The building inspector told me not to put a GFI outlet on the circuit (dedicated) that serves the washer. I thought this should be used if the outlet was around water.
Thanks,
Paul
The building inspector told me not to put a GFI outlet on the circuit (dedicated) that serves the washer. I thought this should be used if the outlet was around water.
Thanks,
Paul
Fine Homebuilding's editorial director has some fun news to share.
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Get home building tips, offers, and expert advice in your inbox
Fine Homebuilding
Get home building tips, offers, and expert advice in your inbox
© 2024 Active Interest Media. All rights reserved.
Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.
Get home building tips, offers, and expert advice in your inbox
Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.
Start Your Free TrialStart your subscription today and save up to 70%
SubscribeGet complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.
Already a member? Log in
Replies
There is no requirement for the GFCI for clothes washer receptacle unless it is within 6 ft of a sink. The "wet bar" requirement has been extended to any basin (eithr in the 2005 NEC or the proposed 2008).
There is logic behind all of this.
The clothes washer is grounded via the ground terminal on the plug and receptacle.
And ground fault will flow safely through the ground conductor and if big enough it will cause the breaker to trip.
But where you have an open sink it is possible that you could use a portable appliance and drop it into a sink full of water.
But there is no prohibition to using a GFCI there.
.
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
Edited 4/3/2007 3:22 pm by BillHartmann
As I understand it, if it's DEDICATED for a specific grounded appliance then GFCI is not required (though other rules may trump this one). Some inspectors have demanded that the dedicated outlet not be a duplex, but that rule seems a bit much, since often a gas dryer, water softener, or something similar also needs to be plugged in.
It's sometimes not good to have a washer on a GFCI since washers can develop current leakage as they age, causing the GFCI to trip without really "protecting" anyone or anything. Plus the electric motor can cause nusiance trips.
DanWrong requirments.Spaces in unfinished basements and garages required GFCI protection. There are exception in those spaces for dedicated appliance receptacles.If this is a "laundry room", which even if it was in a basment would imply a finished space, then there is no general requirment for GFCI's.The next requirement is with 6ft of a sink. Here is the 2005 NEC "(7) Laundry, utility, and wet bar sinks ù where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink"Here is the commentary in the handbook."Recognizing that sinks at wet bars are not the only location where a ground-fault shock
hazard exists, this requirement now also covers sinks in laundry and utility areas. With
this change, GFCI protection requirements are now in place for all areas in a dwelling
unit in which a sink is installed. The revised text of this requirement does not limit the
GFCI requirement to only receptacles serving countertop surfaces; rather, it covers all
125-volt, 15- and 20-ampere receptacles that are within 6 ft of any point along the
outside edge of the sink. Many appliances used in these locations are ungrounded, and
the presence of water and grounded surfaces contributes to a hazardous environment,
leading to the revision of this requirement for GFCI protection around sinks. Unlike
the GFCI requirements for garages and unfinished basements, there are no exceptions
to GFCI protection for receptacles installed within 6 ft of laundry, utility, and wet bar
sinks. As illustrated in Exhibit 210.14, any 125-volt, 15- and 20-ampere receptacles
installed within 6 ft of a wet bar, laundry, or utility sink is required to be GFCI
protected."Also the commentry on washer in a bathroom."GFCI receptacles in bathrooms prevent accidents. Therefore, 210.8(A)(1) requires that
all 125-volt, single-phase, 15- and 20-ampere receptacles in bathrooms have GFCI
protection, including receptacles that are integral with luminaires and, of course, wallmounted
receptacles adjacent to the basin. Note that there are no exceptions to the
bathroom GFCI requirement. For example, if a washing machine is located in the
bathroom, the 15- or 20- ampere, 125 volt receptacle that is required to be supplied
from the laundry branch circuit must be GFCI protected."Also note that this is one of the areas that local amendments like to play with..
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
Edited 4/3/2007 4:30 pm by BillHartmann
Thanks for the reply. The outlet is less than 2 feet from the laundry tub, which is why I put in a GFI. The inspector didn't just say that I didn't need it, he told me to remove it before he would pass the inspection.
There is nothing in the NEC that prevents you from sticking a GFCI in anyplace that you want.Whether a GFCI is required or not as I said that it one of the areas that locals like to modify. But I have not seen any codes that prohibit using a GFCI.But for something like this I would replace it with a regular recept and then as soon as his car leaves the driveway but the GFCI back..
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
I looked up Waterloo's building code and I see that they are still using the 99 NEC. And while there are a number of local amendments none of them affect GFCI requirements.http://66.113.195.234/IA/Waterloo/index.htmThat version does not require GFCI's at landry and utility sinks. But again no prohibition againts having one..
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
Yup, that's been my experience with GFCI on the washer. Once in a while it'll nuisance trip.
-- J.S.
Once in awhile, every GFCI will nuisance trip.