dispute over elec. code

pinko | Posted in Energy, Heating & Insulation on April 23, 2008 05:48am

This is sort of a follow-up/addendum to an earlier question to all the well-versed elec. pros here…

I’m having a bit of a dispute w/ my building dept. about a particular of the NEC. I’m building a ‘guest house/office’ (separate structure from the main house) which has its own service.. In other words, a separate service drop and meter. The meter is part of a meter/main service combo installed on a pedestal 50 feet from the building. It’s a 200A service. The service equip is basically mobile home equip. w/ a main disconnect and an over-current device (main breaker) AT the pedestal/meter base. There, it has its own grounding rods installed, and the service neutral and grounding bus-bars are BONDED at the case–as per code. From there, I have an underground conduit (Sch.40 pvc, 2.5″) connecting the building to be supplied, which terminates at a distribution panel inside the structure (conduit penetrates the foundation at the crawl space and continues up into the panel in the house.) So I’m essentially running a feeder to the building…Copper…2/0 for the conductors, 1/0 for the neutral.

It is not a mobile home. It’s a permanent structure on a block foundation. The Code in sec. 250.32 specifies that for a feeder of this type, the cable must be a 4-wire (W/ ground) OR a 3-wire, w/ the building supplying it’s own grounding system.

I’ve asked the dept. why I MUST use a 4-wire feeder (w/ a grounding wire run w/ the 3 supply conductors) to connect the building, as they’ve told me, when the code seems to clearly state that is not the only option. No one seems to be able to show me where the code specifies otherwise.

Anyone know why, specifically, I need to pull a 4-wire (mobile-home feeder) to a permanent structure, vs. a 3-wire w/ a separate grounding system at the new building? Do I have a legitimate argument here? (the 4th wire—#1 copper—is costing me about $100 extra. I’d rather not run it if I don’t need it).


Edited 4/22/2008 10:49 pm ET by pinko

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. PeteBradley | Apr 23, 2008 06:30am | #1

    It's not worth trying to "win" this one for $100. Even if you did, you'll likely pay for it in other ways.

    Pete



    Edited 4/22/2008 11:31 pm ET by PeteBradley

    1. pinko | Apr 23, 2008 06:36am | #2

      Sooo...Do you mean I'm right about the Code here?

  2. cap | Apr 23, 2008 07:28am | #3

    IS there any metallic path like a phone line, CATV, or metal piping, other than the feeder, between the pedestal and the building?  If so--you must run the equipment grounding conductor.

    This per the 2005 NEC.

    I believe the 2008 NEC requires an EGC, the thinking being that a parallel metallic path might be created in the future.  

    Check to see what NEC version is the basis for the local Code, and also see if the AHJ has adopted any amendments to the NEC.

    Cliff

    1. pinko | Apr 23, 2008 02:45pm | #5

      Cliff, I also read that portion of the (2005) Code, and no, there is no metallic connection between the building and the pedestal, or between the building and anything else for that matter.Does the 2008 NEC specifically require the 4th wire? I have the 2005 and I believe the 2005 is the standard here right now. But, I could be wrong about that.

  3. wallyo | Apr 23, 2008 08:20am | #4

    Pinko I am not an electrician but my first thought is that the city, is taking your panel in the structure to be a sub panel in which case the ground and neutrals are isolated; thus four wires are needed not three and no grounding rods either. The remote is not just a meter but a meter and disconnect and it gets the grounding rod.

    http://www.groverelectric.com/pdfs/35_How_To_Install_200amp_100amp_SubFeed.pdf

    more info http://www.groverelectric.com/how_to_do_it.htm

    links are from my favorite Plumbing/Electrical supply house in the world Grovers.

    1. pinko | Apr 23, 2008 02:52pm | #6

      I appreciate your info Wally but, I know the sub-panel requirements for a separate (isolated) ground to be pulled. It's just that this is the main service for the structure---not a sub-feed. And it's not a mobile home, therefore, what's the reason I need to run a 4th wire?

      1. wallyo | Apr 23, 2008 04:29pm | #9

        My point is in there view it is not the main service, they are considering that the panel 50 feet away is the main service, it has the main breaker, it has the grounding rods the other panel at the building is a sub panel and needs to be wired as such.I am having a four plex service put in now, the meter base has; mast, 4 meters, four 100 amp breakers it gets, two grounding rods, one tie in with in x feet of the water line as it enters the building. Each other panel is a sub panel and wired as such, four wires to each no grounding rod. I am not doing it a licensed electrician is, that is how he has it.I do not know if you are a licensed electrician or not, but if i was not a licensed electrician (which I am), I would just do as the inspectors asks. Even licensed electricians don't argue with the inspector over something like this, If you want to argue it go ahead, but it may cost you more in the the long run because an upset inspector will go over everything else with much more scrutiny, He will measure every hole and tell you you need nail plates, because the holes are too short from the face of the stud, but not tell you which stud needs them. 100 $ is cheap insurance to keep him on your good side. Just my opinion.Wallyo

        Edited 4/23/2008 9:31 am ET by wallyo

        1. pinko | Apr 23, 2008 05:06pm | #10

          And I agree w/ you, Wally.But my inspector is sort of laid-back country-type folk who is open to 'suggestions'...Admittedly, he's not sure why he wants me to run a 4-wire feeder. I may be able to explain to him why he doesn't. IF the code permits. Btw, he also mentioned he'd like to see a SECOND disconnect on the house at the entry point...something about a "30 foot rule".. Never heard of it. Electricians I talked to never heard of it. The main disconnect is at the meter, in front, and within plain sight of the house; 50 feet away. Anyone here heard of this 'rule'?

  4. BoJangles | Apr 23, 2008 03:15pm | #7

    We always run a separate bare #4 in those cases, not a 4 wire cable.  In fact, I have never seen that done around our job sites.

    Every underground service in our community is run like this.  They require all underground wiring to be protected by a breaker at the pole or service box.

    1. pinko | Apr 23, 2008 04:27pm | #8

      Well I'm not really talking about a "4-wire cable", as in USE or something like that, but 4 individual THHN wires. The 4th wire was sized to be a #1 for the GEC for my 200A feeder---IF I actually needed it. The feeder conductors will be protected by a breaker on the meter combo, as I mentioned before.In any event, no way could I pull a solid bare wire that size through my conduit!

      1. BoJangles | Apr 24, 2008 05:21am | #16

        I'm not talking about pulling a bare #4 wire in the conduit.  When we do it, we run the bare #4 outside of the conduit if we even use conduit.  Most of the time we use USE cable...three strands.

        Why do you need a #1 cable for a grounding conductor on a 200 amp service?

  5. Scott | Apr 23, 2008 05:43pm | #11

    If I understand this correctly, the building is a subpanel from the main overcurrent protection at the service. This opens the old discussion of subpanels having their own ground versus running a bond conductor back to the main panel. It's been discussed here many times; the search function may help you.

    Around here it is almost always ruled that the ground protection be only at the main. Livestock barns (which I don't think your building qualifies as) are just about the only exception.

    Scott.

    Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

    1. pinko | Apr 23, 2008 06:11pm | #12

      Actually, Scott, the inspector told me I ought to ALSO put a grounding system (rods) on the house panel and bond the ground bus--and the GEC--to it as well.. "Can't never have too many grounds" were his actual words, IIR.See what I'm dealing with here?

      1. cap | Apr 23, 2008 06:43pm | #13

        Code does require a grounding electrode on any separate structure--to serve as a lightning or other high-energy event (like cross 'tween primary line and secondary line) drain.

        I don't have a copy of the 2008, I'll check on-line tonight.  But I believe the 2008 does req. 4-wire feeder.

        Cliff

      2. wallyo | Apr 23, 2008 06:46pm | #14

        The only reason I see for the second disconnect breaker at the structure is safety, If I remember it can be done either way. But without has to do something with distance and line of sight. I think it is a good idea to have one at the sub panel, you know the drill, You are working on the sub panel, have the main off 50' away some one sees it is off and flips it on without finding out why it is off.Now I understand you bewilderment, as I see it it is one way or the other not both: 4 wire no rod, 3 wire and rod.Just curious why did you put the panel 50 feet away and not just set the meter base at the structure, with a main panel directly on the other side? R V pad or something?Wallyo

        Edited 4/23/2008 11:47 am ET by wallyo

        1. pinko | Apr 23, 2008 08:37pm | #15

          Quick answer: the meter pedestal is exactly 250' from the transformer pole...the max distance I could get w/ out paying for a new pole...And the building is exactly 300' from said pole. I had to make up the difference of 50' w/ a feeder.

  6. sparkytim | Apr 24, 2008 07:48am | #17

    I think you have a good arguement, however, I like running a ground anyways.  #1 cu sounds to large to me for an equipment ground.  I thought #6 cu was good for 200 amps on a feeder. 

    1. pinko | Apr 24, 2008 05:12pm | #18

      To answer both questions, I have no idea why I needed a #1 wire as the ground. The only reason I can come up w/ is because on a 200A mobile home 4-wire feeder, the cables are 4/0, 4/0, 2/0, 1/0 (AL). Same pattern for my copper, I suppose. Bottom line is, inspector told me he wanted to see the 4-wire feeder, and the 'master electrician' at my elec. supply house said it had to be a #1 (I argued for a #2, but was talked out of it). Incidentally, he also argued for the 4-wire, although he couldn't explain why either.I've bought the wire ($750 worth), I'll be pulling it today, so I s'pose it's a non-issue now.But I still haven't discovered why, per Code, I needed the 4-wire. I guess it'll just be another one of those perpetual mysteries in life.

  7. Gabriel24 | Apr 26, 2008 09:21am | #19

    I have bee reading all these messages, and they are very interesting and very educational. I saw the two web-sites posted about electrical calculations.If I may, I vould like to ask you( assuming I understood correctly):  The guest house you are building has a separate service drop and meter. It is installed on a pedestal 50 feet away and you built an underground conduit sch.40 to connect to the house.  Why the service drop does not come directly from the pole to the house instead of having a pedestal 50 feet away?   This way you would treat the whole set-up as an individual separate house?

    1. BillBrennen | Apr 26, 2008 10:51am | #20

      Gabriel,Re-read posts #15 and #16 for the answer to your question about the 50 foot separation of the meter from the house.Bill

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Making the Move to Multifamily

A high-performance single-family home builder shares tips from his early experience with two apartment buildings.

Featured Video

Builder’s Advocate: An Interview With Viewrail

Learn more about affordable, modern floating stairs, from design to manufacturing to installation.

Related Stories

  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data