How many lights on a circuit?

GotAll10 | Posted in General Discussion on February 28, 2004 05:04am

How many 60 watt light bulbs can I safely put on one 15 amp circuit?

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. MikeQ | Feb 28, 2004 05:58pm | #1

    according to the Ontario Electrical code rule 12-3000 you are allowed 12 recepticles on a 15 amp circuit this is also true for incandescent 60 watt lights . The maximum you can load a circuit is 80% of rated amperage a 15 amp breaker is rated for 1800 watts 80% of this is 1440watts  12 60watt lights draw 720 watts so 12 light bases can be installed on a 15 amp 120volt circuit. 

    hope this helps

    1. User avater
      BillHartmann | Feb 28, 2004 06:28pm | #2

      The NEC has no limit on this for residential applications, so it goes by the load and would allow 24.

      But some locals have modified the code and some inspectors have their own interpretation.

      But you never know when some one might replace the bulb with a larger one (improperaly) or the fixture might get replaced with a larger one.

      So I would not push the number to the max. !2 sounds like a "good" number.

      1. brownbagg | Feb 28, 2004 10:44pm | #3

        Bill is right, no limit to how many, But think about, how many will be on at one time. So you can put 30 if you want but you can only turn on 12. same with plugs, you can have as many as you want but you can only use a certain amount of watt, I cheeted. I put bedrooms on one, bathroom on one, living room/den on one and kitchern laundry room on one.

        Code...... bathroom light and plug cannot be on same circuit, bathroom light can only be on bathroom light. you can combined two bathroom/ lights but you cannot combine bathroom with bedroom lights.

        1. User avater
          BillHartmann | Feb 29, 2004 08:19am | #6

          "Code...... bathroom light and plug cannot be on same circuit, bathroom light can only be on bathroom light. you can combined two bathroom/ lights but you cannot combine bathroom with bedroom lights"

          That is not exactly right.

          A bathroom receptacle requires a 20 amp circuit.

          You have two choices. You can run one 20 amp circuit to the receptacle in all of the bathrooms (even if you have 5 or 10) and have nothing else on that circuit.

          Or you can power the recptacle(s), light(s), and fan from that 20 amp circuit, but one for that one bathroom.

          That is the NEC.

          Howeveer, I know that the inspector in your area makes up his own rules depending on which alternate thursday he does the inspection.

          1. brownbagg | Feb 29, 2004 05:41pm | #7

            (210-52d) separate 20 anp circuit required for bathrooms ( no Lights)

          2. User avater
            BillHartmann | Feb 29, 2004 06:32pm | #8

            What version of the code that are you working from?

            99NEC 210-52(d) only requires a wall receptacle within 3ft of outside edge of each basin. And if refers to section 210-8(s)(1) which just requires that the receptacle be GFI protected.

            Section 210-11 lists the required branch circuits.

            "(3) Bathroom Branch Circuits. In additon of the number of branch cirkcuits required by other parts of this section, at least one additional 20-ampere branch circuit to supply the bathroom receptacles outlets(s). Such circuitrs shall have no other outlets."

            "Exception: Where the 20-ampere circuits supplies a SINGLE BATHROOM (emphasis added), outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with Section 210-23(a)."

            210-23(a) just specifies the size of outlets allowed on different circuits.

            Note an outlet according to NEC-speak is anyplace a "point on the wiring systems at which current is taken to supply utilizaiton equipment". That includes fans and lights, not just receptacles.

      2. Piffin | Feb 28, 2004 11:02pm | #5

        I know the Q is for 60W bulbs but you make a good point. I have "fixed a lot of ceiling fixtures where the connector tab has deformed from the excessive heat where somebody ignored the warning label that says, "This fixture is not inteneded or designed for bulbs exceeding 60Watts"

        Another item here - We do a lot of ceiling pot lights which have their own individual thermal cutout so individually, they are safe, but had one where six fixtures with 90W floods were put on a dimmer switch. The switch itself got hot and burned out in a year or so. 

         

        Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

  2. User avater
    JeffBuck | Feb 28, 2004 11:02pm | #4

    what the others said ..

    and ..

    my electrician uses a rule of thumb of 10 on a circuit.

    Like they already said .. usually 12 will "fit" ...

    so 10's a nice safe round number ...

    add things up first to be safe .. then back off a bit for security.

    Jeff

    Buck Construction   Pittsburgh,PA

         Artistry in Carpentry                

  3. JohnSprung | Mar 01, 2004 11:12pm | #9

    Also consider checkerboarding which rooms have their lights on which circuits.  That way if a breaker trips, you'll still have a little light from adjacent rooms to find your way to the panel.

    And people are also more likely to overload plugs than lights.  If you don't mix them, the lights will be available for most of those trips to the tripped breaker.

    -- J.S.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Sometimes Spray Foam Makes Sense, Sometimes It Doesn't

Spray foam is a great invention, but it's not always necessary.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Making the Move to Multifamily
  • Custom Built-ins With Job-Site Tools
  • An Easier Method for Mitered Head Casings
  • Tall Deck on a Sloped Lot

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data