Will a GFCI outlet work on an ungrounded circuit?
By considering things like energy-efficient mechanicals, window orientation, and renewable energy sources, homes can be evaluated to meet the energy codes. Here's what the IRC has to say.
Yes.
In fact installed GFCI is one of the code approved ways to install "grounding" receptacles without having a ground. They, and any downstream receptacles, are supposed to be labeld No Equipment Ground.
Note - that a plug in tester will not test the GFCI, but the builtin test button does work.
Also GFCI should not be installed to supply an appliance where a false trip might cause damage. That includes refigerators/freezers and sump pumps.
Also an ungrounded GFCI supply a surge protector supply computers or TV's will not give full surge protection with a true ground.
Otherwise GFCI's without a ground are perfect for upgrading kitchen counter receptacles, bath, basement, outside, etc.
Yes. The GFCI works by determining whether there's any difference between the amount of current flowing in the hot and the amount flowing in the neutral. This can be sensed very easily by wrapping a few turns of wire around the pair. Anything sensed by that inductive pickup is a difference current, which means that electrons are escaping someplace. It's a really elegant solution.
-- J.S.
Yes. (Just reenforce what the others have said.) In some cases the test button won't work, but that's the only problem.
No electrons were harmed in the making of this post.
they will work as long as the neutral is still bonded in the panel !!
Even that isn't required. You could have a situation where the "ground" (what the person is standing on) is halfway between hot and neutral. The GFCI would still trip if there were a fault.
but where is the reference, if the neutral is not bonded"
On the pole.Actually, there doesn't need to be a reference per se. So long as any current flows outside of the two wires, the GFCI will trip. It could be because you got between the hot of the GFCI-protected circuit and a 100KV line somewhere (though in such a situation the arcing would probably negate any protection the GFCI provided).--------------
Edited 10/31/2005 6:49 pm by DanH
I was looking this up after I said it, and I have to change my remarks now... I agree ...no bonding is required"
Thank you guys. That is great information for a hopeless inhabitor of old houses.