I have an 80 year old house, with a new cedar shake roof. The attic is basically a bit more than a crawl space, but I do need to go up there from time to time to deal with the vents and the attic fan. I’d like to put some lighting in to make this easier to do.
My question is, what type of lighting would be up to code?
The attic under the cedar shake stays dry, but I’m thinking I might want something a bit more all weather than florescent tubes. Are there any code considerations? Anything that would be best for this type of application?
Thanks,
Glaucon
If you don’t think too good, then don’t think too much…
Replies
Depends on the "where" you are. (insert hint to fill in Profile info)
Here, in my bit of central Texas, my City requires attic lighting if there is an air handler in the attic. It further reuires a switch within 36" of (any) attic access, and if the unit is not immediately adjacent, that the path to the unit be "reasonably" lit. Oh, and there has to be a 15A duplex outlet next to the a/h too.
Now, in the sistercity just to the south of us--the service outlet is required, the light is recommended (strongly) but you can switch the light fixture however your want.
Now, your question on durability is apt. I prefer a heavy-duty incandescent lamp in a weatherproof fixture in attics (with a protective cage if the fixture is less than 60"above the framing, or otherwise sensible).
Pretty much what CapnMac said.
Local DE code says : We need lighting with switch within 36", 15A duplex outlet if any mechanical equipment in attic area - you have a fan, so it would be required. Duplex must be GFCI protected. They are pretty loose on light fixture types - I see a lot of plastic / ceramic bases with a bare incandescent bulb - regardless of clearance. I'd vote for cage enclosed fixture if headroom is tight at all.
Jim
Never underestimate the value of a sharp pencil or good light.
Thanks for your help. Sounds like a caged fixture with a GFCI is the way to go.Glaucon
If you don't think too good, then don't think too much...
I tend to mount 'keyless' type fixtures in the space between the rafters, and use CFL's in them ... with all lamps switched by the attic entrance.
Take care to orient the lights so the bulb points away from any wood ... just in case someone puts an 'ordinary' bulb in there!