Lighting on 20-amp Circuit

zztop | Posted in Energy, Heating & Insulation on September 24, 2003 01:45am

In the latest issue of Fine Hombuilding (just received the November issue), the article on low voltage undercabinet lighting states that lights must be on a 15-amp circuit.  I loosely quote from page 65: “…the NEC requires lighting to be on a 15-amp circuit.  [therefore] I couldn’t tap into the 20-amp appliance circuits.”

Is a 15-amp circuit for lighting in fact an NEC requirement?  Or does the author simply  mean that the 20-amp appliance circuits have to be dedicatd with no other fixtures on them?

Thanks,

vlperk

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    Gunner | Sep 24, 2003 02:58am | #1

    Somebodies probably misquoting someone here. 20 amp for residential lighting in most cases is overkill. The main thing is no you don't want to tap into appliance circuits for under cabinet lighting. I don't have my code book here but it's like any other book of it's nature you can read a lot into nothing.

    Who Dares Wins.

  2. pm22 | Sep 24, 2003 03:24am | #2

     I noticed the same thing myself.

    Article or section 411-6 states "lighting systems operating at 30 volts or less shall be supplied from a maximum 20-ampere circuit.

    As for the more general rule, I found it once but can't find it again. But you can run household lights on either 15 amps or 20 amp circuits. What the author was probably refering to is you can't run the kitchen [or other] lighting from the two dedicated kitchen appliance circuits.

    ~Peter

    EDIT: Found it in Article 210-23 (a): "A 15- or 20- ampere branch circuit shall be permited to supply lighting units..."



    Edited 9/23/2003 11:47:25 PM ET by PM22

    1. Jamie_Buxton | Sep 24, 2003 06:48am | #4

      "Article or section 411-6 states 'lighting systems operating at 30 volts or less shall be supplied from a maximum 20-ampere circuit.'"

      Is that 20 amps at 120 volts (upstream of the transformer) or is it at the lamp voltage (downstream of the transformer)?

      1. BarryO | Sep 25, 2003 02:23am | #5

        My copy of 411-6 reads (1999 NEC):

        411-6. Branch Circuit. Lighting systems operating at 30 volts or less shall be supplied from a maximum 20-ampere branch circuit.

        So the 20A is the 120V branch.

        There were a number of "issues" with that article.  210-23(a) says 20A branches can be used for lighting, so I don't know where he got the prohibition from.

        ALso, he uses landscape wiring inside the walls.  Any low-voltage wiring inside walls needs to be CL2 or CL3 rated.

        They should have had an electrician review this article before publication.

        Edited 9/24/2003 7:24:13 PM ET by BarryO

        1. User avater
          BillHartmann | Sep 25, 2003 04:08am | #6

          "There were a number of "issues" with that article. 210-23(a) says 20A branches can be used for lighting, so I don't know where he got the prohibition from."

          But read the Exception to that section.

          But the article was poorly worded. It should say that it can't be connected to on the 20 amp small applaince circuits.

          1. User avater
            Wayfarer | Sep 25, 2003 08:18am | #7

            It seems like there are a couple issues perhaps:

            1) the maximum 20A issue for lighting; yeah, you can use the latter, but it is way overkill.

            2) tapping into a dedicated 20A circuit (for the kitchen) and its surrounds (ie as per code--dining room and whatever); no! this does not include lighting.

            Basically, as I see it, and I'm just now hooking up the lights in a house that I am wiring:  you have to have two 20A dedicated circuits in the kitchen and immediate area(s) for receptacles/outlets.  Lighting is a whole different deal; yeah, you can incorporate more 20A circuits, but why would you?  Unless of course some lighting is that draining (could it ever be?); at the most, you might find a dedicated fan or some other utility for a 15A circuit, but a 20A?   Nah, leave that for the microwave, dishwasher/disposal, etc.  Everything else in the kitchen is pretty straightforward spec-wise regarding oven, and some of the latter alluded to.

            Oh, and I forgot; I haven't read the new FHB Magazine--I'm a little behind in these parts of the Bay Area, CA.

            Edited 9/25/2003 1:19:59 AM ET by Wiley

          2. BarryO | Sep 25, 2003 10:01am | #8

            Yea, the exception would be the reason not to tap into the 2 dedicated circuits with a lighting load, but there is no general prohibition against attaching lighting to a 20A branch, which is what the article implied.

            Still concerned about the landscape wiring.  There's no assurance that wiring intended for low-voltage direct burial will meet the flame resistance required for in-wall installation.

          3. MisterT | Sep 25, 2003 01:24pm | #9

            My Two Cents,

            I don't know what the code says but...

            I think the gist of the authors comment was that you CANNOT connect a 14ga. circuit (most comonly used for lighting) to a 20amp circuit(12ga.).

            Mr T

            Do not try this at home!

            I am an Experienced Professional!

          4. User avater
            BillHartmann | Sep 25, 2003 06:59pm | #10

            I had a change to read the whole article and feel that it was poorly written, in other areas than this.

            It did not seem to have a focus. More like a Family Handyman Magazine article rather than a "trade" magazine article.

            Now one thing that was not mentioned was fishing the NM. #14 is easier to handle then #12 so he might have gotten in the habit of using that for retro work, BUT that is not what he said.

            And someone else on the forum has said their inspector (I think in the Chiago area) won't allow lighting on 20 amp circuits. I don't know if that is a local rule or just some inspectors odd ideas.

          5. User avater
            DanMorrison | Sep 27, 2003 03:45pm | #11

            Whoa buddy!

            It did not seem to have a focus. More like a Family Handyman Magazine article...

            That's hitting below the belt a little isn't it? I can handle screwing up an arbitrary and hard to read code, but lacks focus? poorly written? Oh man.

            I'm sorry, but you're gonna have to back that up a little bit.

            First we tell you why we're using the system we're using. Then we give an overview of the wiring scheme and talk about dimmers a little bit. There's a drawing illustrating the plan and explaining a little bit about low voltage wiring (bulbs, voltage drop). Then we give a one-page lesson on snaking wire through walls. The installation is very straightforward, as is hooking up the lights. But we go ahead and give a couple of tips on placement (towards the front, run it deep into the corners). Finally, we give the authors favorite system and why. Oh yeah, and as long as we have a photo of wire nuts, we tell the readers a little bit about them.

            Dan MorrisonOne happy assistant editor

          6. User avater
            BillHartmann | Sep 27, 2003 03:54pm | #12

            I think that you made my point.

            "Finally, we give the authors favorite system and why. Oh yeah, and as long as we have a photo of wire nuts, we tell the readers a little bit about them."

            Anybody that is doing this should know enough to use a wire nut and that is part is not needed.

            If there is a new to have a review of different connection systems then that would be worthy of a whole 2 or 3 page article.

            I don't have the article in front of me, but I will try to go over it later.

          7. User avater
            BillHartmann | Sep 27, 2003 09:46pm | #13

            "First we tell you why we're using the system we're using. Then we give an overview of the wiring scheme and talk about dimmers a little bit. There's a drawing illustrating the plan and explaining a little bit about low voltage wiring (bulbs, voltage drop). Then we give a one-page lesson on snaking wire through walls. The installation is very straightforward, as is hooking up the lights. But we go ahead and give a couple of tips on placement (towards the front, run it deep into the corners). Finally, we give the authors favorite system and why. Oh yeah, and as long as we have a photo of wire nuts, we tell the readers a little bit about them."

            Yes, a little bit about this and a little bit about that. What is the focus of the article, select the lights, installing them, proper wiring technics?

            If was about selecting them then it misses a lot of options. There article could just as well said that for this installation I am using XYZ and left more space for other details. Or discussed the different fixture options and left out the wire nuts, for example.

            I was going to complain about the use of "low voltage magnetic dimmers". They are never low voltage or magnetic, but I look a Lutron's catalogs and that seems to be the industry "mis"-terminology.

            But I did find something interesting. A number of the dimmers designed for controlling low voltage circuits do require a neutral. A standard switch leg does not have a neutral. That they would require pulling a 3 wire cable. Now that is the little kind of "gotcha" that would be usefull information in the article.

            You have a "Safety Tip" that say to make sure that the power is off to the box where you are adding the wiring. But at the sametime you are showing running a new circuit to the breaker pannel.

            In my mind those two just don't go together. If they have to bewarned about making sure that the power if off at the box they are should not be adding a circuit to the pannel.

            The paragraph on where to place the transformer and suggested hidding places was good. But then he goes on and discusses the difference between 12v and 24v systems. And talks about "centering" transformer to keep the LV wiring short. Some rules of thumb or design guide lines would have been more usefull here.

            Things don't alwasy work out so nicely where you can put transformer in the center.

            Also he "reused" a box slot where there was a switch for a dishwasher. Now that is an unusally setup. In most cases he would have added a new switch. And that usually entail added or changing a box. Since that is much more likely that should have been discussed.

            The drawing on page 63 indicates taht the transformer is mounted on pressure-treated plywood. I realy don't see that is in the scope of this article. And reason why requires information that is mentioned in the article.

            Aslo the drawing and the discussion indicates that power was run to the transformer and then a switch leg to the dimmer.

            However the picture on page 66 don't show that. (And I maybe wrong, but it does not appear to mounted on PT plywood).

  3. HeavyDuty | Sep 24, 2003 04:00am | #3

    The two sentences

    "...the NEC requires lighting to be on a 15-amp circuit.  [therefore] I couldn't tap into the 20-amp appliance circuits."

    are confusing, they do not relate. PM's explanation was probably the original intention of the auhtor. May be you should ask the auther himself.

    Tom

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Podcast Episode 689: Basement Garages, Compact ERVs, and Safer Paint Stripper

Listeners write in about ventilation and radon control and ask questions about tightening basement garages, ventilation solutions, and safer paint stripper.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Design and Build a Pergola
  • Podcast Episode 689: Basement Garages, Compact ERVs, and Safer Paint Stripper
  • FHB Podcast Segment: Are Single-Room ERVs the Answer?
  • Fire-Resistant Landscaping and Home Design Details

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data