The wall is balloon frame 2 stories, 1×8 T&G sheathing. Expanding a room, I want to make 8 feet wide arch on 2nd floor part of the wall. The arch will leave about 30 inches of wall on one side. Entire wall is 21 feet. I thought 30 inch shear wall is possible because such work is done for garage openings. I plan to use 1/2 inch plywood horizontally, covering studs and header, 8d nails every 6 inches. There is no floor sill but I believe there is a ceiling sill plates. Does this make a shear wall, and should plywood also cover the top sill plates? Would using 3/4 ply be going over board? Thank you.
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
Fine Homebuilding's editorial director has some fun news to share.
Highlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
*
Hi Kwan,
Can you give a little more information about your header size and composition as well as the type and construction of the roof/attic above?
Off the top I would have to recommend you get an opinion from a local engineer/building inspector BEFORE proceeding with this project.
Gabe
*Check with a local engineer! In Los Angeles, the minimum width of shear used to be 3.5:1. For an 8' ceiling, that was about 2'-4" for the wall width. Since the 1994 Northridge quake, it has been reduced to 2:1 or 4' minimum width for an 8' ceiling. Check with an engineer.
*
Thank you for the information. The local town inspector is likely to send me to an engineer. I think I will follow the advice.
*
The wall is balloon frame 2 stories, 1x8 T&G sheathing. Expanding a room, I want to make 8 feet wide arch on 2nd floor part of the wall. The arch will leave about 30 inches of wall on one side. Entire wall is 21 feet. I thought 30 inch shear wall is possible because such work is done for garage openings. I plan to use 1/2 inch plywood horizontally, covering studs and header, 8d nails every 6 inches. There is no floor sill but I believe there is a ceiling sill plates. Does this make a shear wall, and should plywood also cover the top sill plates? Would using 3/4 ply be going over board? Thank you.