Don’t replace that Zinsco panel

BruceT999 | Posted in Construction Techniques on June 25, 2006 09:11am

Twice now I have encountered complaints of lights flickering on residential circuits with 1960’s/70’s era Zinsco subpanels with aluminum bus bars. Lights would blink now and then, TV would shut down (voltage spike protector circuit?) and in one case, a touch-on/off lamp would randomly turn itself on. In one unit the panel was in a dimly lighted hallway and I could actually see, through gaps between breakers, flashes from arcing.

Breakers all were in good shape and showed no sign of damage to the contacts, but the aluminum bus bars were pitted and eroded and coated with nasty deposits of aluminum oxide from arcing.

Instead of tearing out the wall in order to fit a new and bigger box I spent 20 minutes returning the old one to near-new condition.

Those old Zinsco duplex breakers contact each of the busbars at a different level, so swapping the bus bars from left to right puts new metal under the breaker contacts.

All I had to do was to shut off power at the meter, disconnect both feed wires, pull off all of the breakers (allowing them to hang from their wires), pull the two mounting screws from the bonding bar assembly that also holds the bottom end of the bus bars, and slip them out. I then polished the metal a little with steel wool, put the original left bar in the right slot, right in left slot, connected the feed wires, pushed the breakers back in place and put the cover back on.

If the buildings are still standing in 30 more years when arcing damage has happened again, the next guy can replace the box – I’ll be 90 years old and won’t care anyway.

BruceT

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    Gunner | Jun 25, 2006 11:35pm | #1

      Pretty good idea you got there. Mine did the same thing. I didn't even try that. I just changed it out. My thinking at the time was If I have one 220 breaker go bad then I can cover the cost of the new panel. $80.00 at the time. I had previously lost one 15 amp breaker and when I put in my hot tub I had to get a new double pole breaker. I had scrounged them up at work so I got lucky. But the cost would have been pretty steep if I had to pay for them.

       Anyway that was my thinking at the time. That and the fact that I do it for a living so it was no big deal.

     

     

    Rock the Tipi!

  2. renosteinke | Jul 01, 2006 12:20am | #2

    I cannot agree with this idea, for a couple of reasons.

    First of all, in the course of damaging the bussbars, the heat will also damage metal nearby- damage that may not be particularly visible. So, the "fix" probable won't last 30 years.

    Second, the heat will also damage the breakers. Since we have no reliable way to tell if a breaker will continue to trip when it should, the breakers should be replaced. This brings us to...

    Third. The breakers are no longer manufactured. Ones offered for sale are expensive, and are "reconditioned," no longer UL listed (even if the marks are present).

    There are other reasons to consider a new panel, as well as an over-all upgrade to the wiring.

    Old panels often have too few breakers for the necessart circuits. For example, since Zinsco went to the "great scrapyard in the sky," we've come to recognise a need for at least two kitchen circuits. An old house will often have problems with breakers tripping, as too many appliances are used at once.

    Obtaining GFI breakers can be difficult for Zinsco- and Arc faults impossible.

    Finally, sale of the property, and insuring it, will be harder with an obsolete panel.

    1. User avater
      maddog3 | Jul 01, 2006 01:24am | #3

      ....yeah, ......what you said..

      .

      .

      .Wer ist jetzt der Idiot

      ?

  3. User avater
    zak | Jul 01, 2006 02:39am | #4

    Yeahhh.. . . . .  you should have seen my zinsco.  5 mainst to flip before you got all the power off, space for about 15 circuits (I'm now up to 34 on my new panel), etc. etc. 

    You may be right if there's nothing else wrong with the house wiring, but if you're going to work on the rest of the house wiring, I think it makes sense to go ahead and upgrade the panel.

    zak

    "so it goes"

    1. User avater
      BruceT999 | Jul 01, 2006 07:42am | #5

      I agree with Renosteinke, Maddog and Zak, that old places are under-wired by todays standards, but for a single woman in a 900sq foot townhouse, I think re-wiring the place to provide multiple circuits in the kitchen and additional circuits in other rooms would not be worth the cost.As for Zinsco replacements being re-conditioned, I know that they used to be, but there is at least one company making new replacement breakers for Zinsco panels.I inspected all of the breakers before putting them back in the panel and there was no sign of heat damage to cases or contacts and all of them were capable of shutting off and then restoring power to their respective circuits. Is there a safe and reliable way to test a breaker's functionality under actual overload conditions? I suppose I could plug a bobby pin into an outlet, but I don't think I want to :)BruceT

      1. renosteinke | Jul 01, 2006 09:42pm | #6

        The reason that the UL listing is no longer valid on reconditioned equipment is that there is NO industry standard way to test an individual breaker, to ensure that it will trip when it is supposed to. UL tests of new breakers actually destroy the breakers; an assumption is made that identical assemblies, made under identical circumstances, will perform the same. This is validated by quality controls and the testing of random samples. It just is not possible to do this with used equipment- you have no idea where the stuff has been. Likewise, there are new breakers manufactured as replacements to obsolete ones, but virtually all of these are not UL listed. The recent floods, etc., have brought to light 'hidden damage' that may occur in electrical equipment. The fact is, everything wears out... and electrical panels are no exception. Too expensive to change out a panel? Compare the price of a proper "service change" to what you pay for a new roof, or to remodel the bathroom- both tasks routinelt done to older homes. Just because the wiring is not as visible as the new countertop does not mean it's any less important.

        1. frenchelectrician | Jul 02, 2006 07:21am | #7

          for other members in this forum i will let you know that i dealt with alot of zinsco breaker box as well.

           

           myself I do know Renosteinke  very well i keep in touch with him pretty often ,,

           

           anyway many zinsco breaker box is very diffucalt to repair espcally with bussbar burn up and pitted in alum bussbar and many time breaker concat do get weak over the time and it will actally fail.

          how fast it will fail hard to say but overloading get them pretty hot and short circuits ??   humm you are pretty much on your own because the zinsco dont trip very well at all even a overload it will not trip at all.

          i have quite few service calls related to this and many time i strongly recomoned to replace the box with more modern set up because the cost of repalcement breaker is getting to the point where it not even worth [ beepped ] a thing. and many hardware store only stock very limited items and those repalcement breakers are genrally not UL listed at all

          and other thing with Zinsco breakers some of the house wiring is pretty well cooked as well [ just the point before it start the fire ]

          i think there is a link i dont rember where it was and they have class action lawsuit going on but i dont have the facts with me with lawsuit going on.

          all i care is the safety for the homeowner safety sake here

           

          for other peoples if you have a Zinsco breaker box Please do call a real electricican and they will take a look and give you the price to replace the breaker box to safe manner

          i done this alot before the cost i just cant tell you because each area the cost will varies alot and also the local code issuse will show up as well

           

          Merci, Marc

           Master Electrician

        2. User avater
          BruceT999 | Jul 02, 2006 05:57pm | #11

          Thanks Renosteinke and Cap for your answers to the question about testing breakers. I had assumed that there wouldn't be much to go wrong with a breaker, especially since they are called upon to trip very rarely. In 35 years living in my house I have had to re-set a breaker only a handful of times, so other than turning them off and on deliberately, most of them have never had to do anything. So this brings up other questions. Renosteinke said "The fact is, everything wears out... and electrical panels are no exception." If a breaker trips once or twice in 35 years, what wears out? Should I be suspicious of the condition of breakers in my 35-year old Square-D combination meter and service panel box?CAP said, "There is a UL-listed test instrument that measures the magnetic response of a 15 or 20 amp brach circuit breaker." Should I get a licensed electrician to run this test on that Zinsco box or even on my own Square-D?Is it true that you should cycle all breakers off/on annually to keep them mechanically free to trip when needed?Thanks for taking time on this.BruceT

          Edited 7/2/2006 11:06 am ET by BruceT999

          1. renosteinke | Jul 02, 2006 06:13pm | #12

            I have not heard of regular flipping of breakers as a practice, but see no harm in it. Breakers do contain contacts, springs, and sundry little parts. Most will trip from at least two separate causes- usually heat, and magnetism (created by current passing through). Heat can change the behavior of springs, contacts can be damaged by arcing, and everything can be affected by corrosion or grit that interferes with movement. This is where lots of folks in New Orleans are going to get "bit." After the flood, many are using breakers that look, on the surface, to be clean. Give them a few years, however, and those breakers are not going to be reliable. In a similar manner, you can be sure that lots of replaced breakers are going to turn up in the "reconditioned" market. Again, lets look at the costs involved. New breakers usually cost under $5. Obsolete ones, $20. You don't have to buy many obsolete breakers to exceed the cost of a new panel.

          2. rjw2 | Jul 02, 2006 09:54pm | #13

            >>I have not heard of regular flipping of breakers as a practice, but see no harm in it.

            A fairly common maintenace suggestion; I believe the manufacturers recommend it once a year.

             

          3. cap | Jul 03, 2006 02:44am | #15

            Bruce,

            It's a very common maintenance practice; cycle each breaker two or three times once a year to exercise the mechanical linkage and redistribute the grease on the piviot points.  Have spare breakers handy (or be prepared to go get 'em) if a breaker won't close and hold.  I've learned this the hard way...

            Keep in mind that when a breaker trips under a short circuit type fault, the arcing  takes a toll on the contact points.  And when there's an overload that causes a trip, there's wear on the breaker too--the bimetallic strip that overheats, bends, and causes the breaker to open is designed for only so many cycles.  The point is, if a breaker trips more than a few times (on either short or overload conditions), it ought to be replaced.

            Unfortunately, in a lot of instances where a breaker trips, the resident or occupant will try to reset the breaker several times without addressing the cause of the trip.  With an overload, they may get it to close (for a while).    It's only when the breaker fails open, that an electrician is called.  If it fails closed, the fire department usually gets the first call, then the electrician.

            There are only a couple of brands of breakers (FPE two-pole in particular) that have a documented fail-secure problem.  Most of the time, if a breaker fails, it fails safe--i.e., open and can't be closed.

            You could have the breakers tested with the KO breaker tester.  Not many professional electricians have the tester, so you might have to hunt for someone who can do the testing.

            Actually, there's little need for concern with a Square-D panel that has Square-D breakers in it.  Square-D breakers have an excellent reputation for reliability, and their short circuit response is one of the best (quickest).  Square-D (the QO line) is expensive, and you get what you pay for.

            Based on my experience, on a Zinsco panel with 30-year-old breakers, I'd expect at least one breaker in 20 will fail the test.  Does this make the building unsafe?  Not necessarily, if the fixed wiring is all properly installed and maintained.

            As far as the safety of the electrical system, if the branch circuit wiring is questionable, the best thing to do is to evaluate it with a voltge drop tester, fix it up, and add circuits as needed to alleviate overloads.  That may necessitate replacing the panel to accomodate more circuits.

            This brings up the whole topic of the safe working life of fixed building wiring.  People generally assume that building wiring lasts forever.  For instance, knob and tube wiring can continue to serve 70 years on, if installed correctly, not improperly modified, and never overstressed.  Those three conditions are rarely met.

            The NFPA (the folks who publish the NEC and other Codes) is conducting a study on how building wiring ages.  They've actually cut sections of walls out of buildings and taken them back to the lab to dissect and test them.  I'll visit the website and report back what the status and findings are to date.  The website is http://www.NFPA.org, but be advised that the full results of most studies are are generally accessible to members only.

            Cliff

      2. cap | Jul 02, 2006 08:09am | #8

        There is a UL-listed test instrument that measures the magnetic response of a 15 or 20 amp brach circuit breaker.  It drops a dead short across the circuit and measures trip current and time to trip.  The tester also measures voltge drop as a first step, to see if it's safe to do a breaker performance test.

        The manufacturer is KO Instruments.  They have a website.

        The tester isn't cheap.  By that I mean it's over a k-buck.  But it's the only safe way to actually test breaker response for mag trip (i.e., dead short conditions). 

        I've found that about 5-7 percent of vintage zinsco breakers fail the magnetic response test.  These are breakers that will manually cycle and otherwise appear O.K.  Makes it pretty easy to make the case for a panel replacement.

        Cliff

        1. User avater
          BillHartmann | Jul 02, 2006 02:50pm | #10

          Is there any test of the thermo trip on the breaker?IIRC it is not untill you get to around 6-9 times rated current until the magnetic trip controls.I don't have any statistcal information about the details of electrical problems that cause fires, but you often here "caused by overload spacing heaters". Now I would suspect that they are more typically overloaded by much less than would take for the magnetic trip to activate.

          1. cap | Jul 03, 2006 01:58am | #14

            Bill,

            No tester for overload trip testing that I know of.

            And you're right, the fault current on short circuit can reach many times the breaker rating before the breaker opens.  Some breaker brands have higher set points than others.

            It's interesting using the KO breaker tester--seeing a current of 250 to 300 amps for 100 to 200 milliseconds--on a 20 amp breaker that's functioning properly.  The tester is programmed to stop the test if the current goes too high or for too long.

            When I test breakers, I advise the client that there's a small but real risk of blowing apart a weak splice in the circuit.  Not that that's a bad thing, it exposes a weak point, but it's gonna cost money to find and fix it, and they need to know that. 

            I've tested circuits in commercial occupancies, with wire run in conduit, where the high short circuit current causes the wires to slap around violently in the conduit and make quite a racket.

            I believe that a lot of the fires reported as electrical causes by the general press are due to appliances or cords, i.e., not the fixed building wiring.  And most of the fires actually caused by fixed wiring are due to improper use of materials (like using lamp cord as fixed wiring, or overfusing) or substandard techniques (like flying and/or improperly made splices).

            Cliff

  4. rjw2 | Jul 02, 2006 02:20pm | #9

    The cautions mentioned are all worth considering.

    Keep in mind that a contractor has additional concerns in such situations:

    Which is cheaper, trepalcement or refurbishing?  At today's labor prices, usually replacement

    "Last Guy In" syndrome: the last guy/gal to work on a component has "bought it" in the sense that any future problems will probably be blamed on her/him.

    Personally, I'd live with Fed Pac breaker box, butr not a Zinsco in the condition you described, even as "refurbished.

     

  5. Inspector62 | Sep 27, 2012 10:52pm | #16

    With all due respect to the OP, I just strongly disagree.  We aren't exactly talking big money to replace the panels.  If the buss is pitted, simply moving the breakers around is simply not advisable.  Ask this question, would the UL approve this repair?  No way.  There is also another issue not address here, the gutter space is insufficient by today's standards putting undue stress on the wires.

    Bottom line is replacement is the only recommendable option considering the expense to risk considerations.

    http://www.ableinspector.com

    Bruce L. 

    1. florida | Sep 28, 2012 01:49pm | #17

      Do you realize you're responding to a thread that is 6 years old? All those people are long gone.

  6. Bamaben | Nov 25, 2016 09:04am | #18

    Zinsco Power panel

    Where is the master breaker for the Zinsco power panel.  Apparently I do not have one in the power panel itself.  The panel is rated at 150 AMPs

    1. DanH | Nov 25, 2016 01:11pm | #19

      There is a "master breaker"

      There is a "master breaker" somewhere.  If the panel doesn't have one then it's upstream somewhere -- in the "main" panel, if this is a subpanel, or at the "service entrance".

  7. ZinFanDel | Apr 12, 2023 08:10pm | #20

    Amazon, Home Depot etc. now offer replacement copper bus bars with plating...
    https://www.homedepot.com/p/Connecticut-Electric-125-Amp-Type-RBK-UBI-Replacement-Buss-Bar-Kit-for-Zinsco-Load-Centers-UBIZRBK12/100669974

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Simple and Discreet Countertop Power

A new code-compliant, spill-safe outlet from Legrand offers a sleek solution for a kitchen island plug.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Fire-Resistant Landscaping and Home Design Details
  • A New Approach to Foundations
  • A Closer Look at Smart Water-Leak Detection Systems
  • Guest Suite With a Garden House

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data