Calculating draw 220A circuit Question

rjw | Posted in Energy, Heating & Insulation on October 6, 2009 10:03am

I just want to confirm that for an 220/240v electric water heater which draws 4500 watts, max (upper or lower, they don’t operate at the same time), to calculate the draw on either leg I’d divide 4500 by 220 and get 20.5 amps per “leg.”

 

 


“Man’s capacity for justice makes democracy possible, but man’s inclination to injustice makes democracy necessary.”
Reinhold Neihburh: ‘The Children of Light and the Children of Darkness’


http://rjw-progressive.blogspot.com/

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Clewless1 | Oct 06, 2009 10:43pm | #1

    good question. Total draw will be the 4,500 watts total amps is 20.5 amps. Is this per leg or just simply the total.  Check out the couple of examples at this site.

    http://www.ehow.com/how_5328646_calculate-amperage-draw.html

    Don't know if this answers your question, but why are you concerned about e.g. 'per leg' amps rather than just amps?

    1. User avater
      rjw | Oct 08, 2009 02:26am | #13

      >>but why are you concerned about e.g. 'per leg' amps rather than just amps?I was just having a brain fart: 4500 watt water heater on 2 30 amp breakers

      "Man's capacity for justice makes democracy possible, but man's inclination to injustice makes democracy necessary." Reinhold Neihburh: 'The Children of Light and the Children of Darkness'http://rjw-progressive.blogspot.com/

  2. junkhound | Oct 07, 2009 12:32am | #2

    yes,

  3. WayneL5 | Oct 07, 2009 03:57am | #3

    Yes.  All the current flows through both legs, so 20½ amps flow in one leg and out the other.

    1. DaveRicheson | Oct 07, 2009 12:53pm | #7

      , so 20½ amps flow in one leg and out the other.

      Huh?

      Resistive load, two hot legs.

      Better reword that statement.

       

      1. User avater
        SamT | Oct 07, 2009 01:48pm | #8

         so 20½ amps flow in one leg and out the other.

        Huh?

        Resistive load, two hot legs.

        Better reword that statement.

         

        I don't get it! What's the problem?SamTA Pragmatic Classical Liberal, aka Libertarian.

        I'm always right! Except when I'm not.

        1. DanH | Oct 07, 2009 03:18pm | #9

          It should be in one ear and out the other.
          As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

        2. DaveRicheson | Oct 15, 2009 02:44pm | #19

          240v

          Two hot legs ( goes innies).

          One nuetral (goes outie).

          277v

          One hot leg (goes innie)

          One nuetral (goes outie)

          1. DanH | Oct 15, 2009 02:48pm | #20

            If 20 amps is flowing through both hots, the neutral current is zero.
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          2. DaveRicheson | Oct 15, 2009 10:35pm | #22

            yer right

          3. BoJangles | Oct 15, 2009 02:57pm | #21

            240v

            Two hot legs ( goes innies).

            One nuetral (goes outie).

            There's no neutral on his water heater tho.......

             

          4. DaveRicheson | Oct 15, 2009 10:42pm | #23

            yer right too. the white wire is generaly attached to the ground screw.

            point I was trying to make is that with two hot wires  supplying a WH one of then can't be returning current to the source. try that and you'll buck phases and let the smoke out of the breaker, bus and whatever else it can get out of.

          5. JTC1 | Oct 15, 2009 11:18pm | #24

            >>...try that and you'll buck phases and let the smoke out of the breaker, bus and whatever else it can get out of.<<

            What am I missing.......

            Every 240v HWH I have ever seen (or connected) was connected one of 3 ways.

            "Modern" Romex (meaning with ground):

            x-2 Romex (usually 10-2 w/ground) to 2 pole breaker - connections at breaker box = black to 1 pole of breaker, white to other pole of breaker (good jobs will be recoded black or red, but not always); bare ground to ground buss (in a sub-panel) or neutral / ground buss in a SEP.

            At HWH : black to L1, white to L2 terminal; bare to frame or ground screw.

             

            "Old" Romex (meaning no ground conductor within the cable):

            x-3 Romex (again generally, #10)- connections at breaker panel = red to one pole of breaker, black to the other plole of breaker; white to neutral buss.

            Connections at HWH = red to L1, black to L2 (or vice versa); white to frame.

            OR

            x-2 Romex (usually 10-2) to 2 pole breaker - connections at breaker box = black to 1 pole of breaker, white to other pole of breaker.

            Black and white connected to L1, L2 at HWH; sometimes a ground wire run from the frame to a cold water pipe (but not always, and usually poorly connected if present at all).

            No neutral conductor present.

            JimNever underestimate the value of a sharp pencil or good light.

          6. DaveRicheson | Oct 16, 2009 12:54pm | #32

            The original response was made to the remark that current came in on one wire and out on the other.

            Now how does that make sense if both L1 and L2 are hot?

          7. DanH | Oct 16, 2009 03:06pm | #33

            Because it's true. Electricity can't go in unless it's also coming out (at least not at normal voltages). When electrons are going in one wire they're coming out the other. 1/120th of a second later the direction reverses.
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          8. JTC1 | Oct 16, 2009 04:24pm | #34

            Not a licensed electrician, or an electrical engineer.  But do have plenty of "mechanical" or "practical" experience with residential electricity, and my work has an excellent track record of functioning reliably and has passed several hundred inspections, for myself and customers.

            Here is my rudimentary, "practical" understanding / interpretation of how current flows in a 240V circuit, like this water heater:

            >>that current came in on one wire and out on the other.

            Now how does that make sense if both L1 and L2 are hot?<<

            Remember, the following is just my "practical" or "mechanical" understanding; namely a "pure" 240vac device does not require a neutral but, a combination circuit such as a stove with a timer, lights, etc. does require a neutral to return the power from the 120v devices only.....

            A wire carrying Alternating Current (AC) is not "hot" 100% of the time, in reality it turns on and off at a rate of 60 times per second (frequency). ON-OFF-ON-OFF-ON-OFF, etc., making it "hot" only 1/2 of the time.

            In a 120V line, this means that the "hot" is only energized 1/2 of the time, and the neutral is only "returning" current 1/2 of the time.

            This alternating pattern allows a "shared neutral" circuit with 2- 120V breakers on opposite phases to share a single neutral wire (and not overload that shared wire, it can/will overload the neutral if both breakers are on the same phase). Breaker #1 returns through the "shared" neutral wire, then breaker #2 uses the same wire to return. So the source breaker that returns through the single neutral wire forms a pattern of returns that look like 1-2-1-2-1-2-1, etc.

            If there is a load on only one of the breakers connected in a shared neutral circuit then the "shared" neutral wire carries a pattern which looks like 1-0-1-0-1-0.... or, 2-0-2-0-2-0 etc. If a load is applied to the other breaker in the shared neutral circuit, then the pattern of "returns" goes back to 1-2-1-2-1-2 etc.

             

            Long ago, it was explained to me, that in a "pure" 240V circuit (like a HWH with no 120v loads on either leg), the above alternating pattern allowed the power from one pole of the double pole breaker (L1) to return through the conductor connected to the other pole of the breaker (L2). Thus eliminating the need for a neutral(s) in the circuit.

             

            This "practical" explanation may be completely incorrect, but from a "mechanical" installation standpoint - it works everytime, and the resulting connections never raise the eyebrow of the inspector dejour........

            Edumacation / correction welcomed!

            Jim

             Never underestimate the value of a sharp pencil or good light.

          9. DanH | Oct 16, 2009 07:04pm | #35

            More or less correct, but it should be noted that the same thing would occur on a DC circuit, if, for example, one "hot" was +12V and the other "hot" was -12V. No requirement for AC, simply the requirement that voltage between the two wires is twice what the voltage would be between "hot" and neutral/ground.We could go on to explain how there's no real requirement for a neutral or ground per se in an electric power system, just a difference in voltage between two wires. But that would probably just confuse things in this case.
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          10. PeteBradley | Oct 16, 2009 07:39pm | #36

            Your explanation is pretty shaky and I'm not sure you should be passing it on. For starters, voltage in both legs varies as a sine wave, not on and off. In single phase 240, the sine wave of one leg is the inverse of the other, so they add to deliver the higher AC voltage.

            Edited 10/16/2009 12:44 pm ET by PeteBradley

          11. JTC1 | Oct 16, 2009 08:26pm | #38

            >>Your explanation is pretty shaky and I'm not sure you should be passing it on.<<

            I 'splained it was rudementary, "practical", "mechanical", and possibly totally incorrect. Added the disclaimer that I was not a licensed electrician or EE........

            Where were you when the question was asked?

            Do you really think the question was asked by someone who will understand sine waves?

            I'm not sure I do, thanks for the edumication which will require more research on my part.

            Sorry,

            Jim

            Never underestimate the value of a sharp pencil or good light.

            Edited 10/16/2009 1:29 pm ET by JTC1

            Edited 10/16/2009 1:40 pm ET by JTC1

          12. PeteBradley | Oct 16, 2009 10:11pm | #40

            Why post something that you think is "possibly totally incorrect"? How about letting people who actually know the answer respond instead?

            Edited 10/16/2009 3:13 pm ET by PeteBradley

          13. JTC1 | Oct 17, 2009 12:04am | #41

            I would say you are just about a day late to the party.......

            Suggest you re-read the entire thread, start paying especially close attention at post xx.24 from Dave; that would be this one:

            >the white wire is generaly attached to the ground screw.

            point I was trying to make is that with two hot wires  supplying a WH one of then can't be returning current to the source. try that and you'll buck phases and let the smoke out of the breaker, bus and whatever else it can get out of.<

            Think about how well / safely the wiring installation he describes will function.

            What will happen when the breaker is thrown to "on"? How long will it remain "on" with that white wire connected to the ground screw? Assuming the breaker does not trip, what happens if there is a puddle on the concrete floor that the installer happens to be standing in and touches the frame of the water heater?  Lacking 2 hots at L1 and L2, will the heater perform well? At all?

            Now note xx.25 where I described the mechanics of wiring a 240v residential water heater, 3 different scenarios which I have seen. No theory presented, mechanics of proper installation are flawless. 

            Pay close attention again when you get to xx.33 where Dave is obviously still confused.

            Note that by this time other posters are backing me up in my conversation with Dave.

            You have already responded to my xx.35 post where I presented my rudimentary, "practical" understanding of 240 current flow. Theory shaky, mechanics still flawless.

            >Why post something that you think is "possibly totally incorrect"?<

            Because my post xx.35 dealt strictly with electrical theory, not installation mechanics, and nobody else was coming up with an answer - you hadn't posted yet!

            Keep in mind this is a construction forum, mechanics are quite possibly more important than the "perfect" theory behind a statement.  Disclaimers like I posted are fairly normal here - "not a licensed electrician or EE", "practical", etc.

            To the guy in his basement attempting to connect his HWH, accurate, safe, code-compliant, mechanical guidance are probably more important than perfect theory presentations. I try to help when I can, and frequently include disclaimers.

            >How about letting people who actually know the answer respond instead?<

            You did, and presented good, though somewhat sketchy information, but you were a day late to the party.

            So, please explain, how would the fact that current varies by sine wave rather than on-off (as I incorrectly described) affect the safe installation of the water heater? Could Dave finally figure out that a separate neutral conductor was not required from the information which you supplied?

            Get my point?

            Jim

             

             Never underestimate the value of a sharp pencil or good light.

          14. PeteBradley | Oct 17, 2009 02:02am | #43

            There are lots of folks on BT who can explain how to safely install a water heater without getting into guesswork about how A/C works. My comment about a sine wave was directed to you not the original poster.I've taken this as far as I'm going to, so feel free to have the last word if you must. Maybe you can even put in a bunch of disclaimers about how it could be totally bogus but you expect people to read it anyway.

          15. User avater
            BillHartmann | Oct 17, 2009 03:46am | #44

            "For starters, voltage in both legs varies as a sine wave, not on and off. In single phase 240, the sine wave of one leg is the inverse of the other, so they add to deliver the higher AC voltage."That is not entirely correct either.The problem is that the terms voltage, hot, neutral, supply, return, and phase are all RELATIVELY.Voltage is only meaningfull as a measurement between TWO POINTS. Often the 2nd (reference point)is implied and everyone knows what that reference point is and understands what is being said. However, when that "reference" gets confused then we end up with a thread like this.Now PHASE gets even more confusing.Phase is the time or angular difference between ONE signal measured to it's reference and a SECOND signal measured to the same reference.Now the water heater is a 240 volt load that connects to 2 power wires. There are ONLY 2 wires. So one of them is a reference. But thee is only ONE SIGNAL and thus phase has no meaning.The water heater does not know if it is hooked to a split 240 single phase system, 240 system (with out without one side ground) as in England, a 3-phase 240 delta with one side center taped or even a grounded corner 240 delta with the load between the two high legs.In all of those cases the WH sees 240 between the 2 terminals and with only 2 connections phase is meaningless..
            William the Geezer, the sequel to Billy the Kid - Shoe

          16. DanH | Oct 17, 2009 04:53am | #45

            > In all of those cases the WH sees 240 between the 2 terminals and with only 2 connections phase is meaningless.However, if you have two hots and neutral then phase is VERY meaningful.
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          17. WayneL5 | Oct 17, 2009 05:22am | #46

            Here's another explanation that might be helpful in clarifying this for some readers.

            In a 240 volt system, power is provided to the main panel through three conductors --  two hots and one neutral.  The neutral is connected to ground in the panel.  We'll call ground zero volts.  Because the neutral is connected to ground it is also at zero volts in the panel.

            One of the hots is 120 volts "above" zero and the other is 120 volts "below" zero.  So the voltage between either hot and neutral/ground is 120 volts.  Between the two hots is 240 volts -- they are in effect 240 volts apart.

            So an appliance that requires 240 volts is connected between the two hots.  An appliance that requires 120 volts is connected between either hot and the neutral.  To supply 240 volts a neutral is not needed and some 240 volt appliances don't even have a connection for a neutral.  Other 240 volt appliances use dual voltage, for example, a stove may use 240 volts for the heating elements but 120 volts for a light and clock.  Wiring for such appliances includes a neutral.  Internally the heating element would be connected to the two hots, and the light and clock would be connected between one of the hots and the neutral.

            In a 120 volt circuit the current travels through the hot, the appliance, and the neutral; the hot and neutral carrying equal current.  In a 240 volt circuit the current travels through one hot, the appliance, and the other hot; both hots carrying equal current.  In a 120/240 volt appliance the current travels through all three conductors.  One hot carries the full current, the other hot carries less, with the difference being carried by the neutral.  The current of the higher amperage hot always equals the sum of the currents in the neutral and the other hot.

          18. JTC1 | Oct 17, 2009 05:07pm | #47

            Thanks, nicely done.

            This mechanic understood every word!

            JimNever underestimate the value of a sharp pencil or good light.

          19. DanH | Oct 16, 2009 01:10am | #25

            > point I was trying to make is that with two hot wires supplying a WH one of then can't be returning current to the source. try that and you'll buck phases and let the smoke out of the breaker, bus and whatever else it can get out of.Kirchhoff's spinning in his grave.
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          20. excaliber32 | Oct 16, 2009 01:24am | #26

            Why would it need to at 240v?

          21. DanH | Oct 16, 2009 01:25am | #27

            Why would WHAT need to be 240V?
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          22. excaliber32 | Oct 16, 2009 03:02am | #28

            I've never seen a water heater with a neutral.

          23. DanH | Oct 16, 2009 03:04am | #29

            Doesn't need one, since the current through the neutral would be zero.
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          24. brucet9 | Oct 16, 2009 05:57am | #30

            I've never seen a WH with a reverse, for that matter. :)BruceT

          25. gfretwell | Oct 16, 2009 06:37am | #31

            A water heater with reverse is called a water cooler.

      2. WayneL5 | Oct 08, 2009 12:46am | #10

        No rewording needed.  It is correct.

        1. junkhound | Oct 08, 2009 02:02am | #11

          in one leg and out the other

          Only for 8.3 ms or so, then it is out one leg and in the other <G>

           

  4. JTC1 | Oct 07, 2009 04:20am | #4

    Correct formula, wrong number plugged in....

    4500w divided by 240v = 18.75 amps

    "220" is a common misnomer for 240v. As is "110" is for 120v.

    Only your volt meter knows for sure.

    Jim

    Never underestimate the value of a sharp pencil or good light.



    Edited 10/6/2009 9:22 pm ET by JTC1

    1. User avater
      rjw | Oct 08, 2009 02:24am | #12

      In my area, voltages run on he low side for 120/240, and I figured I'd use that lower figure to build in a little leeway in he calc.

      "Man's capacity for justice makes democracy possible, but man's inclination to injustice makes democracy necessary." Reinhold Neihburh: 'The Children of Light and the Children of Darkness'http://rjw-progressive.blogspot.com/

      1. DanH | Oct 08, 2009 02:30am | #14

        But, unlike a motor, the current through a resistive heating element doesn't go up as the voltage goes down. The current at 220V will be LESS than the current at 240V.
        As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

        1. User avater
          rjw | Oct 16, 2009 08:08pm | #37

          >>But, unlike a motor, the current through a resistive heating element doesn't go up as the voltage goes down. The current at 220V will be LESS than the current at 240V.

          Thanks - I was actually just trying to be conservative (high) as to how many amps the unit draws -

          4500W/220V=20.45A

          4500/240V=18.75.

           

          "Man's capacity for justice makes democracy possible, but man's inclination to injustice makes democracy necessary." Reinhold Neihburh: 'The Children of Light and the Children of Darkness'http://rjw-progressive.blogspot.com/

          1. DanH | Oct 16, 2009 08:39pm | #39

            Right, but the power of the heating element is figured at 240V, so there's no need to "pad" that number. You do need to be wary of drawing too much for a given breaker -- 85% I believe is the rule for "mixed load" circuits, but I think it might be different for a fixed load like a water heater. And you need to be wary of using too large of a breaker, as the heater is designed with the expectation that it will be protected by a breaker of the appropriate size, and may be unsafe with a larger one. (The wiring, of course, can be safely oversized up until the point where it no longer fits in the connections, but the breaker still should be no larger than what the device "expects".)
            As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

          2. User avater
            BillHartmann | Oct 17, 2009 12:56am | #42

            It is 80% and that is for any "continuous" load and that is defined as being 3 hrs or more.At one time I thought someone said that water heaters where called out specifically as not being continuous. But either that person was wrong or I remembered wrong or they change the code since then. But I found it a couple of years ago and it code does specifically call out WH as needed a 20% derating on breaker and wiring.

            .
            William the Geezer, the sequel to Billy the Kid - Shoe

      2. JTC1 | Oct 09, 2009 05:54am | #15

        "Low voltage"....Reasonable, but you will still end up with #10 wire and 30A breaker.

        JimNever underestimate the value of a sharp pencil or good light.

    2. 6bag | Oct 09, 2009 04:24pm | #16

      220, 221 what ever it takes.

      1. DanH | Oct 09, 2009 04:28pm | #17

        What was that from??
        As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

        1. gfretwell | Oct 09, 2009 07:04pm | #18

          Mr Mom

  5. gfretwell | Oct 07, 2009 04:50am | #5

    That is the amps through one element and they are interlocked by the top thermostat so only one is on at a time.
    Dr Kirchoff says the amps through one leg will be the same on the other. It is a rated 4500w load @ 240v so it is 18.75a. If you only had 230 or 220v the amps would be less. (the resistance didn't change)

    1. junkhound | Oct 07, 2009 05:53am | #6

      amps would be less...

      whoa there, remember this was posted by BOB!  He is a constant power load<G>

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Shoulder Your Buckets

Add a strap for easy carrying and pouring when working with 5-gal. buckets.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Ramon Martinez, Site Supervisor
  • What Size Nails?
  • Stop Ice Dams When Reroofing
  • Outdoor Lighting

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data