breaker box – add a grounding buss bar
rezajohn | Posted in General Discussion on February 13, 2008 07:41am
homeowner, amateur home electrician; Do I isolate an add on grounding buss bar to the metal breaker box with non metallic spacers; or do I just fasten the buss bar to the inside of the breaker box with a few machine screws?
  1. JTC1 | Feb 13, 2008 03:55pm | #1
    There are usually threaded holes already in the box to accomodate the ground buss bars from the manufacturer.
    Add-on ground bar is screwed directly to the panel box.
    In the main service entrance panel, the neutral bar is also bonded to the metal panel box - either by a screw or a small rod.
    In a sub-panel, in the same building: the ground bar is still attached directly to the metal panel box. BUT, the neutral bar is isolated from the metal box by removing any bonding screws / rods / bars.
    Service entrance panel -- ground and neutral are both bonded to the metal panel box. Continuity exists between panel box, ground bar, neutral bar, and ground rod or ufer.
    Sub panel in same building -- neutral bar is isolated from the metal panel.  Ground bar is attached directly. Continuity exists between ground bar and box. Neutral "floats" within the panel box.
    Jim