Can anyone tell me the minimum distance from the top of a firebox to the bottom of the wood mantle?
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
Skim-coating with joint compound covers texture, renews old drywall and plaster, and leaves smooth surfaces ready to paint.
Highlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
it's a function of the projection of the mantle shelf...at three inches up, you can go one inch out, four inches up, can go 2 inches, and like that...
This mantle sticks out 2", then has crown mold 45 deg., than top of mantle wich totals only 7" out.
By his formula, that would mean you need to be at least 14" above the openning, but I always keep it a good 18" above the openning to start. I believe code disallows wood within 8" of the openning.
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
On this zero-clearance fireplace, 48" x 40" OSM, (with 8" of steel above the opening), 8" tiles works out perfect with 16" under the mantle.
I had a handout from a local building dept. once, but I can't find it now. Anybody have one?
Jack
but you can't put any wood three inches up from the openning.
Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!
Around here (CA), you can't have any combustible material within 12" of the firebox. Designing mantles can get interesting - lol.
Is this a wood burning FP or one of those gas log deals.
Someone correct me but doesn't it make a difference?
Doug
It's a wood burning jobbie.
I went with the 8" tiles above the 8"es of metal above the opening. Totals around 16". I'll let y'all know what the inspector says later.
Respect, Jack
And as I've discovered, there really isn't any great rule of thumb. It is dependent on the projection, but all the fireplaces that go in around here are premade units and they come with this neat little guidebook tucked into the bottom. Usually about page 3 is the manufacturer's minimums for clearance. I don't know that I've ever seen anything that lets wood within 6", even flat. Most of them start around 6 on the side and 10 on the top.
My "guide book" is only concerned about the hearth size, and being too close to any walls on the side.
ZERO information on the mantle height.
The zero clearance, sealed combustion chamber gas fireplace I'm putting in next month sez 4" of noncombustible wall sheathing, then sez you can put <flat> wood molding over that right up to the edges, as long as it doesn't stick out past the steel lip around the unit.
And the mantle, 2" up, lets you go 2" out, 4"/4", etc.
But why do they always put that little book at the BOTTOM of the box? How about in a plastic envelope on the outside?, or at least on the top? I guess they really don't want us to "RtFM" before it's installed.......
Steve
Confused yet? Lemme explain it again.......