Does anyone have a link to span tables for I beams. I am wondering what size beam I need to span 33 feet in a garage to eliminate any posts. The garage is 24 feet wide. and the roof is 4/12 asphalt with 3/4 sheeting. the walls are cement block. the rafters are 2 feet apart. currently there is a wood beam that mainly consists of a 6×6 beam with one post in the center. the garage was a stable in its earlier life. any resources would be greatly appreciated
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
From plumbing failures to environmental near disasters, OHJ staffers dish on our worst and best moments.
Featured Video
How to Install Exterior Window TrimHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
To fgure a beam size you need to know the loading. Since your profile isn't filled in and you did't say where you are, you could be in northern Canada or southern Florida.
I had and engineer spec an 8" 34# for a 25' span with only the second floor load on it (not roof). It wasn't enough. The floor was still springy.
33' is going to be a huge beam. Taller is better than heavier (something I wish my engineer had mentioned)
If you go 10 or 12" tall you don't need as much meat in the steel.
If you reduce the joist span by using two beams you get a stiffer floor too. (another thing that went unspoken).
One heck of a lot larger one than you imagine. 33' is a long span
Welcome to the
Taunton University of Knowledge FHB Campus at Breaktime.
where ...
Excellence is its own reward!
What kind of depth do you have to work with?
A 14" beam will be a lot more manageable and perform better than a 10" beam. Don't take those numbers as meaning anything- they're just off the top of my head.
Jon Blakemore
RappahannockINC.com Fredericksburg, VA
If the garage is 24' wide, why do you need to span 33'? Do you mean you need a 33' beam with 24' between supports? Actually if that's the outside dim of the garage, your span is less than 23'.
"Put your creed in your deed." Emerson
"When asked if you can do something, tell'em "Why certainly I can", then get busy and find a way to do it." T. Roosevelt
If the building is 24'x33' and the beam is just going to hold up ceiling joist for attic space, he can just run a I-beam or properly sized lvl or glulam the 24' way and run two small lvl's the 16' way butting into the 24' beam on each side to hold up the ceiling joists.
Joe Carola
If the garage is 24 feet wide, why do you need to span 33 feet?
My take is that the garage is 24 x 33. The beam is a ridge beam supporting the roof rafters.
If it's a 24'x33' garage, why not run the ridge beam the 24' way and the rafters run the 33' way? You obviously want a full cathedral ceiling and have a choice which way to run the beam, no?
If this is single story new construction, why not just use trusses?
I was thinking this was carrying a second floor.
If this is single story new construction, why not just use trusses?
Sounds like a one story garage and he wants a full cathedral ceilings. In order to get thast you need a structarl beam. Using scissor truasses gives you a lower ceiling.
If the main picth is a 6/12, then the bottom of the scissor trusse I think would be arouind 3/12. This is why scissor trusses are no good if you want a high ceiling and if you are limited with height restictions scissor truuse won't work that well.
If he doesn't care about a full cathedral, scissor trusse will work fine.
Joe Carola
Why not read the original post? It's not new construction. The garage is a converted stable.
I didn't miss that. But the guy's talking about essentially reconstructing the garage (or at least the roof), so there's no reason to be constrained to simply replacing the existing beam.
As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz
Sixteen replies, and the OP hasn't come back to read any of the messages. Makes me wonder if we're all wasting our time...
He's not dead, He's electroencephalographically challenged.
> Makes me wonder if we're all wasting our time...You're on BT and you gotta even WONDER about that???
As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz
I think Dan deserves an award for this one. http://forums.taunton.com/tp-breaktime/messages?msg=123181.19
Mike
Small wheel turn by the fire and rod, big wheel turn by the grace of god.
Edited 8/9/2009 1:21 pm by ruffmike
I thought the same thing. So to save MY time I'm recommending a W36X300. Ought to cover it.
Runnerguy
You want that galvanized?"Put your creed in your deed." Emerson
"When asked if you can do something, tell'em "Why certainly I can", then get busy and find a way to do it." T. Roosevelt
Just to be safe, that's probably not a bad idea. Also, I was figuring on 50ksi steel but everybody probably assumed that.
Runnerguy
Just to be safe, that's probably not a bad idea. Also, I was figuring on 50ksi steel but everybody probably assumed that>>>>>>>>>>>>>>>..
>G<
Now we got a problem with headroom, LOL
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
Yo Piffin,
Now we got a problem with headroom, LOL
Headroom, headroom we ain't got no problem with headroom....walk in the room and bang you head all day long! With that level of steel he shouldn't ever have one single problem with knocking it out of place.
Pedro the Mule - & he can use the little stars he creates to light it up at night
He never mentioned reconstructing roof or anything else, just wants to get rid of the post
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
He didn't mention it, but he's talking about it.
As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz
That's what I was thinking -- trusses. Or even a 24-foot beam or two supporting a longer beam the other direction.
As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz
Span tables for steel beams are in the Steel Construction Manual. I think they are up to the 13th addition now. There is the short answer to you primary question.
Long answer is that if you change the load path, as you are indicating, you will also need to change columns to support the beam, as well as new stem walls/footings due to the additional loadings. And not knowing your locale, soil, snow, seismic and wind loading allowances may need to be taken into account, which may require additional lateral bracing, especially for such a long span.
Recommend getting a local engineer to assist you with this.
I think I can say, and say with pride that we have some legislatures that bring higher prices than any in the world. - Mark Twain
"currently there is a wood beam that mainly consists of a 6x6 beam with one post in the center. the garage was a stable in its earlier life."
A bunch of you guys just missed the boat on this one by not reading the OP
It is NOT new construction
It is NOT a ridge beam
It is NOT running in the 24' direction
Welcome to the
Taunton University of Knowledge FHB Campus at Breaktime.
where ...
Excellence is its own reward!
"currently there is a wood beam that mainly consists of a 6x6 beam with one post in the center. the garage was a stable in its earlier life."
"A bunch of you guys just missed the boat on this one by not reading the OP"
The descriptoin is a bit vague, but I see it as a 4/12 roof with the rafters supported by an old 6"x6" beam. How is it not a ridge beam?
Well, with all the work I have done on old places, I have never once seen a 6x6 ridge beam, so I was picturing it at the ceiling level.You are right, he neither specifies, not rules out that it is the ridge beam. If that is the case, it could be even easier than I imagined to run the steel 24' direction
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
No I can't say I've ever seen one either. You are probably right. I don't think I have the slightest idea of what's going on here
Methinks the 6 x 6 is at the ceiling level (reading between the lines that aren't there).
Jeff
There may be a way to re-engineer this whole thing fairly easily to use a beam in the 24' direction, but would need several photos top show the current layout and structure before I could sketch up a solution.
Welcome to the
Taunton University of Knowledge FHB Campus at Breaktime.
where ...
Excellence is its own reward!
More info please - 24' deep x 33' wide? Attic storage? (or not) Habitable space above? (or not) Snow region? Roof load? etc.
You're likely going to be in the W12x26 or W12x40 range, depending upon some of the above and deflection criteria.
You'll need 3 1/2" or 4" lally columns at both ends with suitable foundation/footing bearing - keep that footing in mind (you're not going to sit on slab/block).
Jeff
Edited 8/9/2009 12:51 pm ET by Jeff_Clarke
I was thinking more like W14x38(36) but we know nothing about upper storage and snow loading
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
Based on the original post he needs a beam that will span 33 ft to carry a load that a 6X6 can carry over 16.5 ft. (Assuming there are no point loads involved?)
Edited 8/9/2009 1:32 pm ET by sisyphus
True, but if you are reverse engineering it, you need to know if that 6x6 is White oak, Heart Pine, or spruce, and whether it was sufficient or is in failure.
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
No question that the OP should provide more information. It did say that the structure was stable previously which could imply that it has gone awol since but I took it to mean that the beam (as you say wood species unknown) had been sufficient. Whether it met code or best practice is, of course, another story.
Was a stable. Is unstable.
"Was a stable. Is unstable."
You're right I missed the "a" when I read the first post.
We just built an attached 36' x 24' garage w/storage above. Engineer speced two sets of double 18" x 24' LVLs, evenly spaced, for the main beams.
We'll have a kid
Or maybe we'll rent one
He's got to be straight
We don't want a bent one
He'll drink his baby brew
From a big brass cup
Someday he may be president
If things loosen up
in my pea sized brain me thinks maybe a few girder trusses supporting the ridge and bearing on the walls would be best.
Woods favorite carpenter
You got some good darn peas in that pod of yours
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
We're wondering if this thing fell down on your head yet?
but even if you've vaporized, it's been an interesting discussion. Thanks for teasing us into it.
Welcome to the
Taunton University of Knowledge FHB Campus at Breaktime.
where ...
Excellence is its own reward!