JonBlakemore | Posted in Tools for Home Building on March 5, 2003 07:38am

Had a discussion with a fellow worker the other day.  Running of a generator, the skil saw was taking some time to wind up.  50′ 12 ga. supply, with a 3 way and another 50′ 12 ga. cord.  I don’t think that is an excessive amount of length and ga. to run one tool.  We were commenting on the matter, and he said that there is probably 300′ of cord total off of the generator (some cords were vacant, others were plugged in to tools but not on at the moment).   His claim was that, regardless of whether a cord is supplying a running tool or not, all those cords add to voltage drop.  I think that the electrons will run from positive to ground in the most direct route.  Who is correct? 

 

Jon Blakemore
Reply

Replies

  1. Steve1 | Mar 05, 2003 09:08pm | #1

    voltage drop in a cord depends only on the tools actually running at the time and of course the length of the cord

    your slow windup time may be dependent on the generator too, it senses a load and powers up, all takes a few seconds

    most electric motors take far more current to start up than run even under the heaviest load

    used to use a craftsman tablesaw years ago that actually would not start with a 50 foot14ga cable

    had to start by spinning the blade by hand!!! my high school shop teacher im sure would cringe and cancel my diploma

    1. JohnSprung | Mar 06, 2003 03:29am | #3

      I have the same kind of thing with the new 2 HP motor on my Unisaw.  If I just hit the switch, it'll blow a 30 amp fuse, so I had to make a starting cam, like on a hand crank car, and I spin it up with a drill motor to keep the surge down.

      -- J.S.

      1. MarkH128 | Mar 06, 2003 06:25am | #4

        Put 60 amp fuses on it. Fuse wont blow anymore.

        1. Steve1 | Mar 06, 2003 06:31am | #5

          i hope that was a joke mark!!

          1. MarkH128 | Mar 06, 2003 06:40am | #6

            Spinning up a unisaw with a drill is a joke too. Yeah I was jokin'.

          2. FrankB89 | Mar 06, 2003 08:52am | #7

            OK, here's something somewhat unrelated, but a true story that will chill your blood...

            I worked in big old-growth Doug Fir sawmills for a number of years.  The primary breakdown saws were 10' double cut bandmills where the logs were canted up and the cants were transferred to the next machine...an "edger" which contained a gang of large circular saws which could be independently set to slice up a cant up to 12" X 72" X 40'.

            The arbor shaft in such an edger is massive...6" dia. and about 8' long and powered by 200+ HP electric motor.   The arbor is supported by and spins in large roller bearings.  The bearing on the end away from the motor is mounted on a "door" and the whole assembly is held in place by a large arbor nut (3" left-hand threads).

            To change the saws, the arbor nut is usually removed with a big socket on a rattle gun, but when the saw change is complete, the arbor nut is usually tightened manually with the same socket on a 1"  Proto breaker bar.

            One morning as the mill was starting the first shift, the filers had completed the edger saw change and had tightened the arbor nut....but neglected to remove the socket and breaker bar which were left hanging on the nut.

            The sawmill foreman, a rather portly gentleman, was standing on a catwalk directly above the edger.  When the operator started the machine, the breaker bar flew off at high velocity and buried itself clear past the length of the handle knurling (about 6") in the foremans chest.  He went down like he'd been pole-axed,  suffered a collapsed lung and several broken ribs.

            Happily, he survived, but that breaker bar with the bloody handle hung in the office untill the mill closed a few years later.  (It was stated by his doctor that a man with less "padding" would not have survived).

             

            Edited 3/6/2003 12:55:16 AM ET by Notchman

          3. CAGIV | Mar 06, 2003 09:17am | #8

            OUCH!View ImageGo Jayhawks

          4. MajorWool | Mar 07, 2003 03:26am | #12

            That is exactly how a T-handled wrench flies off the chuck in a metal lathe. The first rule of safety is that it is never left in the chuck, ever.

          5. JohnSprung | Mar 07, 2003 02:43am | #10

            Well, they don't make 60 amp screw-in fuses....  ;-) 

            The reason for this is that until I get cut over to the new service, all I have is a 30 amp two wire 120 volt services that's been there since 1926.  This drill motor and cam as pony motor arrangement is amusing, but for now it gets the job done.

            -- J.S.

          6. User avater
            BillHartmann | Mar 07, 2003 07:27pm | #17

            John

            They make 60amp pennies <G>.

      2. junkhound | Mar 06, 2003 10:33am | #9

        John, is that the motor discussed on a previous thread, the 120/240 model you have to run on 120V?

        1. JohnSprung | Mar 07, 2003 02:45am | #11

          Yes, it's the same one. 

          -- J.S.

          1. junkhound | Mar 07, 2003 05:36am | #13

            Only possible "in-code" help I could suggest for your 2 HP motor would be to put a 3-5 uF AC run type capacitor across the line just after the switch, that will help reduce the current during startup (and running) by improving the PF - if you want to try it and have a box to put it in (about 4" by 6" by 4"), e-mail me and I'll mail you a couple of surplus ones to try.  

            Of course, a penny under the fuse is still unacceptable <G>.

          2. JohnSprung | Mar 11, 2003 03:41am | #18

            Thanks.  I finally found my box of big capacitors over the weekend, the smallest I have is 10 uF, would that be OK to try?  BTW, my BIL is also looking for a 25 uF 370 VAC, which I also don't have in the junk box.  Any leads on a good source?

            Thanks again --

            -- J.S.

  2. TKanzler | Mar 05, 2003 09:45pm | #2

    Sorry, but your coworker is wrong and steve is right.  You've got about 200' of 12 gauge wire (100' out and 100' back), which, at about 2 ohms per 1000', is .4 ohms, plus the resistance of the connections and the saw cord.  With a 40A startup wallop (just a WAG at locked-rotor), that's about a 13% voltage drop.  And that's assuming the generator can even provide that much current for startup, and that it's running full-speed already.  Sounds perfectly reasonable that the saw starts a bit slower than with a shorter cord of the same gauge.

    Be seeing you...

    1. User avater
      JonBlakemore | Mar 07, 2003 06:49am | #14

      40a startup?  I thought the max Amperage figures on tools were for startup and high load times.  Could a skil saw really draw 40a? 

      Jon Blakemore

      1. MarkH128 | Mar 07, 2003 07:13am | #15

        The nameplate amps is at full rated load. The locked rotor (startup) current draw is considerably more, maybe 40 amps or more. Thats why there is a blink on your lights when you click the trigger on the saw.

      2. TKanzler | Mar 07, 2003 04:39pm | #16

        They don't nameplate locked-rotor codes on universal motors, so 40A was an educated WAG, but I just happen to have certification data sitting on my desk for a 3 hp Marathon (induction) motor, like what's used on a Unisaw.  While the full-load current (FLA) is 12.4A at 230V, the locked-rotor current is 93.1A.  It would be 186.2A (!) if it could be configured to run on 115V, while only drawing 24.8A under rated load.  Induction motors have a kVA code, or locked-rotor code, on the nameplate, which is used to calculate the approximate inrush current.  

         Code Letter

         kVA/hp Range 

                 A

         0.00 - 3.14

                 B 

         3.15 - 3.54

                 C

         3.55 - 3.99

                 D

         4.00 - 4.49

                 E

         4.50 - 4.99

                 F

         5.00 - 5.59

                 G

         5.60 - 6.29

                 H

         6.30 - 7.09

                 J

         7.10 - 7.99

                 K

         8.00 - 8.99

                 L

         9.00 - 9.99

                 M

         10.00 - 11.19

                 N

         11.20 - 12.49

                 O

         12.50 - 13.99

                 R

         14.00 - 15.99 

        For single-phase motors, multiply the code letter value x hp x 1000, and divide by nameplate voltage (generally 115V or 230V).  So a 1.5 hp motor with "B" in the Code spot on the nameplate would draw 3.15 X 1.5 x 1000 / 115V = 41A minimum on startup, and up to 46A at the high end. 

        I seem to recall that Delta's contractor saw with the dual-hp motor had much higher code letter(s); two code letters because it's really a 2 hp, nameplated at 1.5 hp for 115V service, but the locked-rotor current works out to be twice as high at the lower voltage (they need the higher code letter at 115V to adjust for the lower nameplate hp, since it's really a 2 hp at either voltage).Be seeing you...

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Speedy PEX Expander

The M12 ProPEX expander from Milwaukee is the fastest expanding tool.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Convert a Porch to a Mudroom
  • Podcast 599: Trees Moving Buildings, Epic Thermal Bypasses, and Supplemental Dehumidification
  • Podcast 599: Members-only Aftershow — Tools That Changed Residential Construction
  • Remodeling Done Right

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • Code Check Complete 3rd Edition
    Buy Now
  • 2022 Fine Homebuilding Archive
    Buy Now
  • Pretty Good House
    Buy Now
  • 2023 Tool Guide
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 318 - October 2023
    • Make Mudsills Square and Level
    • Turn Up the Heat With Induction Cooktops
    • The Fine Homebuilding Interview: Lloyd Alter
  • Issue 317 - Aug/Sept 2023
    • Finishing Drywall With Seamless Results
    • A Flat Roof in a Cold Climate
    • Compact Cordless Shop Vacs
  • Issue 316 - July 2023
    • Timber-Framed Solar Canopies
    • Build a Transom Above a Stock Door
    • Understanding Toilet Design and Efficiency
  • Issue 315 - June 2023
    • How to Craft a Copper Roof
    • 5 Lessons from Building in a Cold Climate
    • The Advantages of Cellular PVC Siding
  • Issue 314 - April/May 2023
    • 7 Options for Countertops
    • Tool Test: Wood-Boring Bits
    • Critical Details for Ductless Heat Pumps

Fine Homebuilding

Follow

  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok
  • twitter

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok
  • twitter

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in