too many ground connections?

paul42 | Posted in General Discussion on October 2, 2007 06:13am

I’m looking at the grounding system on my new house and it just does not look right to me.

320 Amp service.  As I understand it, the meter base will be wired to a 200 amp panel in the garage, and a nearby 200 amp disconnect.  The 200 amp disconnect is wired to a 200 amp panel in the “unfinished basement” – which is actually just a really tall crawl space with a concrete floor.

Three ground rods and a ufer ground.  One ground rod connects to the 200 amp panel in the garage, one ground rod connects to the 200 amp disconnect, and the third ground rod attaches to the 200 amp panel in the crawl space.  Both 200 amp panels have the ground connected to the neutral.

The meter base and the 200 amp disconnect are not in place yet, and the ufer ground isn’t wired yet.

My understanding is that all of the ground wires should connect to one panel, and that is the only panel that should have the ground and neutral connected.  This obviously isn’t wired like that.

 

 

 

Reply

Replies

  1. User avater
    ShelterNerd | Oct 02, 2007 07:54pm | #1

    I'm no electrician but my recollection from conversation with my electrical inspector is that every panel should have it's own ground rod and that the ground and neutral should only be bonded at the main.

    ------------------

    "You cannot work hard enough to make up for a sloppy estimate."

  2. User avater
    BillHartmann | Oct 02, 2007 08:35pm | #2

    The panel is the basement is definitly a NO-NO.

    The neutral should not be bonded to the ground at that point. And you need a 4 wire connection between the disconnect and main panel.

    And there is no need or advantage to ground rod at that point. Only EXTERNAL structures need additional ground electrode system.

    You don't need all of the ground electrodes. By the code the ufer is enough. Don't need any ground rods.

    But there appears to be lots of confusion or local amendments about this.

    Now 400 amp service is a bit trickly.

    The neutral can be bonded to ground electrode system anyplace between the disconnect and the weather heat for overhead service. That is what the picture shows in the NEC handbook. Basically that means at the at the meter or at the disconnect.

    But in either case the disconnect and the meter need to be bonded together. I THINK that can be done with with wire or metallic conduit and using special bonding bushings and nuts.

    And where you have more than one electrode I THINK that the it bonded at one place and the other(s) at other places in the ground electrode system. IE the disconnet, the meter, or the other electrodes.

    Lot of special and detailed requirements on this and I probably have several wrong. But I know that what you describe is also wrong on several points.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
  3. User avater
    SamT | Oct 02, 2007 09:03pm | #3

    All your grounds must be bonded into one system; rods, pipes, ground busses, and ufer.

    All your neutral returns must also be bonded into their panels' neutral busses, then all the neutral busses must be bonded together.

    The neutral and ground systems must, and can only, be bonded together at or near your primary (main) "Hot" system disconnect. IOW, the ground system cannot touch the neutral system more than once.

    SamT

    1. paul42 | Oct 02, 2007 09:37pm | #4

      That agrees exactly with my understanding - plus I thought that the three ground rods should be wired in series to the ground connection on the main panel with one contiguous wire.

      I asked the electricians and they were certain that it was wired correctly. 

      I mentioned it to the state licensed inspector.  He said that since the crawl space panel was NOT a subpanel of the garage panel, that both should have the ground tied to the neutral.

      Oh well, if the city inspector says it passes inspection, I can always fix it after they are all gone.

       

       

      1. HWG | Oct 03, 2007 12:48am | #5

        Paul, having more than one ground rod in a system is a big no-no from a lightning protection standpoint (and hence the requirements in the NEC).  Granted there can be multiple grounds rods if they are connected together properly into a grounding ring, and I am NOT referring to the ground wires within your electrical wiring, but a separate ground ring.  I manage 9-1-1 centers and this is a huge issue for us -- we are like a lightning magnet with all of our electronic equipment.  The NEC allows the grounding and grounded legs to be bonded together only at the main service entrance, not at any of the subpanels.  Bonding at subpanels, and having multiple ground sources, allows lightning to flow "backwards" through these wires in its efforts to equalize the potential throughout the building and blows the electronic equipment as it does so.  One point of ground per structure, and only bonded at the service entrance.  Very important.Woody

        1. CaseyR | Oct 03, 2007 02:43am | #6

          For a detailed and interesting discussion of grounding electrode systems and lightening, check out the following:http://www.iccsafe.org/cgi-bin/ultimatebb.cgi?ubb=get_topic;f=11;t=000932;p=2

        2. User avater
          BillHartmann | Oct 03, 2007 03:46am | #8

          I had a long detailed reply with copies of the code, but my system locked up and it took too long to do it again."Paul, having more than one ground rod in a system is a big no-no from a lightning protection standpoint (and hence the requirements in the NEC)."That is not correct.In fact is a ground rod is used as a ground electrode it either has to be tested to be less than 25 ohms or a single ground rod needs to be installed at least 6 ft way.I also list a series of different types of things that can be used as electrodes and any of them that exist MUST BE USED.The key is tht they are treated as a Ground Electrode SYSTEM and only bonded to the neutral at one place in the system, the service entrance."Bonding at subpanels, and having multiple ground sources, allows lightning to flow "backwards" through these wires in its efforts to equalize the potential throughout the building and blows the electronic equipment as it does so"Bonding at a sub-panel also can lead to electrical danagers other than lightining damage.The code also allows a SUPPLIMENTRY ground electrode to be connected to the EGC at equipment. However, it can't replace the EGC..
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  4. DanH | Oct 03, 2007 03:08am | #7

    You don't specifically state -- is it an attached or unattached garage?

    If your view never changes you're following the wrong leader
    1. paul42 | Oct 03, 2007 04:06am | #9

      There is a breezeway between the house and garage, but a common foundation and roof, so it has to count as attached.

      1. DanH | Oct 03, 2007 04:31am | #10

        Hard to say if that counts or not.
        If your view never changes you're following the wrong leader

        1. paul42 | Oct 03, 2007 04:33am | #11

          The panel in the garage serves several circuits in the house, so I doubt that the inspector would consider them separate.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Tools for Managing Home-Building Financials

Production manager Ian Schwandt explains how financial tools such as QuickBooks or Buildertrend can help companies track project costs for a healthy outcome.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast 485: Air-Sealing a Mobile Home, Owner/Builder Tests, and Ready-to-Tile Shower Bases
  • Podcast 485: Members-only Aftershow
  • Fastener System for Solving Deck Fascia Board Expansion
  • Improve Home Efficiency With Inflation Reduction Act Rebates

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • Code Check Building 4th Edition
    Buy Now
  • Pretty Good House
    Buy Now
  • Outdoor Projects
    Buy Now
  • 2021 Fine Homebuilding Archive
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 309 - Aug/Sept
    • 10 Steps to Install Crown Molding on Cabinets
    • How to Get Sturdy Walls Without OSB
    • Choosing the Right Construction Tape for the Job
  • Issue 308 - July 2022
    • Pretty Good House Book Excerpt: Copper Farmhouse
    • 10 Dos and Don'ts for Electric In-Floor Heat
    • A Sturdy Rail for Outdoor Stairs
  • Issue 307 - June 2022
    • How to Raise a Post-Frame Home
    • Trimming Deck Stairs
    • Evolving an Energy-Efficient Envelope
  • Issue 306 - April/May 2022
    • Framing Stairs to an Out-of-Level Landing
    • Building a Zero-Energy Home for Less
    • Good-Looking and Long-Lasting Traditional Gutters
  • Issue 305 - Feb/March 2022
    • The Steady Surge in Residential Solar
    • The Fine Homebuilding Interview: William B. Rose
    • How Good Is Your Air Barrier?

Fine Homebuilding

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2022 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Account

  • Log In
  • Join

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in