Electrical Troubleshooting Question

Saltworks | Posted in Construction Techniques on June 26, 2007 12:46pm

I have a pool pump that is tripping the breaker in the basement.  20A breaker, dual pole, 240 volts across the black and white wire.

I shut off all the switches in the pool house.  Breaker still trips.

I removed all the wires from the underground cable in the box in the pool house.  Breaker still trips.

I tried leaving just the black wire connected.  Breaker doesn’t trip.  Hook up just the white wire, breaker trips.

I found the junction box in the basement where the house wiring connects to the underground cable to the pump house.  Disconnected the wires, turned on the breaker, breaker doesn’t trip.

Wired an extension cord to the cable to the pool and plug it in, GFCI trips.

Is there any doubt that I have a defective underground cable from the house to the pump house?  Is there any additional trouble shooting I should do before I start digging?  I think I have isolated the problem, but if there is anything else I can do before digging, I would like to hear it.

Thanks for any advice. 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    maddog3 | Jun 26, 2007 12:55am | #1

    disconnect it at the pump house and keep checking ... might be something out there ...

    .

    .

    .

    .

    , wer ist jetzt der Idiot ?

  2. paulwaterloo1 | Jun 26, 2007 01:40am | #2

    You have a load that is grounding out. Something on the hot side is not properly isolated to the neutral side.

    If you turn the power off to the 240 VAC circuit and then took a resistance measurement between the hot and neutral, you will find you have a low resistance. You have already started isolating the problem, you just need to finish finding the problem.

    It could be the wiring on the hot run, but I might suggest that it is a load instead. What kind of loads do you have? Isolate them one at a time with the power OFF and take a resistance reading. When it goes up to infinity, you found the problem.

    A lot of electrical problems can be found in a connection, not normally in a wire run. Or it is a load. Could of been something vibrated a connection loose and it is now touching ground.

  3. DanH | Jun 26, 2007 01:47am | #3

    > I tried leaving just the black wire connected. Breaker doesn't trip. Hook up just the white wire, breaker trips.

    Sounds like somewhere the white has been connected to ground or to another white that isn't fed through the GFCI breaker. Remember, the white must as isolated as the black once it leaves the breaker -- can't be tied to any other whites.

    So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin
  4. User avater
    BillHartmann | Jun 26, 2007 03:54am | #4

    You have said several things here that some of the other people have missed.

    Also you said seveveral thing that aren't very clear.

    "I have a pool pump that is tripping the breaker in the basement. 20A breaker, dual pole, 240 volts across the black and white wire."

    So this is a 240 volt only circuit. No neutral and no 120 volt loads.

    In a circuit like that the white wire is suppose to be remarked to show that it is a hot wire and not a neutral. Usually done by wrapping with black or red tape.

    Is this just an overcurrent breaker or is a breaker that also has GFCI function? And if so can you tell the which caused it to trip?

    "I shut off all the switches in the pool house. Breaker still trips."

    How many switches and what do they operate?

    "I removed all the wires from the underground cable in the box in the pool house. Breaker still trips."

    Does that include the ground wire?

    "Hook up just the white wire, breaker trips."

    Again does that include the ground wire?

    "Wired an extension cord to the cable to the pool and plug it in, GFCI trips."

    To the pool or the pool equipement? And how did you make the connections a 240 extension cord is not common?

    And what did you plug it into? Where is this GFCI?

    It sounds like you tried to completely bypass the underground cable. If you did bypass the underground cable them this test shows that you have other problems (which might be a bad test).

    Note that underground cable is not legal for supply pools, at least not for somekind.

    http://www.selfhelpandmore.com/homewiringusa/2002/accessory/index.htm

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
  5. User avater
    SamT | Jun 26, 2007 04:48am | #5

    I removed all the wires from the underground cable in the box in the pool house. Breaker still trips.

    I found the junction box in the basement where the house wiring connects to the underground cable to the pump house. Disconnected the wires, turned on the breaker, breaker doesn't trip.

    **************************
    NO doubt at all. Jerk that suckka outa there.

    SamT

    1. DanH | Jun 26, 2007 06:26am | #6

      [Meant for the OP] Do you have a multimeter? "Ohm" between the ground wire and the other two with the cable disconnected at both ends. If there's enough leakage to trip the GFCI you should read less than infinite resistance on one of the wires.
      So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

      Edited 6/25/2007 11:28 pm by DanH

      1. Saltworks | Jun 26, 2007 02:00pm | #7

        Thanks for the replies I've received so far.  I'll try to clarify some points.

        There is no load on the wires in the pool house because the troublesome wire has been disconnected from everything.

        No, I did not disconnect the grounds when I was testing the circuit. 

        The two switches in the pump house that I shut off are breakers that control the two pumps (one main pump for filtering that runs a lot and one booster pump for the rolling vacuum that runs around the bottom of the pool when needed)

        I connected the two wires to the pool house to a 120V power source via an extension cord only to see if I could get some power to the pool house.  I plugged it into a GFCI outlet in the basement.

        The interesting thing is that the pump was running two days ago.  It seemed to be running poorly (pressure was low).  I shut it off to check the strainer in case it was clogged.  Strainer was not overly clogged, so I tried to restart the pump and that's when the breaker in the basement started tripping.

        The fact that things were running makes me wonder if there could be another problem, although my testing leads me to think there is a problem in the cable from the house to the pool house.

        1. User avater
          maddog3 | Jun 26, 2007 03:49pm | #8

          two wires, Black and White on a 240v breaker ....it trips so you disconnect those two, fiddle around, and then power them up using a 120v extension cord.. how do you do that ?
          how could just make one of them a neutral ?
          is ithe bare ground your neutral ?.

          .

          .

          ., wer ist jetzt der Idiot ?

          1. Saltworks | Jun 26, 2007 04:18pm | #10

            I have just disconnected the grounds at each end of the cable to the pump house.  Neither end of the cable is attached to anything.  I used an ohm meter to check resistance between the white and the bare neutral.  Zero resistance.  I checked the resistance between the black and the bare neutral, it's very high (although not actually zero).

            If there is any other conclusion to draw other than a short in the underground cable, I would like to hear it.  I think I will be digging unless another solution presents itself.

            The house was built in 1999, not when I lived here.  Sticker indicates electrical was inspected an passed, so the use of the bare conductor as a neutral, which is what it appears to be, must have been legal at the time.

          2. DanH | Jun 26, 2007 04:31pm | #13

            Yeah, the cable is toast. Likely it was nicked during installation, or has a factory splice that didn't get cut out like it should have. Or maybe a gopher or some such. (Have you done any digging or fence post setting in the area recently.)

            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          3. paulwaterloo1 | Jun 26, 2007 04:32pm | #14

            This thread is confusing at the least. I read your initial post about 8 times to figure it out. So you have:

             

            - 240 VAC circuit that supplies power to Two electric motors that drive pumps, that's the only thing on the circuit.

            - It trips when the breaker is energized.

            - You have close to infinite Ohms between the hot and neutral (you state it is very high, although not actually zero). You wouldn't have a neutral on this system, just two hot legs, this needs to be clarified. You state that between neutral and the bare wire you have 0 ohms which would indicate to me that this is a 120 VAC circuit or the white leg is part of a 220 VAC circuit and is grounded. Does it have a single or two pole breaker at the breaker box?

            Personally, it sounds like a motor winding has failed, but need more information:

            1. Is the wiring in a conduit, or is it ROMEX?

            2. How is the wiring marked, sounds like black, white and bare. Check it at the breaker box, if the white and black both feed into a separate breaker, this would be the configuration for a 220 VAC circuit. If only the black feeds into a breaker and the white is tied to the common/neutral, it's a 110 VAC circuit.

            3. Have you disconnected the motors at the junction box at the motor and energized the circuit to see if the breaker still trips? Do one motor at a time. If it doesn't trip, then it sounds like your wiring is good and the motor stator winding has failed (grounded out). If that is the case, you need to replace the motor.

            If it no longer trips with one motor disconnected, measure the resistance from the hot lead of the motor winding to the bare frame of the motor. If the resistance is 0, the stator winding has failed and that is your problem. It should be very high (megaohms).

            Can you post pictures of what you are trying to do? This is a very easy problem, but is very hard to understand, pictures would make it very easy.

          4. User avater
            maddog3 | Jun 26, 2007 05:37pm | #16

            from what he wrote, the bare ground is being used as the neutral for the black and white.... two separate hots out to the pump house and then one to each pump . along with a bare wire...sounds like the inspector missed it or whomever installed it pulled a fast one....

            .

            .

            ., wer ist jetzt der Idiot ?

          5. User avater
            BillHartmann | Jun 26, 2007 07:08pm | #20

            He never used the term neutral until well after other people had used that term.Paul kept using the term neutral."You have a load that is grounding out. Something on the hot side is not properly isolated to the neutral side.""If you turn the power off to the 240 VAC circuit and then took a resistance measurement between the hot and neutral, "And here he is not using the term consistantly.That is my I made very seecific comments and questions. But he did not verify them one way or anyother..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          6. User avater
            maddog3 | Jun 26, 2007 08:23pm | #21

            you're right something was not adding up , I couldn't figure out how 240 or 120 could run a pump well I hope he at least ran 12/3 W G.

            .

            .

            ., wer ist jetzt der Idiot ?

          7. paulwaterloo1 | Jun 26, 2007 09:00pm | #22

            I would like to formally appologize and recall anything that I said that was incorrect.

            :-)

            A picture is worth a thousand words. And you are right, it probably was the motor running on 110 VAC versus 220.

          8. User avater
            maddog3 | Jun 26, 2007 05:14pm | #15

            any other conclusion? nope you will be digging...may as well replace the cable with three wire / ground.

            .

            .

            ., wer ist jetzt der Idiot ?

          9. DanH | Jun 26, 2007 06:33pm | #17

            One other thought: Before you rip up anything, carefully examine the cable where it enters the junction boxes at both ends, and make sure that there's no spot of skinned insulation or some such that could cause this.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          10. Saltworks | Jun 26, 2007 07:03pm | #18

            To all who replied, thank you for your assistance and patience.

            I did what I should have done sooner, I ran a new cable above ground to the pump house.  Everything works perfectly.  I will start digging and burying soon.  I know it would have taken less time to do that than the amount of time that has been expended here, so thanks again.

            In addition, the pump now works fine, too, with normal pressure.  I think that yesterday I thought I had a pump problem and then thought I had a coincidental line problem.  I bet that the line was the whole problem from the start, and the pump was running poorly because it may have lost part of its power.  I'm no electric motor guy, so who knows.  All I know is that all is well and the obvious answer was the right one.

          11. DanH | Jun 26, 2007 07:08pm | #19

            It may be that only half the double-pole breaker tripped, feeding 120V to the pump. It would still struggle to work, but would run slowly and would be apt to overheat.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          12. USAnigel | Jun 27, 2007 02:48pm | #24

            Run in conduit this time, easy to replace if needed to again.

        2. User avater
          BillHartmann | Jun 26, 2007 04:14pm | #9

          "The fact that things were running makes me wonder if there could be another problem, although my testing leads me to think there is a problem in the cable from the house to the pool house."It is possible for their to be a problem with the cable and pumps still work.All it takes is a small nick in the insulation and water getting into it to get enough leakage to trip a GFCI.You did not indicate 2 pole breaker was just an over current protection are if it was also a GFCI breaker.But even if it was only overload it is possible for a short to start developing between the one hot and grand and still supplying power ot the load.Depends on what kind of damage and just what is happening inside the cable..
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          1. Saltworks | Jun 26, 2007 04:24pm | #11

            Bill

            It's not a GFCI breaker, but see my reply to Maddog, it certainly appears that I have a short between the white and bare ground in my feed to the pump house.

        3. DanH | Jun 26, 2007 04:29pm | #12

          The cable could be undersized or have had a bad spot in it, and overheated.
          So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

  6. edlee | Jun 27, 2007 05:01am | #23

    Did anyone mention that UF cable isn't generally used for wiring pools?  You  refer to underground cable, so I'm figuring that's what you mean.

    If you follow the NEC or some derivative of it then the approved method is to use  wiring that has an insulated ground.  This usually means conduit with individual conductors pulled through it. UF has a bare ground wire so is not approved for this use (the NEC refers to it as "covered").

    This requirement kicks in where the wiring leaves the house and goes underground.

    FWIW...................Ed



    Edited 6/26/2007 10:04 pm ET by edlee

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding the Right Fixer-Upper

Get expert guidance on finding a fixer-upper that's worth the effort.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data