Plumber help needed. Don’t laugh.

| Posted in Construction Techniques on September 28, 2006 01:31am

I recently had a house inspection and they cited my water heater pressure relief valve as faulty. I called the inspector to find out how he tested it. It turns out he didn’t test it because he said that he ‘never opens the valve on water heaters because sometimes they’ll never shut off again. There was evidence of it leaking because the bottom of the tube had corrosion on it, so I cited it as faulty”.

Anyways, I don’t know anything about plumbing and the valve did leak last year for awhile but stopped at some point.

My question: should I just replace it or try to prove that it is functional?

My next question: If I replace it, is there anything I need to know, or should I just crank it off and put a new one on?

My plumbing history: Not good. I coulda made a three stooges episode when I changed the element in my last hot water heater.

Facts: I’ve got a gas hot water heater. It is installed too close to the furnace. I don’t know how it passed inspection. The place is a three years old condo that I recently sold.

blue

 

Reply

Replies

  1. User avater
    IMERC | Sep 28, 2006 02:00pm | #1

    change it..

    cake and pie..

     

     

    Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming

    WOW!!! What a Ride!

    Forget the primal scream, just ROAR!!!

  2. User avater
    BossHog | Sep 28, 2006 02:55pm | #2

    I'd probably just replace the thing. They're only about 10 bucks, I think. Not enough to be worth fighting over.

    Life is like a dog-sled team. If you aren't the lead dog, the scenery never changes.
  3. DanH | Sep 28, 2006 02:59pm | #3

    Is it going to cause a problem if it dribbles for a few days while you get around to changing it? If not, you can have a shot at testing.

    If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison
    1. blue_eyed_devil | Sep 28, 2006 03:06pm | #4

      Dan, I actually can't test it. The lever is so close to the furnace plenum that I can't flip it up to test it. I would if I could. If it leaks, then I'd change it.

      If I change it, do I have to do anything special, like shut off the water?

      blue 

      1. User avater
        BossHog | Sep 28, 2006 03:09pm | #5

        You'd damn well better shut off the water, unless you want an extended 110° shower.(-:
        Politicians are the same the world over: they promise to build a bridge even when there is no river [Nikita Khrushchev]

      2. User avater
        ErnieK | Sep 28, 2006 03:26pm | #6

        That would definitely be interesting.  By all means shut the feed water off.  Then relieve the water pressure by flipping the valve.  To bad you can't test it, but best to change it.  Very simple procedure, just don't bust it out.

        1. blue_eyed_devil | Sep 28, 2006 03:33pm | #8

          Very simple procedure, just don't bust it out.

          Now you have me worried!

          How do I "not bust it out"? I'm thinking I have to get a big wrench and twist the valve, but I don't have any way to get inside and stabilize whatever's in there.

          This seems more complicated than framing an irregular roof with multiple planes, multiple heel heights and  wandering wall heights.

          blue 

          1. MSA1 | Sep 28, 2006 05:42pm | #22

            I've had success in the past with old pipe fittings be actually trying to tighten it just a little to get it moving. then try backing it out.

            If it breaks in the tank you may be able to get the remainder out by tapping the piece away from the threads (picture making the hole smaller). Once the piece is folded in you should be abe to remove it. But lets not think about that now. It'll come out no problem (just keep telling yourself that the whole time your doing it). 

          2. User avater
            ErnieK | Sep 28, 2006 09:58pm | #27

            When I said bust it out I was referring to the typical "grab the cheater bar and give it a turn...lol!  I know they can be tight and in tough positions but they are actually easy to change. 

            If it won't turn easily, use a small pipe wrench and tap on the end with a hammer.  The jarring generally breaks the corroded threads.  If the water is off, lift the valve and let it bleed just enough to work.  

          3. User avater
            IMERC | Sep 28, 2006 10:10pm | #30

            or tighten it a little bit 1st...

            tapping might break something... 

             

            Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming<!----><!----><!---->

            WOW!!! What a Ride!<!----><!---->

            Forget the primal scream, just ROAR!!!

          4. User avater
            ErnieK | Sep 28, 2006 10:29pm | #31

            This is true.  I have installed hundreds and it never ceases to amaze me the lengths people will go to install or remove a tapered fitting.  The "grab a bigger wrench" theory is so prevalent! 

            Nevertheless, tapping gently almost always works if someone has wrenched it pretty good.  Even those lovable factory lugs!

          5. User avater
            IMERC | Sep 28, 2006 10:50pm | #32

            like if Blue opens that drain valve....

            if it won't close and he has to change it and it's plastic... and it snaps off...

            hope he has an internal pipe wrench... 

             

            Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming<!----><!----><!---->

            WOW!!! What a Ride!<!----><!---->

            Forget the primal scream, just ROAR!!!

      3. Lefty | Sep 28, 2006 03:26pm | #7

        Replaced my drain valve a week ago.

        1) Turn off gas valve ( or electric breaker)

        2) Run hot water in sink or somewhere to get heater and contents cooled off.

        3) Turn off cold water inlet

        4) Drain out water

        5) Replace safety valve

        6) replace drain valve ( my suggestion, use a ball valve and add a hose connection for easier flushing.) This plastic POS on all heaters should be outlawed.

        7) Re-open water inlet, be sure to close hot water valve in sink. don't ask.

        8) re-open an re-light gas.

        It's not often that I can contribute but I try to when I can. Hope this helps. Its pretty simple and use lots of pipe dope on fittings.

         Long time lurker, new profile

        1. blue_eyed_devil | Sep 28, 2006 03:34pm | #10

          Lefty, your list seems right for the drain valve, but I'm working on top of the water heater. I'm thinking that I don't need to drain it. Am I off track?

          blue 

          1. Lefty | Sep 28, 2006 03:46pm | #16

            You will need to drain only enough to get it below the vent valve level but if you're going to all that trouble, the drain valve is a piece of cake to change and if it leaks after you finish the vent, or if it breaks off like mine did, you will have a 10 min. panic to get it under control.

            My drain valve was leaking a little at the threads, we had cooled the tank and were getting the garden hose ready to drain the heater, no water shut off yet. The drain broke off clean and they can fill laundry room floor in a hurry under pressure.

            Just a suggestion. Good luck. I still hate plumbing but I did stay at a Holiday Inn Express one time. <g>

             Long time lurker, new profile

          2. User avater
            IMERC | Sep 28, 2006 03:59pm | #17

            shut the heater down..

            shut off the water to it and let off the pressure...

            unscrew it...

            pipe dope the new one and screw it in...

            hook up the drain line..

            turn the water on...

            go to a faucet some place in the air and bleed off the air.. let the hot water flow fer a bit...

            relight the heater and yur good to go... 

             

            Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming<!----><!----><!---->

            WOW!!! What a Ride!<!----><!---->

            Forget the primal scream, just ROAR!!!

          3. blue_eyed_devil | Sep 28, 2006 04:12pm | #18

            Imerc, it sounds so simple that I will try to do that.....after I get back from my weekend duck missing excursion. I can't find my camera to take a picture of the situation. It's pathetic. I can't believe that the plumbing and heating guys would place the two together so closely. There is plenty of room in the closet to space them out a foot or more, but they chose to put them so  close that the lever hits the ductwork.

            RJW, Before I do anything, I'm placing a call to the original plumbing and heating contractor and asking them if they'll come over and explain how/why they installed the units so close. I already tried to move them a 1/4 " or so and they didn't budge. I'd have to re do the gas line and supply lines to get more room. I'm thinking that this might be a health and safety violation and am hoping the contractor has enough character to take care of business.

            I shoulda hired a home inspector before I moved in...

            blue 

          4. User avater
            IMERC | Sep 28, 2006 09:20pm | #25

            DO NOT change or open the drain valve unless you have spare worm cans..

            drain off as much is needed using the T&P valve before ya change it....

            rag the installerd and get them to deal with it...

              

             

            Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming<!----><!----><!---->

            WOW!!! What a Ride!<!----><!---->

            Forget the primal scream, just ROAR!!!

          5. DanH | Sep 28, 2006 04:40pm | #19

            He did mention changing the T&P valve, but you kinda had to look for it.The reason for changing the drain valve is that there's a chance that, once it's opened, it won't close again either. This is less likely than the similar problem with the T&P valve, but not uncommon.On the other hand, totally draining the tank takes a long time, and removing the drain valve and it's nipple can be even more challenging than removing the T&P valve.

            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          6. MSA1 | Sep 28, 2006 05:42pm | #23

            You need to drain it below the valve.

          7. User avater
            rjw | Sep 28, 2006 07:35pm | #24

            Different jurisdictions have different requirements (and/or enforcement) of the "above a drain" / "outside" rules

            Youth and Enthusiasm Are No Match

            For Age and Treachery

          8. JohnSprung | Sep 28, 2006 09:37pm | #26

            If you're only doing the T&P, then you only need to drain enough to keep water from coming out of the hole at you. 

            The other thing you have to consider is whether the supply valve really shuts off all the way, or does it let a little thru?  Draining a couple extra gallons may be enough to get the job done before the leakage by the supply valve makes a mess for you. If it's really bad, you may want to leave the hot running a little in the sink the whole time.

            Opening the bottom drain valve once a year to get the crud out is a good idea.  Replacing the crappy plastic drain valve with a good one makes that safer and easier.  So, as long as you're messing with the W/H, consider doing all that at the same time. 

            BTW, how old is the heater itself?  Maybe swap it out now, so it doesn't crap out on you in the dead of winter?  Is there an expansion tank in the system?  That'll take care of those pressure spikes that may make the T&P dribble.  We can always think of more ways to spend your time and money....  ;-)  

             

            -- J.S.

             

          9. User avater
            CapnMac | Sep 28, 2006 09:58pm | #28

            but I'm working on top of the water heater. I'm thinking that I don't need to drain it. Am I off track?

            Yeah, a little bit.  The relief valve on top (no mandated to be on the sides) is more properly called a "TP" valve, as it is designed to relieve either pressure or temperature exceeding the WH's specs.  The drain lines from a TPV are copper for that very reason (running 180+º water can be tough on PVC).

            Unless, of course, you are in a jurisdiction that does not require a drain line from the TPV.

            However, since it's a valve that "sets," you will need to darain the tank at least some amount just to get it out.  (If it's on the side, you for sure want the tank drained to that level, unless you like mopping.)

            Given your description of "too close" to the furnace, I'm actually guessing that closign the CW at the cut off, and draining the DHW will be to your advantage.  That's because, with the CW supply loose, and the tank mostly empty, you ought to be able to give it enough of a turn to rotate the TPV to a better spot.

            However, if this is a gas heater, make sure that turn does not obscure the gas/pilot contorl, or the pilot inspection window (don't ask).

            Hope that has not made it clear as mud.Occupational hazard of my occupation not being around (sorry Bubba)

      4. DanH | Sep 28, 2006 03:33pm | #9

        If it's that cramped you're gonna have fits changing it. The valve has a temperature sensor that extends about 6 inches into the tank. Practically speaking you need about 10 inches of clearance above the valve (if mounted vertically) and 18-24" around it to swing a wrench. You may need to remove the duct if it's that tight.The water supplying the water heater needs to be turned off. Also turn off the water heater heat (flip breaker or turn gas valve to "pilot" or whatever) so you don't have problems with thermal expansion. Open the lowest hot water faucet in the house to relieve pressure, then drain a couple of gallons from the heater drain valve. (Caution, the water will be VERY HOT!)Or call a plumber.

        If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

        1. brownbagg | Sep 28, 2006 03:37pm | #12

          note: here the pop off valve has to be plumbed to outside.

        2. Stray | Sep 28, 2006 03:41pm | #13

          Can you pop the flue off the WH and rotate it to get better access away from the duct? 

           Ithaca, NY  "10 square miles, surrounded by reality"

        3. User avater
          jagwah | Sep 28, 2006 03:43pm | #15

          Emory cloth the rust and drips off the offending pipe. Then clean all around the waterheaters sensor. You might even install a waterheater blanket.

           All this so it looks like you replaced the sensor and even got a new waterheater. Have 6 or so Killians Red beer icing in a 5 gallon bucket in the path to the waterheater. Put on some music like the sounds of a NASCAR race in the background.

          Invite him for a late afternoon inspection......yuck! I gross myself out 

  4. User avater
    rjw | Sep 28, 2006 03:34pm | #11

    FWIW, I don't call out a situation like that as "defective.".

    In fact, to me, the drip marks/corrosion indicate the opposite: that it is working as intended

    It is not unusual for there to be a pressure surge in municipal systems and/or water heater temps which cause the valves to open briefly

    If you can't trip the valve because of its location, you're going to have to shift the water heater to replace it.

    FWIW: HI's don't test 'em for the reason he gave.

    Neither do any plumbers I know, even though the tag on the T/P valves call for them to be checked by a plumber every 3 years.


    Youth and Enthusiasm Are No Match

    For Age and Treachery

  5. FastEddie | Sep 28, 2006 03:43pm | #14

    Leave the valve alone and change the drip tube.

     

    "When asked if you can do something, tell'em "Why certainly I can", then get busy and find a way to do it."  T. Roosevelt

    1. DanH | Sep 28, 2006 04:41pm | #20

      They don't call you Fast Eddie for nothing!
      If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

  6. MSA1 | Sep 28, 2006 05:37pm | #21

    I'd change it. The problem is that if its not opened up regularly it could have corrosion built up on it and if you open it now, it may not shut off completely.

    Kind of like sink shutoffs and breakers (both, i've been told should be turned on and off yearly). 

  7. JJV | Sep 28, 2006 10:04pm | #29

    Bloody DIYers.  Call a pro, will ya??  ;-)

    Tongue firmly in cheek...

     

    Maybe someday I'll know a little something.

  8. ccal | Sep 28, 2006 11:40pm | #33

    Leave it alone. Theres nothing wrong with it. Tell them to call the inspector and ask why it is labeled as faulty when it was never tested. They all drip a little every now and then. Could even be condensation collecting on or in the line.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Fast, Accurate Wall Framing

A rear addition provides a small-scale example of how to frame efficiently.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Podcast Episode 693: Old-House Hazards, Building Larsen Trusses, AI in Construction
  • FHB Podcast Segment: Finding Hazardous Materials in a Fixer-Upper
  • A Classic Paint Sprayer Gets a Thoughtful Refresh
  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in