhh, better ask"
Thanks for the reply
decided to go 1" after remembering what it was like pulling through 1/2" pvc