partial ground?

brucet9 | Posted in Energy, Heating & Insulation on November 2, 2007 09:11am

I hope some of you sparkies can tell me what’s wrong.

40-year old SoCal tract house. Copper wiring, NM 12-2 with ground, steel boxes, ground wires clipped to edges of boxes (apparently run outside the boxes to clip on the front edge), duplex non grounding outlets (except in kitchen, baths and laundry room of course).

HO wants to replace outlets with grounding type.

Voltage tested on one of the outlets between hot and grounded slot = 115V; between hot and grounding clip on box = 95V. Tested box is neither first nor last on circuit; don’t know how many outlets there are upstream.
What is the likely cause of the low potential?
What problems might there be if I were to install grounded outlets where ground voltage is just 82% of normal?

BruceT
Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. DanH | Nov 02, 2007 01:30pm | #1

    The 95V is "phantom" voltage, meaning the ground isn't really connected. If you use regular outlets you'd be violating code and common sense safety rules installing 3-prong outlets here.

    You can use GFCI outlets (or one GFCI at the head of the run, with the others "daisy chained" through it), but then you're supposed to apply a label to each outlet saying "ungrounded", and the outlets are no good for surge protectors (though perfectly safe for humans).

    If your view never changes you're following the wrong leader
  2. JTC1 | Nov 02, 2007 02:54pm | #2

    I am trying to get a grip on your current installation.

    >>Copper wiring, NM 12-2 with ground, steel boxes <<

    OK - cable containing black, white and bare conductors all contained in a non-metallic sheath. Steel boxes.

    >> ground wires clipped to edges of boxes (apparently run outside the boxes to clip on the front edge),<<

    Very confusing - the original installer brought 12-2 with ground inside of the steel box, stripped the outer sheath back and then threaded the the bare grounding conductor outside of the box and ground clipped it to the front edge of the box??????? This makes no sense. I find it hard to believe that someone would do this --- way too much work.

    >> duplex non grounding outlets <<

    OK

    >>(except in kitchen, baths and laundry room of course).<<

    Meaning that these outlets are already 3 prong grounding type? Or that when the existing 2 prong outlets are replaced, they will be replaced with GFCI type?

    >> Voltage tested on one of the outlets between hot and grounded slot = 115V;<< meaning between the hot and neutral slot of an existing 2 prong duplex? Or between hot slot and the ground slot on an existing 3 prong duplex - see above question.

    >> between hot and grounding clip on box = 95V.<<

    Understood.

    Jim

    Never underestimate the value of a sharp pencil or good light. 

    1. DanH | Nov 02, 2007 05:08pm | #3

      >> ground wires clipped to edges of boxes (apparently run outside the boxes to clip on the front edge),<<I've seen this before. The ground wire is doubled-back out the hole for the cable, then around the outside of the box and held in place with one of those metal edge clips. Kinda made sense when the ground wire had no useful application inside the box. Probably not the ideal way to do it, but not in itself a problem.The net of course is that the ground wire is not solidly connected somewhere, and therefore it cannot (in good conscience) be used to ground 3-prong outlets.
      If your view never changes you're following the wrong leader

      1. JTC1 | Nov 03, 2007 03:20am | #6

        OK, that's a new one on me.

        I've seen most of the stuff Mike Hennessey mentions in his .6 post, but have never encountered a ground wire clipped to the outside of the box. I wonder if that was a regional practice which never caught on here.

        Seen plenty of ground wires which enter the box and are then clipped to the box edge, but the conductor was inside of the box. From pre-threaded ground screw hole days.  Also encounter a fair amount of cloth wrapped romex with a down-sized grounding conductor -- 12-12-14 and 14-14-16.

        Jim

        Never underestimate the value of a sharp pencil or good light.

  3. User avater
    BillHartmann | Nov 02, 2007 06:07pm | #4

    Current code requires that ground wire be brought inside the box and connections made there.

    But I have heard that in the early days of grounded circuit that was not always done. In some places it was just wrapped around the screws on the romex connectors.

    And I don't think that all of the box clips are UL listed.

    95 volts is kind of high for "phantom" voltage. My guess is that there is a (very) bad connection at one of the places with a lot of oxide under the clip.

    Or there is a run in he cable where there is a nail in it.

    If you want to do the work I you could pop the clip and if the wire terminate inside and then loops out use some needle nose plier to pull it in.

    In some places it might require a cutting out the old box, pulling it out to get access to the wires and then putting in an old work box.

    However, the wires will probably be short and a pain to work with.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
    1. MikeHennessy | Nov 02, 2007 07:09pm | #5

      I mostly work on old stuff, and I've seen lots of ground wires wrapped around the screws on the romex connector. (Back when ground wires in Romex first came into wide use, I don't think boxes even had tapped holes for ground screws. I've also seen it wrapped around outlet mounting screws, crimped to the side of the box without a clip, and many times just cut off at the Romex connector.) In the cases were the box was grounded from the outside, the ground wire was rarely routed to the inside and then back out -- it looked like the installer used the ground wire like a zipper, pulling it back to open up the sheath, then putting only the black and white into the box.

      Assuming the romex connector screws were tightened at all, I'd be surprised if the OP could get the ground wire to pull back into the box without breaking it at a bend or trashing the rest of the cable at the connector, leaving a worse problem than he started with.

      I suspect new boxes will be the only solution. Probably easier in the long run anyway.

      Mike HennessyPittsburgh, PA

  4. Howard_Burt | Nov 03, 2007 08:04am | #7

    All of the 50's to early 60's era houses I have seen in California had a separate ground run from the nearest cold water pipe to the outside of the box. The ones in my own house had a split bolt type connecter that had been thru bolted in the box.

    In my own 1950's house, only the bath, kitchen sink, and laundry had a ground wire to the box. The 3 prong plugs were added to these outlets in the late 60's.

    Could it be that maybe your ground wire might be corroded where it connects to a water  line?

    1. User avater
      BillHartmann | Nov 03, 2007 05:12pm | #8

      "All of the 50's to early 60's era houses I have seen in California had a separate ground run from the nearest cold water pipe to the outside of the box. The ones in my own house had a split bolt type connecter that had been thru bolted in the box."Note that the code still allows a wiring to be upgraded by fishing a separate ground wire.HOWEVER, CONNECTING TO THE NEAREST COLD WATER PIPE IS NOW FORBODEN. But it did follow code at the time. The prolbem is that pipes often get replaced with plastic.There are several problems with it and when you run into it you need to evaluate it and see about fixing it.The wire can connect to the ground bus in panel, to any point on the ground electrode system, or to another box with a ground wire that connects back to one of the first 2 places.
      .
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      Edited 11/3/2007 12:52 pm by BillHartmann

      1. onder | Nov 03, 2007 05:53pm | #10

        HOWEVER, CONNECTING TO THE NEAREST COLD WATER PIPE IS <NOT> FORBODEN. But it did follow code at the time. The prolbem is that pipes often get replaced with plastic.Did you mean <now> forbidden but not at the time?The new added ground can be bare?

        1. User avater
          BillHartmann | Nov 03, 2007 08:00pm | #12

          Yes, it should be NOW FORBIDEN.Thanks I corrected it."The new added ground can be bare?"AFAIK, yes. With out cross reference everyplace in the code where "ground" is used the section tht allows the use of a separate wire uses "equipment grounding conductor" and bare or insulated, solid or stranded, copper conductor is one of many types of equipment grounding conductors.
          .
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          1. onder | Nov 03, 2007 09:46pm | #13

            Thx.

  5. renosteinke | Nov 03, 2007 05:37pm | #9

    When the ground wire was first introduced, there was a brief period when ground wires were run separately from the circuit conductors. Even when the grounds entered the boxes, they were often folded over the lip, and spliced outside the box. This method was also used to add a ground wire to existing 2-wire circuits. If you look closely, you're almost certain to find that the ground wire is quite a bit smaller (#16) than the circuit conductors.

    95v is pretty high for a "phantom" voltage. It is more likely that their is a loose splice, poor bond at the panel, or some other high resistance connection.

    The whole point of the ground wire is to clear faults ... that is, make the breaker trip ASAP. A high resistance path pretty much defeats the whole point.

    The best solution is to completely rewire the entire circuit with modern wiring methods.

    Perhaps you can find, and fix, the bad connections. I doubt it, though.

    That leaves you with treating the system as if it were 'without a ground wire,' and GFI protect the circuit. With an old house - and assuming your panels are of a current make - the easiest way to do this is to get GFI-type breakers. Shared neutrals, and inter-mixed circuits (a major problem when there is DIY work done) can make that impractical. If you have problems installing GFI-type breakers, you probably have other problems present, and really ought to get a Sparky.



    Edited 11/3/2007 10:37 am ET by renosteinke

    1. DanH | Nov 03, 2007 07:55pm | #11

      95V isn't at all high for a phantom voltage, measured from hot to ground. Keep in mind that especially if the ground is run separately, it's much more strongly capacitatively coupled to ground than to the hot wire.
      If your view never changes you're following the wrong leader

      1. woodway | Nov 03, 2007 10:47pm | #14

        Please explain what you mean by "much more strongly capacitatively coupled to ground than to the hot wire."

        1. DanH | Nov 03, 2007 11:25pm | #15

          I mean there's more capacitance to "ground" (which includes most of the surrounding structure) than to the hot wire. The apparent voltage of a disconnected wire, when measured with a high-impedance voltmeter, will be determined by the ratio of the capacitances to ground and hot.
          If your view never changes you're following the wrong leader

    2. brucet9 | Nov 04, 2007 09:51am | #18

      Thanks for your insight.You wrote, "...you're almost certain to find that the ground wire is quite a bit smaller (#16) than the circuit conductors."
      Right you are, they're 16ga; part of the original NM cable.You wrote, "It is more likely that their is a loose splice, poor bond at the panel, or some other high resistance connection."
      Poor bond at the panel - would that be found by testing voltage between hot post on the circuit breaker and the ground wire for that circuit?
      loose splice - would I have to test voltage between hot and ground clip at each box working upstream until I find 115V?Presumably I could fix the splices by pulling the grounding clips off and twisting/crimping the ground wires together? Re-wiring is problematic due to the fact that one wall outlet in the middle of the circuit is in the center of a 10-foot-wide floor-to-ceiling mirror and the other side of the wall is stucco exterior.If simple fixes don't work, I think a referral to a sparky will be the next step.
      BruceT

      1. DanH | Nov 04, 2007 03:40pm | #19

        Have you tried to trace the problem down to a specific connection. Find the earliest point in the chain where there's a problem and see if tightening the connections there (or at the box prior to that) does the trick.
        If your view never changes you're following the wrong leader

      2. DanH | Nov 04, 2007 03:41pm | #20

        (You can even temporarily ground one of the problem boxes and see if the others become grounded, to see how wide-spread the problem is.)
        If your view never changes you're following the wrong leader

      3. renosteinke | Nov 04, 2007 05:48pm | #21

        So, how does one further identify a problem like yours? Well, first, let's eliminate that 'ghost voltage' issue. Ever have a car battery read 12v, yet fail to start the car? Notice how the headlights dim almost instantly? The 'true' voltage is read when there is a load applied.
        Same with a 'ghost' voltage. Rather than use an electronic meter - which can be fooled by a lot of things - measure using a "Wiggy," a meter that uses a solenoid to move a bar across a scale. The load of the solenoid requires some power .... not much, but something .... so it will not read 'ghost' voltages. Still, a "O" voltage reading does not mean that the problem has gone away. There is still the question of having a good ground path. Let me illustrate the problem with an example:
        We 'know' that the ground rod has no role in clearing faults (that is, making a breaker trip) because the resistance is too high; there is no way for that rod to carry more than a few amps. Our breakers can work, because the ground wire is connected to the neutral at the main panel. Installed properly, the ground wire provides a path of essentially no resistance back to the PoCo. No resistance = lots of amps flow = tripped breaker.
        You need to find where there is a lot of resistance in the ground wire part of the circuit. While this can require some special equipment and training to find the problem, there are some things you can do yourself. The first is to realize that the problem can be at any point in the circuit; it may even be the accumulation of several small problems. You can check EVERY connection back to the panel. Is the screw on the buss tight? Are the wires securely twisted / crimped / wire nutted together in each box? Is there a little wire that directly attaches the receptacle to the ground wires from the Romex? It's not unusual for one of these wires to be 'almost broken' or just resting within a wire nut. That's a problem to fix. If you're taking the voltage measurement at the receptacle, using the same slots that plugs use .... maybe your meter probes are not making god contact. Or, the only 'grounding' connection it through the screw that's holding it to the box. Not a good way to do it. You need to open the box, and you need that little pigtail. It's also not impossible that the fault is within the receptacle. Beyond this, we're well out of the training of homeowners, and -sadly- far too many electricians.

        1. brucet9 | Nov 04, 2007 09:01pm | #23

          I really appreciate your thorough replies to peoples' questions.You have expanded the possibilities for my low-voltage-to-ground problem beyond the specifics of my situation to also cover 3-prong outlets with ground screws on them and grounding wires that are actually inside the box - helpful for other situations as well. Thanks."Rather than use an electronic meter - which can be fooled by a lot of things - measure using a "Wiggy..."
          Apparently analog is sometimes better than digital."...the problem can be at any point in the circuit; it may even be the accumulation of several small problems."
          16ga copper wires pinched against galvanized boxes by steel clips in a daisy-chained circuit; add 40 years of oxidation. What could possibly go wrong?Looks like I can improve the ground connections if I pry off the clips and twist/crimp the ground wires of each leg of NM together and make sure that all is tight in the panel. If that fails, I'll call in a pro.BruceT

  6. edlee | Nov 03, 2007 11:49pm | #16

    I lived and worked in Northern California for a while. Sometimes during demo I'd see #16 bare wire run around near the old NM and attached to the outside of the boxes, usually by wrapping around one of the screws on top that holds on the side of the box.

    Boxes were often finished black.  Anyone know why they used to make'm that way?

    Ed

    1. DanH | Nov 04, 2007 12:55am | #17

      > Boxes were often finished black. Anyone know why they used to make'm that way?Actually, it was the soot from the fires.(Black wouldn't show as much if the box wasn't entirely covered by cover plate, etc.)
      If your view never changes you're following the wrong leader

    2. brucet9 | Nov 04, 2007 08:25pm | #22

      "Boxes were often finished black. Anyone know why they used to make'm that way?"Coming from an industrial paint mfr background, I would suggest that boxes in the early days would have been painted to prevent rusting because painting was cheaper than galvanizing and they were probably painted black because black is the cheapest paint to make.BruceT

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Mortar for Old Masonry

Old masonry may look tough, but the wrong mortar can destroy it—here's how to choose the right mix for lasting repairs.

Featured Video

Builder’s Advocate: An Interview With Viewrail

Learn more about affordable, modern floating stairs, from design to manufacturing to installation.

Related Stories

  • Fire-Resistant Landscaping and Home Design Details
  • A New Approach to Foundations
  • A Closer Look at Smart Water-Leak Detection Systems
  • Guest Suite With a Garden House

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data