I’m in need of a form which shows the calculations for an electrical subpanel for a residence.
Anyone know where I can locate/download one ?
My local inspector is requiring one in order for me to relocate a sub-panel.
I’ve ‘googled’ and looked at numerous sites but have turned up empty handed. I’ve gone through the city’s website and located the requirement in their code but no example(s) of forms.
Much thanks
Replies
They are looking for two things that I can think of:
1. What is the amperage you plan on providing from the subpanel? Break it down to circuits and how many amps you intend to provide from this panel.
Note, just because you have 5 20amp breakers doesn't mean you need a 100 amp panel ;).
2. How long will the wire need to be to reach from the main panel to your new subpanel - and how is it being run (conduit, raceway, bundles with other wire, buried underground.
With those two numbers, load and distance, you will be able to calculate the correct gauge of wire needed to connect the two. It might need a larger wire than normal if the wire is in a hot location (attic or bundle) or is far away (a shed 200' away)
Rebuilding my home in Cypress, CA
Also a CRX fanatic!
If your hair looks funny, it's because God likes to scratch his nuts. You nut, you.
How about this one, posted right here on the Fine Homebuilding site: http://www.taunton.com/finehomebuilding/PDF/Free/Service_Feeder_Calculations.pdf
It's in the How-To section, look at the blue bar at the top of the page.
Put can that be used for a sub-panel?The basic numbers can work (3 watts/sq ft, etc). But I don't think that you can take the demand factors. That is only good for an whole dewelling.I know that table 310.15(b)(6) reduced size for dewelling feeders, works like that..
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
I tried to retrace your steps to find the "feeder calculations" table and I never did come up with the same table you did. How, step by step, did you go to the " how to" section to find that step by step table calculation?I tried the electrical section of "how to" and put in several word combinations to the search function and couldn't find that table. What am I doing wrong?
I tried to retrace your steps to find the "feeder calculations" table and I never did come up with the same table you did. How, step by step, did you go to the " how to" section to find that step by step table calculation?
How-to > Electrical > Design and Planning (in blue bar on left side of screen) > New Construction > Sizing an Electrical Service by Cliff Popejoy > View as PDF
Edited 2/1/2008 7:38 pm by Stuart
Perfect...Thanks
This is a little form I drew up for a basic home calculation:
Dwelling Unit Calculations
(Use 120/240 volts)
Step 1. General Lighting
Area__________sq.ft. X 3 = ____________VA
Small Appliances [2 X 1500]____3000____VA
Laundry ____1500____VA
TOTAL ____________VA
First 3000 VA @ 100% ___-3000____VA X 1 = _________VA
3000 to 120,000 ____________VA X .35 _________VA
Over 120,000 ____________VA X .25 _________VA
TOTAL _________VA à________VA
Step 2. Appliances [Note: washing machine is included on the launder circuit.]
Cold Water Heater _________VA
Dishwasher _________VA
Garbage Disposal _________VA
Trash Compactor _________VA
Other _________VA
TOTAL _________VA à or
If more than 3 _________VA X .75 = à ________VA
Step 3. Heat vs. Cold
Air Conditioner @ 100% _________VA
Electric Heat _________VA Largest à ________VA
Step 4. Dryer
5000 or Nameplate VA [___amps X ___volts] [greater] à ________VA
Step 5. Stove
Result from 220-19 or 8000 VA à ________VA
Step 6.
Total of 1 thru 5: (6)________VA
(6)_________ = (7) ________Amps
240v
Step 7. Use Table 310-15(b)(6) if 120/240v
Or use 310-16 [if 3 phase or above 400 Amps}
Step 8. Apartment = 100 Amp service
House = 200 Amp service
Big house = 400 Amp service
But for a subpanel, you would just need a list of all your expected loads. But I don't know why they would require calculations for a subpanel.
~Peter