Q: Outlet placement & NEC/State codes

Nuke | Posted in Construction Techniques on March 5, 2006 07:09am

I live in Gwinnett County, Georgia. Yesterday, I was visiting a friend and somehow the discussion got onto basement finishing and being that neither he nor I were licensed electricians wondered about the frequency of and placement allowance for electrical outlets within a home.

So, this morning I go up and noticed that while most electrical outlets in my home are not under a window, I do have a couple that are. Also, the maximum distance between two outlets in the same room without a break in a wall (i.e. a door or window) is nine (9) feet.

Ok, now I know what my county inspectors are like (could use 3X the manpower) and I knew what the builder’s superintendent was like (non-attentive, which is why he was fired after 3-4 years of bad construction), so I wonder about whether any violations in my home were possible.

Anyone working as an electrician in GA know whether or not electrical outlets under a window, and the greatest unbroken wall-run can be between sequential outlets can be?

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    Nuke | Mar 05, 2006 07:37pm | #1

    Ok, NEC says 12' spacing in non-kitchen/bath areas. I Googled it and read from several results to this. Of course, Georgia/Gwinnett county could have amended this to more restrictive condition.

    1. User avater
      BillHartmann | Mar 05, 2006 08:55pm | #4

      Here is a good summary of all of the numbers.http://www.codecheck.com/pg27_28electrical.html#rough

      1. User avater
        razzman | Mar 06, 2006 02:53am | #6

        bill-

        What are they saying about the '44 ft' under the 'cable'...

        [NEC99'] {NEC 2002}

        View Image

        Rough

         

        View Image

        View Image

        Appliances

         

        View Image

        Disconnecting Means

         

        View Image

        Closet

         

         

        View Image

        General-Purpose Circuits

        Receptacles

        View Image

        Cable

        Romex¯ {NM Cable] Not in {Type I or II} buildings [>3 floors except 1- & 2-family} .............................................................................[336-5a1]{334.10} Min. 4in. sheathing into box, max. 1in. . . . . . . . . . .[370-17c], local]{314.20} Protect from physical damage . . . . . .[336-6b][334.15] Nail plate req'd if cable < 14in. to stud face ... F-e13 [300-4a,d] {300.4AD]} Secure <=12in. of box and at least every 44 ft. .[336-18] {334.30} Clamp cable to box with approved clamp, EXC .[370-17b,c]{314.17B,C} No clamp OK if single-gang plastic box & secured <=8in...........................................................[370-17cX] {314.17Cx} Clamp listed for 1 or 2 cables max. {not chase

         

          

         

        'Nemo me impune lacesset'No one will provoke me with impunity

        1. DanH | Mar 06, 2006 03:35am | #8

          I think that's a misprint -- the cable is to be "secured" every 4.5 feet. "Securing" can be done by stapling, running the cable through a hole in a stud or joist, or similar means. An exception is allowed for cables "fished" through enclosed areas.
          If ignorance is bliss why aren't more people

          happy?

          1. User avater
            razzman | Mar 06, 2006 04:36am | #9

            That was my first impression too but I like to ask to be sure. Thanks

             

              

             

            'Nemo me impune lacesset'No one will provoke me with impunity

  2. andy_engel | Mar 05, 2006 07:55pm | #2

    Don't know Georgia, but have a nodding familiarity with the NEC. Yes, outlets can be placed under windows. You're right about the 12 ft. spacing, but you must also have them within 6 ft. of each side of any door. If you've got a big bank of sliders, you may have to add floor outlets to get the required spacing. For those purposes, outlets must be less than 4 ft. from the floor. Also, within 2 ft. (if memory serves) of bathroom sinks, and within 2 ft. of each side of kitchen sinks.

    Andy

    "Never try to teach a pig to sing. It wastes your time and annoys the pig." Robert A. Heinlein

    "Get off your dead #### and on your dying feet." Mom

    1. FrankDuVal | Mar 05, 2006 08:50pm | #3

      The only time you need receptacles in the floor is if the sliders are non-opening, therefore they are large windows. An opening slider is a door, and there needs to be a receptacle within 6 feet of each side of the door. But, there is the any wall wider than 2 feet needs a receptacle. So two sliders with a fixed section of 24" or more between them technically needs a floor receptacle. The kitchen rule is a receptacle within 2 feet of any point along the back splash of a counter top, so yes within 2 feet of the sink, or any other break in the countertop (end, stove, whatever). Also any countertop 12" or wider needs a receptacle.Frank DuVal You can never make something foolproof because fools are so ingenious.

      1. andy_engel | Mar 05, 2006 10:37pm | #5

        Thanks for the clarification.Andy

        "Never try to teach a pig to sing. It wastes your time and annoys the pig." Robert A. Heinlein

        "Get off your dead #### and on your dying feet." Mom

  3. DanH | Mar 06, 2006 03:27am | #7

    One way to envision the basic rule is that you should be able to place a floor lamp with a 6-foot cord (plus a few inches more for slack) anywhere around the perimeter of the room and have the cord reach an outlet (without crossing a doorway). This means 12 feet between outlets, and no more than six feet from doorway edge to the first outlet.

    However, there are all sorts of exceptions -- short walls between doorways don't need an outlet, hallways don't need as many, etc. And of course kitchens and bathrooms have a whole separate set of rules.

    There are no restrictions in the NEC (that I'm aware of) with regard to placing an outlet under a window. In fact, it's always nice to have a "Christmas tree outlet" under or very close to a picture window.

    Of course, state or local authorities can override NEC, and local inspectors can "interpret" the rules in strange ways.

    If ignorance is bliss why aren't more people

    happy?

    1. FrankDuVal | Mar 06, 2006 05:43am | #12

      I like a Christmas Candle receptacle under every window on the front of the house controlled by one switch. But, it is too much money for most customers! And then there is the "why doesn't this receptacle work?" questions the rest of the year!Frank DuVal You can never make something foolproof because fools are so ingenious.

  4. GHR | Mar 06, 2006 05:17am | #10

    There is no requirement for recepts in basements.

    Depending on what you write on the plans for finishing the basement you may or may not have to comply with the 6' rule (as it often is called).

    1. User avater
      BillHartmann | Mar 06, 2006 05:19am | #11

      An "unfinished" basement requires one receptacle. Likewise a garage.

  5. User avater
    Matt | Mar 06, 2006 05:51am | #13

    >> So, this morning I go up and noticed that while most electrical outlets in my home are not under a window, I do have a couple that are. << I'm gonna guess that the house was wired overhead, and placing receptacles under windows would have meant additional drilling for the electrician.  Re the ones that are under a window they may have had to be placed there to satisfy the 6' rule without putting more outlets than the minimum in the room.  That's just a guess.  To get a more definitive answer, you would have to tell us how the floor systems are constructed - 2x10, webbed floor trusses, slab floor crawl space, etc.

    1. DanH | Mar 06, 2006 06:23am | #14

      It should be noted that there's nothing in the code that says you can't have MORE outlets than one every 12 feet. The incremental per-outlet cost is small, and it's often worthwhile to put in a few extras, if you're building for yourself.
      If ignorance is bliss why aren't more people

      happy?

      1. globaldiver | Mar 06, 2006 07:16am | #15

        Boy am I glad to hear you say that!  I'm wiring my shop, and along one wall I have a two boxes every other stud; one at 12" from floor and one at 48".....every other box in the line is a different circuit in case I'm working with more than one tool at a time.....everybody has been giving me cr*p about having so many outlets, but I figured the wall is only going to be open once.....  One of these days I'll get some pictures posted.  --Ken

      2. User avater
        Matt | Mar 06, 2006 03:33pm | #16

        Knowing the code is one thing and I know you put that out there for the general population here at BT.  Knowing how production electricians do business is something else.  The electrician I use charges $35 per outlet extra - the HO gets charged $50.  It's a pretty standard price.  Most HOs will go for it if they want a few extra outlets.   To be fair and build good customer relationships the way I do it is if they want an outlet in a particular spot, we see if we can work it into the 6' rule, 2' rule, or which ever one applies.  If not - they pay.  I definitely have extra outlets in my house - for example, like 6 in the garage including a 220v.

        As far as the way production electricians do business, on a house I recently completed, when they roughed it in they put in a 125a service for a 2000 sq ft house - which I thought was rather skimpy - let me call it cheap - I said something about it and they showed me the numbers where it was more than adequate - never mind there was only 1 slot left in the box...   Then - I got the rough-in bill they had added $225 to the quoted price because the breaker panel was remotely located from the meter base.  I told the head guy that it was on the plans he priced out and I wasn't gonna pay for it.  His response - "OK, fine, we will get it back on the next house"...  Don't get me wrong, this is a good company who is very predictable at meeting their scheduling commitments, very few callbacks, and their prices are good - but they definitely charge for every little thing that is extra.  They crack the whip on their guys too... the lead mechanic on a truck gets any re-inspect fees subtracted from his check...  This company does a large volume of business though, and I can guarantee no man ever goes without a full 40hr week and they get some benefits.

        1. User avater
          Nuke | Mar 06, 2006 03:46pm | #17

          This house is an unfinished basement w/stubs for future plumbing. The ceiling above is comprised of 1.75"x11-7/8" Boise-Cascade I-joists for the house's first floor. I've lived in this thing for ~5 years now. I originally placed boxes for the convenience of the rooms' intended functions. Now, I re-thought about it and decided to make it to, or in excessive, of code. Thinking future-owners, here.

        2. FrankDuVal | Mar 07, 2006 06:21am | #18

          Matt said:
          "As far as the way production electricians do business, on a house I recently completed, when they roughed it in they put in a 125a service for a 2000 sq ft house - which I thought was rather skimpy - let me call it cheap"Wow!!!I have not seen a house built here in central VA with less than a 200 amp panel in over 15 years!!! I have never installed less than a 200 amp panel, even on a barn. Lots of extra pole spaces in that one. Here the POCO supplies the meter base and the wire to the meter base, so the only extra expense for the homeowner is the panel price and service entrance cable (a few feet usually). I have done quite a few 400 amp services, two 200 amp panels, for more pole spaces and heat pump loads. Again, one extra panel and a few feet of service entrance cable (plus labor!).Frank DuVal You can never make something foolproof because fools are so ingenious.

          1. User avater
            Matt | Mar 07, 2006 02:28pm | #19

            I hear ya.  I was shocked.  One thing that may have effected it was that it had gas heat, hot water & range and no garage.    Question: if it had a "gas pack", does that mean the AC runs on gas?  Don't know, and it seems counter intuative, but the house I grew up in had a gas AC unit.

            BTW - I have 400a in my house too.

          2. User avater
            BillHartmann | Mar 07, 2006 04:24pm | #20

            "Question: if it had a "gas pack", does that mean the AC runs on gas? "There where some gas powered absorbtion AC maybe 20 years ago, but I don't think anyone makes then any more or at least they are very, very, very rare.When I hear the term gas pack I think of a heat pump with gas furance as the backup heat.So you would have have the resistive loads that take lots of amps.

          3. User avater
            Matt | Mar 08, 2006 06:40am | #27

            Here is an example of a gas pack:

            http://www.trane.com/Residential/Products/PackagedUnits/GasElectric/PGE_XL1200.aspx

            It is something different than a split system which is what I think you are maybe describing.

            One distinguishing characteristic of what we call a Gas Pack is that there is no indoor equipment.  The large "packaged unit" sits outside next to the foundation and there is a large hood that covers the supply and return trunk lines as they go through the foundation.  I guess you are right though - the AC is electric, although I don't really know if it would be classified as a heat pump - as far as I know, the heat is always generated by burning gas. 

          4. User avater
            BillHartmann | Mar 08, 2006 07:34pm | #28

            Those particular units appear to be just furnace/AC and I see that they offer similar packaged heatpumps.Does not appear that they do offer packaged heat pumps with gas backup. But there if the can package a gas furnace/AC there is no technical reason that could not offer heatpump with gas backup. Probably just not enough market. For splits it is easier to mix and match.

          5. User avater
            Nuke | Mar 07, 2006 04:47pm | #21

            Securing Cable et al

            Ok, so I have to secure the cable when said cable comes within 12" of a box. I take this to mean an outlet, switch, or ceiling recepticle, correct? And the interpretation is that between boxes (runs) ~4.5 feet? I did not notice whether or not there are reccommendations for methods of securing outside of staples and other such metal, or part-metal, fasteners. What crazy things have others been using outside of staple-ish like fasteners?

            Also, I noticed that HD sells boxes called 'Old Work'. These are of a design in which they are not fastened to a stud. These are not LV boxes, either. I spoke to someone last night and he used them in new work (basement, I think). So, if someone just make wire drops to the bottom of their stud-cavity box location and drywalls over and then cuts out tight openings later with the intention of using these Old Word boxes is this actually an accepted practice?

            Also, just because Home Depot sells something does that mean the local authorities are accepting of it in use? It made me wonder if someone like HD could be ordering stuff on a large scale and accidentally ships to some stores where local code prohibits use of such a product.

            BTW, these Old Word boxes use four screw points with tabs on them. When you turn the screws the tabs stand up. As you continue to screw the screws on these tabs the leading edges of the tabs apply force on the backside of the drywall. Surprised me when I first ran across them in the store--especially since up until yesterday I hadn't known a soul that used them.

          6. User avater
            BillHartmann | Mar 07, 2006 05:39pm | #22

            Old work boxes are old. Been around long before HD every came along.But I have never seen one with 4 tabs. All of the common rectangular plastic boxes that I have had 2 tabs. Round ceilign boxes 3. There is also a low voltage version that is the same, but does not have a back, it is just a sleave.There are alos metal and maybe plastic ones with metal bat wings on the side. You squeeze then to get in to the hole and then there is a scew in the back that you tighten to draw up the wings against the DW.There are also madison (battleship) clips that can be added to any box that has ears. I could not find a picture, but it is a stamp metal device with 4 fingers. two slip behind the DW and the other two are bend around the box. One goes on each side of the box.Now the NEC is only 1/2 of the code. It also requires you to use APPROVED MATERIALS and follow MANUFACTURES INSTRUCTIONS.So to get the complete story you need to go through the UL specs and approval lists.But my guess is that all of the old work boxes the plastic "trap doors" on the plastic boxes where cable goes through meet the requirement of clamping the cable near the box.

          7. DanH | Mar 07, 2006 06:03pm | #23

            As was stated earlier, the code makes an exception to the fastening rule for "old work". It's probably up to the inspector, though, whether one can invoke the "old work" exception in a newly constructed or remodeled area.In the case where cables are dropped into the walls and terminated later, they still should be fastened to the studs at appropriate intervals to near the point where the box will eventually be.

            If ignorance is bliss why aren't more people

            happy?

          8. DanH | Mar 07, 2006 06:04pm | #24

            Also, because HD or Lowes or even the local HW store sells something does not mean it's acceptable to local authorities. And because the salesmen there say it's OK does not meant that it really is.

            If ignorance is bliss why aren't more people

            happy?

          9. FrankDuVal | Mar 08, 2006 06:16am | #26

            Nuke,If you are getting the basement inspected, I doubt the inspector will pass rough-in electrical with the romex hanging in all the stud bays for receptacles. They do pass hanging romex for wall sconces! ( at least around here). The grounds need to be made up for rough-in, so only single romex hanging usually passes.Double gang old work boxes have four swing tabs on them. I use this style all the time on remodel work. You can get really tight sheetrock fits with them! Plaster walls are a little tougher but do-able.Staples need to be approved for the application. No wire fence staples or bent nails. I do use the cable stackers sold by 3M and others to run three plus wires along a stud. Others:
            What do you use to fasten romex to the side of a metal stud? I haven't had the pleasure to work with metal studs except exposed work with conduit. I know about the plastic bushings for the holes through the studs. Some of those black cable stackers screwed to the stud? I've heard metal studs are the "cat's meow" for basement remodeling.Frank DuVal You can never make something foolproof because fools are so ingenious.

        3. User avater
          Soultrain | Mar 07, 2006 06:17pm | #25

          "they put in a 125a service for a 2000 sq ft house"

          It all depends on what's in there.  If they are running gas appliances, they likely will never come close.

          I put a 200A service in my house (2700 sq ft) - mainly because I forsee adding a shop in the back yard some time in the future.  When I ran the numbers to apply for my permit, it worked out to 75A, so I could have got away w/ a 100A service if I were so inclined.

          Most houses today - even ones in small lots where there is no place for out buildings - get 200A service because the HO will fall over w/ anything less than that.  A friend of mine (who is an electrician) lives in a house that is total electric (including electric baseboard heat).  He has a 100A service with no trouble at all.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Vintage Sash Windows Get an Energy-Efficient Upgrade

Low-e storm panels improve the energy efficiency of these old sash windows without changing their classic look.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • From Victorian to Mid-Century Modern: How Unico Fits Any Older Home
  • Designing the Perfect Garden Gate
  • Vintage Sash Windows Get an Energy-Efficient Upgrade
  • Design and Build a Pergola

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data