mike_maines | Posted in Energy, Heating & Insulation on April 24, 2009 11:29am

I’m stumped on this one.  Yesterday I looked at a two story house where the owner, among other things, noted buckling roof shingles and black stains under the roof sheathing.

Easy, I figured.  Not enough insulation and/or air sealing in the insulated attic floor, and probably no soffit or ridge vents.

Well, there are propa-vents, leading to vented vinyl soffits, and there is a properly installed ridge vent.  The attic floor had additional joists to raise the floor level enough for 8-10″ of blown fiberglass on top of the original 6-8″ of fiberglass batts.  There is probably not enough air-sealing, and an insulated air duct runs through the space, but it looked about as well done as I’ve seen.

The owner had a fan installed in a gable end vent, wired to a humidistat set to turn the fan on when the humidity reached 35° or so.

So the question is, why is the roof sheathing black, and why are the shingles buckling?

 

View Image

Reply

Replies

  1. User avater
    rjw | Apr 25, 2009 12:11am | #1

    It's black from mold - probably the most on the north side -- probably above kitchen and/or bath areas.

    I'd look for (a) a very damp craw space/basement (b) waste vents discharging in the attic (under the aded insul?)

    Unless there are really great reasons to buy, I'd shy away from a resale point of view. That's a subjective view.


    "Ask not what the world needs. Ask what makes you come alive... then go do it. Because what the world needs is people who have come alive."

    Howard Thurman


    http://rjw-progressive.blogspot.com/

    1. mike_maines | Apr 25, 2009 01:38am | #2

      Bob, to keep things short I left out:

      Very nice dry full basement.

      South side (pictured) and north side appear to have equal amounts of mold/mildew.  Kitchen is two floors below. 

      I'll check on waste vents, didn't think of that one, but the quality of construction looked pretty good up there so I'd be surprised if that was the culprit.

      This is a service project for past clients we did a kitchen and bathroom addition for.  They're a retired couple, own the house and aren't going anywhere.  They just want things fixed, and fixed right.  The buckling shingles look weird to me and the roofer (high-end) who looked at another part of the project with me.

      You know, you reminded me that after we did the kitchen ten years ago, we remodeled their master bath on the second floor about five years ago.  I'll check that we didn't mess up the vent fan there.

      Have you seen shingles fail prematurely like this, about ten years into what look like 25yr 3-tabs?  Could interior moisture contribute to shingle failure?  I suppose if the plywood is saturated it could have delaminated.  I'll check on that too.

       

       

      1. User avater
        ToolFreakBlue | Apr 25, 2009 02:34am | #3

        Don't think it is the source of your problem, But I understood it was a No-No to combine gable vents, especially power vented, with ridge venting.On second thought maybe that is problem. The gable vent is drawing air backwards through the ridge vent and the system is not able to function properly.
        TFB (Bill)

        1. mike_maines | Apr 25, 2009 03:34am | #4

          That's an interesting thought.  There are propa-vents at the eaves to act as insulation baffles, but they don't run all the way up the rafters.  Maybe closing the gable vents, leaving the fan off, and allowing the stack effect to do its thing with the propa-vents is the way to go.

          1. coldbuilder | May 03, 2009 11:43pm | #5

            sound like gabel fan could be creating negative pressure in the attic to the extent that it is causing tar to diffuse through your ply and quickly killing the shingles. ever heard of that before? curious..."A small leak can sink a great ship."
            -Benjamin Franklin-

          2. mike_maines | May 04, 2009 04:06pm | #12

            sound like gabel fan could be creating negative pressure in the attic to the extent that it is causing tar to diffuse through your ply and quickly killing the shingles. ever heard of that before? curious...

            Interesting thought, but there are ridge and soffit vents, so I seriously doubt there is any negative pressure involved.  It's not that big a fan.

      2. DanH | May 04, 2009 01:12am | #6

        Have certainly heard of 20-25 year shingles failing in less than ten. Just ask thousands of people who got Certainteed shingles some years back in the Midwest.
        The modern conservative is engaged in one of man's oldest exercises in moral philosophy; that is, the search for a superior moral justification for selfishness. -John Kenneth Galbraith

      3. User avater
        Dinosaur | May 04, 2009 05:23am | #7

        Have you seen shingles fail prematurely like this, about ten years into what look like 25yr 3-tabs? 

        Mike, I have a shingle warranty claim right now I am trying like hell to get the BP rep to come and look at. Been after his invisible arse since October and I'm getting cranky....

        Same basic problem--buckling and cupping 25-year 3-tabs after 9 years--but only over one small area of the roof, and it's the porch roof at that (no heated space under it).

        View Image

        We figure it was a bad lot of shingles; I checked my bills for that job and found we had two batches delivered because of a screw-up in ordering.

        Dinosaur

        How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

        1. Clewless1 | May 04, 2009 06:51am | #11

          talk w/ the manufacturer, man ... don't guess about what it may or may not be. The manufacturer knows what will cause his product to go bad. At least START there. Without that, you don't have a leg to stand on anyway. Know what will cause the condition and determine if that house has the condition. THEN you can talk about what to do or what MIGHT happen ... talk is cheap ... follow up on it.

          1. User avater
            Dinosaur | May 05, 2009 03:41am | #18

            talk w/ the manufacturer, man ... don't guess about what it may or may not be. ...At least START there. Without that, you don't have a leg to stand on anyway. ... talk is cheap ... follow up on it.

            "I am trying like hell to get the BP rep to come and look at. Been after his invisible arse since October and I'm getting cranky...."

            What part of the above extract from my original post did you not understand the first time around??

             

            The rep is hiding. My dealer has 5 unresolved, uninspected (by the mfgr) warranty claims on his desk, and has had some of them there for a year. Mine's been there since last October. The rep has turned into an anwering machine that listens but does not call back.

            I went in in person again two weeks ago and witnessed the dealer leave yet another message on the rep's voice mail. Still no answer. If I don't get an inspection sheduled for this week, I'm calling the mfgr's main office direct and am gonna make a very hairy nuisance of myself....

            Dinosaur

            How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

          2. Clewless1 | May 05, 2009 07:19am | #20

            That's what I meant, no installer, no local rep ... straight to the manuf. If they have unrealiable people installing or representing their product, maybe they're interested in that fact.

          3. User avater
            Dinosaur | May 05, 2009 10:58pm | #21

            Okay, we misunderstood each other.

            The claims weenie at the main office said it would take 4-5 weeks for an inspection; I told him his local rep had already stalled for 7 months so he could stuff that. Sent him some of those pix by e-mail and am supposed to have an answer by next week.

            We'll see. I may wind up covering this one outta my own pocket; thank bog it's only a couple of square out of a 10-square job.

            Dinosaur

            How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

        2. mike_maines | May 04, 2009 04:08pm | #13

          That looks familiar.  That's only 9 years old?  Wow.

          1. User avater
            Dinosaur | May 05, 2009 03:48am | #19

            Yeah, I did that job in 2000. It actually looks worse than some parts of a job I did in 95 using el-cheapo 10-year 3-tabs. Weird. The affected area is only about 75-100 sq. ft. You can see by the photo that the rest of the roof is in perfect shape.

            This is the only problem I've ever had with BP shingles in over 16 years; I prefer their stuff to IKO as there is better uniformity in cut and colour...but I am getting pretty bent about the damned rep hiding out so he won't have to come up with a lousy four packs of shingles on a 30-square job.

             

            Dinosaur

            How now, Mighty Sauron, that thou art not broughtlow by this? For thine evil pales before that whichfoolish men call Justice....

      4. Clewless1 | May 04, 2009 06:47am | #10

        Check w/ the shingle manufacturer; he will tell you under what kinds of adverse conditions that shingles will fail. It's usually fairly specific if I recall ... like auto mechanics ... not a lot of guess work.

  2. Clewless1 | May 04, 2009 06:44am | #8

    Because it should have been a 'de'humidistat?  I'm sure that is what you meant, though. There is a difference and if you assume one is the same as the other ... maybe that IS the problem. Also humidistats/dehumidistats tend to be problematic in that they don't have staying power ... should maintain/replace every few years ... maybe more.

    1. mike_maines | May 04, 2009 04:12pm | #14

      The switch is activated once the humidity reaches a certain level.  I've never heard the term "dehumidistat," care to educate me?  Is it an "on" switch instead of an "off" switch?

      It looks like this: http://www.nextag.com/Honeywell-H46C1166-Humidity-Control-88515317/prices-html

      1. Clewless1 | May 04, 2009 04:37pm | #16

        A dehumidistat works just the opposite of a humidistat. I don't recall the details of how they work. A dehumidistat is often used to control e.g. a bathroom fan ... shutting it off when it senses the shower moisture has been removed. We used them often in the pacific NW where controls were required by energy codes. It was one option.

        Due to their sensing technologies, humidity sensors are much more prone to failure than e.g. a sensible temperature thermostat. The part that senses humidity is very sensitive and prone to 'fowling' (for lack of a better word). In an attic, it may be much more prone to dust/dirt affecting it ... don't know.

        1. mike_maines | May 04, 2009 06:03pm | #17

          Either way, once the humidity reaches a certain level a switch is activated.  I can't see how a humidistat could be that different from a de-humidistat, other than one opens the circuit and the other one closes it.  Good tip on the propensity for failure though. 

          We just discussed it briefly in our office and decided that we will recommend closing off the gable end vents and deactivating the fan, to let the stack effect ventilate the attic.  If it doesn't work it can be un-done. 

  3. Clewless1 | May 04, 2009 06:45am | #9

    Also leaks in the ducts can be VERY detrimental in terms of pumping unwanted air into the attic. If they aren't sealed, all the insulation in the world won't do them any good.

     

    1. mike_maines | May 04, 2009 04:13pm | #15

      Also leaks in the ducts can be VERY detrimental in terms of pumping unwanted air into the attic. If they aren't sealed, all the insulation in the world won't do them any good.

      Good point, I'll check on that too.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

A New Approach for Millwork Finishes

The LED-cure products from LED Coating Solutions offer a fast-curing, zero-VOC finish that works well for trim and cabinetry in small shop settings.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Sharp-Blade Solution
  • Podcast Episode 684: Masonry Heaters, Whole-House Ventilation, and Porch Flooring
  • FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity
  • Tools and Gear for the Moms Who Get it Done

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in