Outbuilding Electricity supply

benraymond | Posted in Energy, Heating & Insulation on December 24, 2010 03:12am

Hello all,

I’m going to be building a shed out back of my house.  I want to get electricity to the site before I get the crushed stone that I’m going to put under the foundation.  

I read the quick article in Fine Homebuilding about getting electricity to the outbuilding – Underground rated cable with PVC conduit when it enters or exits the ground, buried 1 foot deep.   

I’m a little concerned about just burying the cable – does anybody put this stuff in PVC conduit all the way through?  Do I have to worry about water getting in the conduit? Flexible or rigid?

The article showed some kind of bushing on the end of the 90 degree bend of the conduit as it exits underground – do I really need this?  Didn’t see any bushings in my big box store.

 

Any replies greatly appreciated,

Ben

Reply

Replies

  1. DanH | Dec 24, 2010 03:50pm | #1

    Direct burial cable is rated for exactly that, and has a long history for safe and reliable use.  You do need to make sure it's buried deep enough, and I think that code requires 18" in some cases, so you want to verify the proper depth (keeping in mind that it never hurts to go deeper).

    The one case where you might want to consider using conduit the whole way is if the soil is exceedingly rocky (with sharp rocks).

    Obviously, if you use conduit for just the start and end of the run then water does get into the open ends of the conduit.  But this is not harmful (so long as the conduit enters the structure above the "high water line").

    You do need the bushings, at least to be code compliant.  I believe (but stand to be corrected) that your basic box bushing will do the trick -- what's wanted is simply the radiused opening that would normally face the inside of the box, to eliminate any sharp edges bearing on the wire.

    1. Amish Electrician | Jan 07, 2011 12:36pm | #11

      First, a few corrections:

      Direct burial cable is required to be buried deeper than conduit; in this instance, I believe 24" is called for.

      Then the cable needs to enter boxes, etc., with the proper fittings. These fittings will provide strain relief as well as protecting the cable from abrasion.  The problem with these fittings is that they are (often) not listed for outdoor use. Pay attention to the details.

      From a design standpoint, what's 'legal' isn't always smart. This forum is replete with threads where someone wants to make a change six months later, and doesn't want to dig up and replace the wire they just ran. Run pipe, and all is well- you can easily replace or add wires without digging anything up.

  2. sapwood | Dec 24, 2010 07:21pm | #2

    Some day you will want to dig in your yard. It might be for a fence or for a tree, but you (or someone) will dig. So, take impeccable notes and make a map. It won't hurt to put caution tape 6" above the wire or conduit also.

  3. junkhound | Dec 25, 2010 07:03am | #3

    i gots 'bout 20 sheds with power,

    alla da feeders are 2-3 ft deep sintz i gots mah own backhoe,  

    after backfill of about 6 " i throw whaterver trash is around on top as a warning nex time ah digs somethin', tin cans, drywall ends, lumber with rot, rusted fence or wire rope, jimmy hoffa, etc......

    Have found that old worn out extension cords that osha wont letcha us onna job site with some tar on the bad spots makes grate unnergrnd feeders........ some have lasted 30 year......  

    1. benraymond | Dec 25, 2010 10:26pm | #5

      No backhoe for me unfortunately.  That ground is cold and hard, so I am having to work for 12 inches deep.  I think I will put some conduit over the part that does run under my lawn (only about 12 feet) and leave the rest as is.

      Thanks for all the replies,

      Ben

  4. DanH | Dec 25, 2010 09:03am | #4

    Of course, JH has had several dogs mysteriously drop dead while walking across the yard.

    1. junkhound | Dec 29, 2010 10:00pm | #8

      these guys tried to dig some Cu up ofr scrap....

  5. gfretwell | Dec 25, 2010 11:04pm | #6

    If you want to be legal, the rule is

    PVC conduit at 18"

    Direct bury cable at 24"

    or if this is GFCI protected, in a residential yard

    a single circuit 120v 20a or less it can be 12" (cable or PVC)

  6. Amish Electrician | Dec 29, 2010 03:23pm | #7

    I saw that FH article, and I had some reservations about it then. I'd like to take a big step back, and approach this job from a fresh perspective.

    First off, be HONEST with yourself. Just what do you really wnat to accomplish? Simply put a light and plug out there ("just in case"), or are you building a workshop/ "man cave?"  How likely is it that your needs will change over time?

    Secondly, I HATE digging. So, I make sure I don't have to do it more than once.  This means: a foot-wide trench, 30" deep, with a nice bed of sand both under and over the oversize pipe(s) I place in it.

    You want it deep, at least as deep as a full-size shovel blade, so it doesn't get hit whenever the yard sprinklers need fixing. Deeper is better. The FH article was simply wrong about the 12" depth; such would be possible only if there was also some feature that guaranteed that the area would not even be walked upon, ever.

    You want pipe(s) because cables eventually either break, or you want more power and need bigger wires. Use pipe and you can just pull in the new wires. As for using extension cord material? Forget it; some soils will very quickly eat up that rubber, leaving you with bare wires underground. The bigger the pipes, the easier the pull.

    You want two pipes, as someday you'll want a phone, or TV, or sprinkler controls, or some other sort of low-voltage wire out there. Why dig twice when pipe is cheap?

    If you're running more than one circuit, or plan to have a panel out there, you will also need a ground rod at the shed.  You'll also probably need a disconnect switch on the outside of the shed.

    Where the pipes exit the ground, extra protection is required. PVC should be at least Schedule 80. If you're using rigid steel conduit, you'll want to wrap it in pipe tape- especially the first 12" in the ground. A common practice is to use steel for the elbows and the uprights, and PVC for the horizontal run in the bottom of the trench.

    Bringing power to a shed is often a 'tripping point' where a permit is required.

    1. benraymond | Jan 01, 2011 12:07am | #9

      Thanks for the suggestions.

      I'm not going to need a man-cave.  I do want to avoid pulling a permit if possible.  The shed is a long way from the house, and pulling cable over that distance would be a tough sell.

      I think Junkhound was kidding, and I plan to use good underground rated cable in any case, conduit or no.

      Just looking for a light and an occasional place to plug in a skill saw when the need arises.

      Finally, just realized that the pool shed is much closer than the house - That shed has it's own panel for the pump motors and some GFCI breakers for some outside outets - I may go 20 feet lateral rather than 50 feet back to the house.

      Thanks

      Ben

      1. DanH | Jan 01, 2011 12:17am | #10

        Heck, 20 feet is only a couple of lamp extension cords -- easy!

      2. Jigs_n_Fixtures | Jan 07, 2011 05:52pm | #12

        A permit is required if there is power.

        In most jurisdiction a permit is required beginning at either 100 or 120-square feet of "shed". 

        Almost all jurisdictions require a permit if there are permanent provisions for power, water or sewer. 

        I got in trouble once because I had installed a 30-amp plug in the garage, and would feed my shed that had an RV style hookup receptacle, and was wired. 

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Detailed Assemblies for an Airtight Small Home

Drawings and details for building a high-performing slab-on-grade foundation, double-stud wall, and truss roof with nontoxic materials

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast 463: The Best of the Fine Homebuilding Podcast, Volume 3
  • Fine Homebuilding – July 2022, Issue #308
  • Pretty Good House Book Excerpt: Copper Farmhouse
  • Fine Homebuilding Issue #308 Online Highlights

Highlights

Fine Homebuilding All Access
Justin Fink Deck Building Course announcement
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Sign Up See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • Outdoor Projects
    Buy Now
  • Code Check Building 4th Edition
    Buy Now
  • Pretty Good House
    Buy Now
  • 2021 Fine Homebuilding Archive
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 308 - July 2022
    • Pretty Good House Book Excerpt: Copper Farmhouse
    • 10 Dos and Don'ts for Electric In-Floor Heat
    • A Sturdy Rail for Outdoor Stairs
  • Issue 307 - June 2022
    • How to Raise a Post-Frame Home
    • Trimming Deck Stairs
    • Evolving an Energy-Efficient Envelope
  • Issue 306 - April/May 2022
    • Framing Stairs to an Out-of-Level Landing
    • Building a Zero-Energy Home for Less
    • Good-Looking and Long-Lasting Traditional Gutters
  • Issue 305 - Feb/March 2022
    • The Steady Surge in Residential Solar
    • The Fine Homebuilding Interview: William B. Rose
    • How Good Is Your Air Barrier?
  • Issue 304 - Dec 2021/Jan 2022
    • Why You Need Blower-Door Testing
    • Passive-House Standards for Everyone
    • Window Replacement With a Side of Rot Repair

Fine Homebuilding

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Newsletter

Get home building tips, offers, and expert advice in your inbox

Sign Up
This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2022 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Account

  • Log In
  • Join

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Sign Up See all newsletters

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to set_percent%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in