Continuous beam or segmented
carloa007 | Posted in General Discussion on November 21, 2008 06:50am
Need to install a beam in an existing 2×6 load bearing wall 18′ long.
Debating between continuous or segmented beam.
Segmented allows for removing 6 foot sections of the wall at a time and framing in the new post and beam and covering from elements before moving onto next section.
Continuous requires more man power but only have to perform the operation once instead of 3 times.
Suggestions?
  1. user-201496 | Nov 21, 2008 07:19pm | #1
    What is a segmented beam?
      carloa007 | Nov 21, 2008 07:55pm | #2
      beams that stop midspan on a post. I call them segmented in that they are not continuous, but break at a point and another beam section continuous from there to next post.
      1. user-201496 | Nov 21, 2008 08:50pm | #5
        If you decide to bear the beams on a post make sure that you have adequate support below the post down to the foundation.
    xxPaulCPxx | Nov 21, 2008 08:15pm | #3
    Did you see the article about adding a beam to a load bearing wall in place, one LVL at a time, cutting into the existing studs?  This may be a better technique for you.
    Also a CRX fanatic!
    Tu stultus es
  3. runnerguy | Nov 21, 2008 08:28pm | #4
    Given a choice, continious is usually better. A beam going over a post to bearing beyond is subject to less deflection then a beam whos end is ON the post.
    Runnerguy
  4. oops | Nov 21, 2008 09:22pm | #6
    I'm not sure if this is applicable in you case, but a continuos beam is actually stronger(carry more load) than a segmented beam of equal size, shape, material, etc., etc. and each spanning the same distances.  Your problem seems  to have more to do with the economy of reworking the structure than the design of the beam.
    After again reading your  post, I'm not sure of what you are asking or saying. Is the beam to be spanning 18'-0" or three 6'-0" spans? (ie. with two permanent intermediate post supports equally spaced.)  More info.would be helpful.
    I'm assuming the latter in which case, everything being equal, a continuos beam or at least a beam where the joints are staggered, is better solution, if for no other reason, than that everything is just tied together better.
  5. Framer | Nov 21, 2008 11:21pm | #7
    Need to install a beam in an existing 2x6 load bearing wall 18' long.
    Was the beam size to clear-span 18'? If so and you want to break it up, that means you probably don't need a beam anymore.
    6' sections doesn't require any big beam. Those 6' sections makes it 3 separate headers. What size beam was spec'd?
    Let's say you had a  5-1/4x11-7/8" microlam spec'd for an 18' clear-span, now your going to break it up into 6' sections giving you three headers. You do not need a 5-1/4"x11-7/8" microlam anymore because obviously those post will have to be solid blocked to the foundation and you just have 6' spans to worry about, not 18'.
    Joe Carola
  6. brad805 | Nov 22, 2008 12:10am | #8
    My take is you are debating an 18' span vs. three 6' spans.  Given you are replacing a load bearing wall that presumably has a footing sized for the existing load, I doubt replacing with a clear span is an option unless you are prepared to jack hammer out the floor where the new 18' beam ends to install new footings.  Even at 6' spans your existing footing may not be adequate for proper design loads.
    Brad
    1. Framer | Nov 22, 2008 12:31am | #9
      If the wall is sitting on the outside foundation, it doesn't matter what the footings are. If it's an interior wall that sits on the main girder below, then he has to worry about where those posts are if they land in between lally columns and possibly add footings in the basement.
       Joe Carola
      1. brad805 | Nov 22, 2008 01:02am | #10
        Very true, an exterior wall (if concrete) will spread the load very well to the footing.   I was thinking it was an interior wall and didnt even consider the option 18' would be span from one exterior wall to another.
        Brad
FHB Podcast Segment: Waterproofing Below-Grade Foundation Walls
Learn about the pros and cons of waterproofing vs. damp-proofing foundation walls.
  • Why the FHB Summit Is an Industry Event You Don't Want to Miss