I recently failed a final electrial. The inspector wrote
i fasten backfed breakers.
Can anyone explain what that is and how to correct it?
David
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
From plumbing failures to environmental near disasters, OHJ staffers dish on our worst and best moments.
Highlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
*
If you connect a voltage source to what normally is considered the load side of a breaker, you are backfeeding the panel buss through the breaker. I'm guessing you may be wiring a main lug subpanel and you are backfeeding so you have a main breaker to meet a disconnect requirement. In any case you need to fasten the breaker so it can't be popped out of the panel by hand.
*
The panel manufacturor provides a method to do this. The most common method is a small hole through the front of the breaker which accepts a long 6-32 machine screw . The screw engages a tapped hole in the back of the panel.
The panel usually provides the info on the paper glued onto the cover, and it refers to using the backfed breaker as a "main" breaker.
Sometimes you have to buy an accessory kit that has a clamp of some sort.
Lee
*
Also meant to add "or the breaker can't be accidentally dislodged if the panel cover is off, etc..."
*