Interior footings vs radiant floor slab?

JohnWalker | Posted in Construction Techniques on December 7, 2010 01:48am

I am designing a basement foundation which includes interior load bearing walls which have strip footings similar to the exterior walls. On top of these there would be a short stem wall (?) the same height as the XPS and slab.

 

These stem walls are normally 8″ wide so it would seem likely you could end up with that 8″ wide concrete wall sticking up out above the slab somewhat.

 

How do you avoid this? Narrow stem wall or monolithic slab/stem wall & sawcut all around?

 

Thanks

 

John

Reply

Replies

  1. davidmeiland | Dec 07, 2010 03:22am | #1

    What about

    forming footings and stemwall sections for these interior bearing lines, up to the bottom of the slab, and then pour the slab right over the top of them? Install rebar dowels vertically in these sections, then bend them over and tie them into the rebar grid for the slab. You end up with small areas of concrete without insulation under them this way, but I'm not sure what your options are if you need direct bearing to soil within your footprint. 

  2. DaveRicheson | Dec 07, 2010 06:19am | #2

    Interior bearing walls in residential construction are generally handled with a "thickened slab" type pour. Since the loads are not that great and the interior footins are not subject to frost conditions they seldom need to be as deep as the exterior wall footings. Depending on your soil conditions and the calculated load they generally are 12 to 16 inches wide and an addtional 6 to 10 inches of depth added to the slab in the interior footing line. Insulating under the thickened area is just a matter on cutting and installing the rigid foam. Rebar is then installed on dolby's and the radiant tubing run in the normal manner.

    If this is a typical frame construction that is about all you need. If you are building the interior bearing walls with cmu's you may need to adjust your thicken slab area for width  as needed to handle the addition wieght. 

  3. Clewless1 | Dec 07, 2010 08:29am | #3

    Sounds wrong ... or I'm not getting your description (very possible).

    Basement wall w/ a load bearing wall ... I did a bunch on my own house w/ radiant slab.

    As another poster said ... thickened slab at the bearing wall. Frame the wall onto the thickened slab. No stem wall needed. I didn't put anchor bolts in during the pour ... I waited and drilled and set those special anchor bolts (forget what they are called) after the fact. I did take pics of my slab/piping prior to the pour so I could know where my piping was when I went to drill and set my anchor bolts.

    1. JohnWalker | Dec 07, 2010 10:51pm | #4

      thickened slab and drilled/epoxied anchors sound best

      Thanks Dave and Clewless, the combination of your suggestions would work nicely. I've seen a lot of thickened slab edges on commercial work but for some reason i didn't think of that for my situation.

      Putting the anchors in after is probably greatly appreciated by the guy screeding (at least).

      Would you just avoid those areas entirely with the radiant tubes or adjust them to make large zones for drilling after?

      Thanks

      John

      1. davidmeiland | Dec 07, 2010 11:02pm | #5

        I'd get

        someone with a thermal imager to locate them before drilling.

        For a few anchor locations you could do this with a low-priced IR thermometer.

        1. DanH | Dec 08, 2010 07:32am | #6

          Of coure, to do that you've got to have the heat on -- not likely if you're still installing walls.

        2. Clewless1 | Dec 08, 2010 07:58am | #7

          Doesn't work if you need to frame now and heating the slab is in the [relatively] distant future.

          1. davidmeiland | Dec 08, 2010 12:55pm | #9

            I didn't realize

            you guys don't have a way to heat up the tubing. it doesn't take much. 

          2. Clewless1 | Dec 08, 2010 08:58pm | #11

            If you don't need to, why bother? Heat up the tubing; locate, rent, and/or borrow a thermal imager ... just measure and be done with it. If it was already done and he didn't know where he could drill then that might be worth the trouble. I think I left my thermal imager in my other suit.

      2. Clewless1 | Dec 08, 2010 08:13am | #8

        It requires some care in planning. You can either largely avoid the area w/ e.g. only one or two crossings. But it depends on the circulation and layout of your rooms/zones. In my case, I covered two rooms w/ one zone, so there were practical limits. I criss crossed my wall w/ the tubing ... 7/8inch I think and like 16" oc.

        I think the best is to lay out the tubing like you want and then measure from the walls where you want to locate e.g. 3 anchor bolts; centering them between loops. When you go to drill, you can have confidence of location. If you have tight spacing, you might want to alter it at those points ... easy to allow the tubing lines to be closer at your anchor points and then fan out again a foot away from the wall. That way, you give yourself a few more inches of confidence when you go to drill. Bottom line is to have good documentation on where your tubing is. I took pics of mine and had my tubing tied to my steel mesh reinforcing ... which allowed me to more easily determine where my tubing was.

        The thermal imaging method COULD work, but usually your framing is done LONG before your system is up and running. In my case, my floor didn't see heat for at least a year after my wall framing was done.

        That's the beauty of the radiant system ... you can configure much however you like and tailor it for your needs.

  4. DaveRicheson | Dec 08, 2010 02:58pm | #10

    Anchors

    Mark a couple of referance points on adjacent walls and label them. Lay out your tubing and then lay a couple of tape measures across the tubing and pulled from the referance marks. Take  several pictures of the tubing with the tapes laying across it. Print the pictures, laminate them and keep them in a safe storage spot.

    After your floor is poured, lay the tapes back in place to the referance marks. Use your pictures to  locate the tubing at the corresponding measurements.  Mark those locations on the floor with a large fet tip marker. Drill your anchor bolts in at least 3" away from  any of the marks.

     I do it all the time for plumbing and conduit runs beneath slabs. It just got easier and cheaper with digital cameras and computers. You can edit and annotate you photos also.

    I use to make up "home owners manuals" for clients when doing remodels and additions using either Polaroid shots or prints from a 35mm SLR. If done clearly with the tapes. you can use them for years of future remodels and trouble shooting.

  5. harryv | Dec 09, 2010 11:07pm | #12

    Interior footings & radiant

    We do this a lot. I agree with Dave Richeson's method. We lay out and mark all interior walls after the rigid insulation is installed. The radiant installer then keeps his loops away from any areas that could be a problem later. It's our responsibility to advise him of anchor type and locations. I've also had to place hold downs during the footing pour to get the required imbedment depth. Tape measures and string lines are all it takes. Pouring a stem wall to top of slab height is very difficult and can almost guarantee cracks in the slab radiating from the corners. Our radiant installet staples the tubing to the rigid insulation. We use rebar for reinforcemnt and it's installed after the tubing. This keeps the tubing low in the pour and provides a little insurance for drilling or saw cutting the slab later. I think this method is superior to tying the tubing to the top of the rebar or welded wire mesh. Take measurements and lots of digital photos prior to the pour. Can't count the number of times an architect has wanted to change someting after the slab is poured and we've gone back to the photos to see if the changes could be made safley with regard to the radiant tubing. I hope this is of some help.

    HV

    1. JohnWalker | Dec 10, 2010 01:35am | #13

      how to keep XPS in place?

      Harry/Dave, others

      Thank you for the great advice.

      Do you insulate under the interior footings or just the sides? Ideally I'd have 2" XPS throughout but i suspect placing it under the interior footings is not structurally recommended. Do you box the footing with XPS and leave the bottom open to bear on the existing ground? How do you keep it all in place?

      John

      1. harryv | Dec 11, 2010 12:09am | #14

        XPS In Place

        We insulate to the footings. We hold the rigid foam back to the edge of the footings so the thickened area of the slab has full bearing across the footings top. If the interior  footings are quite a bit lower than the slab, we would probably pour a stem wall up closer to the bottom of the slab elavation in order to retain the backfill.  I like to put our perimiter foam in place and friction fit  areas I can to keep it from moving. I will also try to ramset the perimiter foam to the foundation so it does not get disloged and move up during the pour. I have never "boxed" down to a footing with rigid foam. I am afraid that a buried corner may cause a crack. You could stake the foam down with gutter spikes if you have an area you are afraid might move. The weight of the rebar helps hold the foam in place also.

        Harry

      2. Clewless1 | Dec 11, 2010 10:02am | #16

        Here's a shot of part of my house just before the pour. Held the insulation back to the edge of the thickened slab. Thermally it's a bit of a compromise, but I think structurally a reasonable (if not necessary) tradeoff. The footing was a bearing wall between a living area and a bedroom. You could run the tubing seperate, depending on your zoning/layout, etc as I mentioned earlier.

        Hope this pic upload works ... not sure I've done it since the "upgrade".

        1. JohnWalker | Dec 11, 2010 01:20pm | #17

          a picture is worth a 1000 words...

          Thanks Clewless

          That very clearly illustrates how you left a void in the insulation for the thickened slab footing.

          If you have any other similar pictures detailing that kind of pour I would really appreciate seeing them.

          (You could send them to my email account rather than the forum if desired but I don't know how to do that without putting my address up and NOT getting a ton of spam.)

          Thanks

          John

        2. davidmeiland | Dec 11, 2010 08:20pm | #18

          Is the

          wire mesh laying on the insulation, or was it raised before/during the pour?

          1. Clewless1 | Dec 12, 2010 03:21am | #19

            It was raised during the pour. In hindsite, I'd have liked to have it on dobbies. I think I asked the contractor about this and he thought it best to not have them and he is a reputable contractor. Never had issues w/ the slab. We did a acid etched stain finish and the slabs turned our very nice and consistent. We've had no cracking issues at all and it's been in place like 5-6 yrs now.

  6. User avater
    Jeff_Clarke | Dec 11, 2010 08:16am | #15

    If you are worried about the possibility of drilling through radiant tubing after the fact simply cut some 12" lengths of  1 1/2" x 1 1/2" steel angle and use electrical tape to tape them on top of the tubing ('legs down') in the area of concern.    When post-pour drilling with a masonry bit if you're near a tube the drill will hit the steel, which you should be able to feel (as the steel deflects the masonry bit).

    Jeff

    1. harryv | Dec 13, 2010 11:49pm | #20

      If you are worried

      Jeff, That's a great Idea!!!

      1. DanH | Dec 14, 2010 06:29am | #21

        Of course, don't depend on the shields not getting displaced during the pour -- belt and suspenders.

        1. harryv | Dec 15, 2010 12:11am | #22

          Of course, don't depend on

          Belt and suspenders???????

        2. harryv | Dec 15, 2010 12:11am | #23

          Of course, don't depend on

          Belt and suspenders???????

          1. DanH | Dec 15, 2010 07:02am | #24

            Yep, you got it right -- double up on the protection.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Hole Saws That Are a Cut Above

The Spyder carbide-tipped hole saws cut quickly with a quick-release arbor that makes it easy to remove the core.

Featured Video

Builder’s Advocate: An Interview With Viewrail

Learn more about affordable, modern floating stairs, from design to manufacturing to installation.

Related Stories

  • Podcast 551: Power Tool Batteries, Building as a Third Career, and High DIY
  • Podcast 551: Members-only Aftershow—Badly-Built Homes
  • Podcast 550: PRO TALK With Carpentry Program Instructor Sandy Thistle and Graduate David Abreu
  • Podcast 549: Energy Upgrades, Chimney Inspections, and Questions About a Home You Might Buy

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • Pretty Good House
    Buy Now
  • 2023 Tool Guide
    Buy Now
  • 2022 Fine Homebuilding Archive
    Buy Now
  • Code Check Building 4th Edition
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 314 - April/May 2023
    • 7 Options for Countertops
    • Tool Test: Wood-Boring Bits
    • Critical Details for Ductless Heat Pumps
  • Issue 313 - Feb/March 2023
    • Practical System for a Seismic Retrofit
    • Fine Homebuilding Issue #313 Online Highlights
    • Practical System for a Seismic Retrofit
  • Issue 312 - Dec 2022/Jan 2023
    • Tool Test: Cordless Tablesaws
    • Gray-Water System for a Sustainable Home
    • Insulate a Cape Roof to Avoid Ice Dams
  • Issue 311 - November 2022
    • 7 Steps to a Perfect Exterior Paint Job
    • Options for Smarter Home-Energy Tracking
    • The Fine Homebuilding Interview: James Metoyer
  • Issue 310 - October 2022
    • Choosing a Tile-Leveling System
    • Choosing Between HRVs and ERVs
    • Custom Built-in Cabinets Made Easy

Fine Homebuilding

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in