I have an electric question.
I need to install a circuit in a box for an outdoor socket.
Their is room for one more breaker in the box , but no more room on the neutral bus bar. can I put two wires under one screw? I know it is against code, and I know the box needs to be updated.
I just want to get that outdoor socket in so I can stop running an extension cord out the window .
Thanks.
D.C.
Replies
You CANNOT place more than one white, neutral, grounded conductor under one screw in the neutral bar. [Unless listed by the mfgr.]
Two green, ground wires are usually OK. So if this is a main panel, you might be able to move a green or bare ground wire to another ground wire hole to free up a space.
NOTE: It is legal to make a splice in a panel box. For instance, in this instance, you could turn off the involved breakers, take off one of the other #14 white wires, splice it to your new #14 white wire and a short length of #12 white wire which you then insert in the recent vacated hole in the neutral bar. If using #12 guage stuff, then use a #10 pigtail. Solid connection of neutrals is very important. Select a neutral from a different phase if you do this.
~Peter
Contents may settle during shipping but then we might just be selling you air.
>>NOTE: It is legal to make a splice in a panel box.
FWIW, Different jurisdictions have different interpretations on that issue.
"It is as hard for the good to suspect evil, as it is for the bad to suspect good."
-- Marcus Tullius Cicero, statesman, orator, writer (106-43 BCE)
NEC 373-8. This is written backwards. "Enclosures .. for overcurrent devices shall not be used as junction boxes...unless adequate space ...is provided." There is usually room in a panel "less than 40%" of the space for a splice or two.
Of course, in new work, this looks sloppy and unplanned but in this instance, this is old work.
~Peter
Thanks.
A couple of jurisdictions near PGH just don't allow splices in breaker panels, most (all?) of them in NW Ohio do. (Many/most panels never see the shine of the AHJ's flashlight around here!)
"It is as hard for the good to suspect evil, as it is for the bad to suspect good."
-- Marcus Tullius Cicero, statesman, orator, writer (106-43 BCE)
I will try a little different approach, some panels have accomendations for 2 wires under a neutral screw, older Westinghouse comes to mind.
If your panel won't allow for it you can take a 2 wire circuit out of the panel and put it in a junction box near the panel along with your new circuit, from there you can run a 3 wire to the panel to feeed both circuits. Using the appropriate breaker(s) of course.
bake
In some cases the box will acommodate an add-on bar.
dear dan,
to add a bus bar, how do I connect them together?
d.c.
Generally the add-on bus bar is used for grounds (and just screwed to the grounded box), in a box originally set up with a common ground/neutral bar. I think I've also seen one where the add-on bar had a jumper that screwed to the top corner of the original bar.
My inspector will allow two wires under one screw if they're both the same guage, for 15A & 20A branches. Mixing 12 AWG and 14 AWG on the same screw is a no-no: in most cases, the 14 AWG ends up being loose.
And dont forget that any outside recepticle must be on a GFI breaker.
Bill Koustenis
Advanced Automotive Machine
Waldorf Md
>>And dont forget that any outside recepticle must be on a GFI breaker.
Or (at least in my area) be a GFI receptacle or downstream from one on the load side.