Hanging a furnace in “mid air”

Leon | Posted in Energy, Heating & Insulation on February 28, 2004 08:12am

In installing a forced air furnace, is there any reason why I can’t  suspend it from the roof rafters in my garage, about 7 feet off the floor (the garage roof is about 12 feet high)? 

This would allow me to get the condensate easily into a P-trap in the adjacent laundry room, and would also give me more usable space in the garage.  At first glance it seems weird to see a furnace “hanging” along the wall in midair, but is there any reason (or code) that disallows this? 

I guess one obvious potential drawback would be more complicated servicing/maintenance, but I am looking primarily for things that make this illegal rather than simply impractical (though I’d be curious about both).  FWIW, I’m in Southern CA.  I plan to ask my inspector on Monday, but any a priori knowledge would be helpful.

Thanks in advance,

Leon


Edited 2/28/2004 12:44:06 AM ET by leon

Reply

Replies

  1. DanH | Feb 28, 2004 09:40am | #1

    Ask the furnace manufacturer what their mounting requirements are.

  2. sungod | Feb 28, 2004 10:52am | #2

    OK in the garage, but you cannot use the flexible plastic duct cause they may penetrate the firewall.  So 22 guage (I think?) ducts will be required.

  3. User avater
    Dreamcatcher | Feb 28, 2004 11:23am | #3

    Leon,

    Seems like I have seen a unit that was made to be suspended. I think it was in a crawlspace with a dirt floor that I saw it.

    It was a long time ago so I could be mistaken.

    good luck.

    gk



    Edited 2/28/2004 3:28:21 AM ET by gabe

    1. DaveRicheson | Feb 28, 2004 05:30pm | #4

      As Dan said, find out if the model you have can be hung first. Then make sure your rafter/joist/ceiling will support the point load. If the furnace weights 200 pounds and is supended at fout corners, you get 50 lbs. per point. Depending on span,joist material, and location of the unit, you could end up creating more problems than the location of a condesate drain warrents.

      Dave

  4. fortdh | Feb 28, 2004 08:34pm | #5

    Can you do a wall mounted platform, and save the car space below?

    If only for the drain, you could get a condensate pump, but understand space is also a goal.

    I don't like to see the way many are suspended. I have seen some that broke the back of the air handler when a side panel was removed. If you can put it on a sturdy platform, put a sheet of foamboard under it to rest on, and it will eliminate a lot of vibration. Servicing with a step ladder against a shelf will be safer than something suspended that can swing. Also, a stable base will be better for the metal duct connections.

    Hope this helpful for discussion with inspector. Paul

    Energy Consultant and author of Practical Energy Cost Reduction for the Home
  5. WayneL5 | Feb 28, 2004 11:06pm | #6

    Many manufacturers make units intended to be hung horizontally.  You're best off if you buy one made for hanging.  All the supports and access are already configured to install the unit easily.

    1. Ruby | Feb 29, 2004 12:37am | #7

      They just installed a 4T furnace like you are describing in our attic. It is part of a heat pump system.

      It is suspended from the rafters horizontally by some eight chains, at least, four to the side.

      It has a drip pan below built integrally that has it's own drain, that if it ever shows to have any water off it on the outside of the house drain spout, I am supposed to turn everything off and have it serviced. It also had a regular drain into the water heater vent drain. 

      Ask the manufacturers in your area about them. That is what all builders here seem to have been installing the last several years, with good results.

    2. DanH | Feb 29, 2004 12:41am | #8

      Yeah, I think a lot of crawlspace type furnaces are designed to be hung.

      There are, of course, space heaters designed to be hung that are used in warehouses, etc, but I assume that a true furnace is desired here, to heat the house, not the garage.

    3. DanH | Feb 29, 2004 12:42am | #9

      One other point (to reiterate what was said earlier): Consider how the unit will be serviced, and provide appropriate ladder rests and maybe a sort of tool tray.

      1. Leon | Feb 29, 2004 06:20am | #10

        Thanks for the great responses, guys!  I guess I should have been a bit more clear: I am not necessarily committed yet to an actual method of suspending the furnace, I was primarily asking about the idea of "placing" a furnace horizontally somewhere below the rafters.

        From your suggestions, I am leaning towards a platform of some sort, probably with a ledger bolted to the studs at the wall, and a couple of threaded rods connecting the outer portion of the platform to the rafters.  Not worried about the details right now, I'll see what the inspector says.

        And I am aware of the drip pan drain that is supposed to be the tell-tale sign of a problem in the primary drain, I'll be sure to run it that way.  Also aware of the requirement for all-metal ducting inside the garage, thanks for the reminder :).

        Anyway, I think I have enough to go talk to my "final authority" on Monday and see what he thinks.  I'll keep you posted!Leon

        1. reinvent | Feb 29, 2004 04:16pm | #11

          Make sure the wall and ceiling have at lest 5/8 drywall on them. Also you might consider putting a sheet of durarock on the deck between the plywood and the furnace for some fire resistance.

  6. Jock | Feb 29, 2004 04:31pm | #12

    Check w/ your local fire marshall and/or bilding insp. If it is going to be in the garage, it must be at least 8ft. off the floor. Gasoline vapors and all that stuff. Like the other posts have said, there are units built to be suspended.

    1. Ruby | Feb 29, 2004 05:00pm | #13

      Check with your inspector about this:

      Here, by code you need to have a specific sized access to the attic at no more than 20' from the furnace. Should not be a problem in the garage.

      Many hang them in the attics above the garages, if that is the best place for them, they told me. No one mentioned IN the garage.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Fire Separation Distance

Learn how the IRC addresses ways to prevent the spread of fire from one property to another.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Issue #320 – Dec. 2023/Jan. 2024
  • Podcast 607: Wood Foundations for Winter Builds, Adding Headroom, and Aeroseal for Leaky Ducts
  • Podcast 607: Members-only Aftershow—Holiday Gifts for Home-Building Enthusiasts
  • Fine Homebuilding Issue #320 Online Highlights

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • 2024 Tool Guide
    Buy Now
  • Pretty Good House
    Buy Now
  • 2023 Fine Homebuilding Archive
    Buy Now
  • Code Check Complete 3rd Edition
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 320 - Dec 2023/Jan 2024
    • How to Reuse Salvaged Wood
    • Chainsaw Retrofit and Energy Performance
    • Maximize HVAC Efficiency
  • Issue 319 - November 2023
    • Nearly Net-Zero ADU
    • An Easy Approach to Coffered Ceilings
    • Understanding Types of Roof Vents
  • Issue 318 - October 2023
    • Make Mudsills Square and Level
    • Turn Up the Heat With Induction Cooktops
    • The Fine Homebuilding Interview: Lloyd Alter
  • Issue 317 - Aug/Sept 2023
    • Finishing Drywall With Seamless Results
    • A Flat Roof in a Cold Climate
    • Compact Cordless Shop Vacs
  • Issue 316 - July 2023
    • Timber-Framed Solar Canopies
    • Build a Transom Above a Stock Door
    • Understanding Toilet Design and Efficiency

Fine Homebuilding

Follow

  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok
  • twitter

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok
  • twitter

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to set_percent%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in