Pertz | Posted in Energy, Heating & Insulation on May 8, 2005 02:22am

One single pole switch, one 3-way switche and one four way switch were to be ganged at a location where leaving a living/dining space, entering a hallway; living and dining lights turn on/off, hallway light on/off.

The center of the three switches appeared to control nothing; certainly not the hallway light that was intended. We were unable to locate any other fixture controlled by that switch. We pulled the box apart, and found that the switch was supplied by 14/3 w.g. The switch device is single pole. The white wire is nutted to the rest of the neutrals in the box. The red and black are in and out of the switch. We started to put a meter on the wires, to see if they appeared controlled by other 3/4 ways around the place. Initially I got 110 on one side of the switch and 0 on the other when “off”, and 110/110 when “on”. Then the other guy started flipping other switches. At one point, on the “off” side, I got a reading of around 15 volts. Later, I tried just putting the meter across the switch itself when “off”, and got about 55 volts between the hot and the other side.

Two questions: first, of course, what’s the source of these weird voltages? Is there a neutral current feeding into this somehow? Found myself totally baffled. Second, would there ever be a situation in which a realdeal electrician would have the hookup I described, i.e., white to neutral, red and black to single pole switch.? I couldn’t think of a situation where that would be done. The closes I could come was: if the power from source is entering the light fixture first, and you want to switch that fixture and also feed power through to others. But then you’ld have the power into the switch itself running from a pigtail, so as to supply the other devices. That doesn’t happen here; power direct to switch, nothing else attached to it. I had gotten very big speeches from the electrician about what pros he and his guys are; all licensed, all trained, blah blah. Any excuse for any of this???

 

Thanks guys.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    BillHartmann | May 08, 2005 03:18pm | #1

    " I got a reading of around 15 volts. Later, I tried just putting the meter across the switch itself when "off", and got about 55 volts between the hot and the other side.

    Two questions: first, of course, what's the source of these weird voltages?"

    I am Karnac. Let me hold up the envelope that has been sealed in an old mayonise jar.

    The answer - Digital Voltmeter.

    Opening the envelope the question was, what did Pertz use to measure the voltage on his "3-way switch".

    That is a common problem of digital voltameters. They are vary high impedence and the wires will act as antennas and sense voltage via capacitive coupling to other circuits.

    If you put a light bulb as a load and measure across that it would have been zero, at least for the 5 volt case. The other case (55) could have had to lights in series. Don't know how many mistakes ther might have been.

    "Second, would there ever be a situation in which a realdeal electrician would have the hookup I described, i.e., white to neutral, red and black to single pole switch."

    There is one that I can think of where a SINGLE 14-3 cable would be used as in a switch leg. That is if you want to be able to add X-10 devices. They require a neutral. However, the neutral should not be tied to anything in that case.

    Now there are all kinds of applications where you would have a 14-3 and another cable, either 2 or 3 wire connected.

    A common application is for switched receptacles in a room. Power comes in on a 14-2, Then the 3 wire cable going to the receptacle has both a alway hot (black) and the switch hot (red).

    In my kitchen I have a pair of switch as the entrence. 14-2 in to the box. Then one switch that controls can lights over a eating bar via 14-2. Then a 14-3 that feeds the center kitchen light and then the light 14-2 to the over the sink light.

    " I had gotten very big speeches from the electrician about what pros he and his guys are; all licensed, all trained, blah blah."

    But what is he doing to fix it. THAT IS THE QUESTION.

    Seems like an "honest mistake". I could see how it would happen. That is a fairly busy box. And specially if he had a "help" install the siwtches.

    1. Pertz | May 08, 2005 03:39pm | #2

      NOT a digital meter: an old, little radio shack piece of crap multimeter i carry in the truck all the time. i think it cost about eight bucks about twenty years ago. Not a digit to its name.

      You mention that there could be lights in series that account for the voltages. tell me more, why would lights operating on the circuit cause that??

      None of the kinds of circumstance you describe for use of a three wire cable seem to apply here. this cable is feeding nothing downstream or separately that would account for it.

      As for "what is he doing to fix it"; that's my worry. I've seen plenty of situations over the years where things seem to work correctly, and, when you actually look at what was done, although it "worked" it was dangerous as hell and totally wrongly wired. E.g., neutrals just hooked to any old ground. I figured if I understood what had happened here i'd have half a chance of knowing whether he really repaired the situation, or just found a work around that makes it look right while staying wrong. And while, sure, anybody can make errors (you're talking to a real pro in that department) I have come to generally mistrust this man and would like some way to confirm he's actually corrected it, not just "got it to work".

      I do appreciate your reply...this is a bit thick.

      Pertz

      1. User avater
        BillHartmann | May 08, 2005 04:23pm | #3

        "As for "what is he doing to fix it"; that's my worry. I've seen plenty of situations over the years where things seem to work correctly, and, when you actually look at what was done, although it "worked" it was dangerous as hell and totally wrongly wired. E.g., neutrals just hooked to any old ground."I know what you mean. Just before I moved into my house I remember the electricans helpers, that where installing final switches and lights comment that they had a bad piece of cable and the electrican was on vacation, but they found a way to work around it.Did not dawn on me that there would be any problem until 10 years later when I was doing some painting and I removed the cover plate in the living room and the kitchen lights flickered.Seem that there was a nail through the 14-3 cable that I mentioned before. They cut the ground and neutral wires at that switch. Then at the light fixture then cut loose the ground and neutral on the bad cable and tied the neutral to the ground wire for the cable that continues on.That only worked because 2 boxes later there was a multi ganged box that had switches on differrent circuits. The grounds for each circuit where just pushed into the box and just touching. (Now code requires that all ground in a box be tied together.).An analog VM can also have false readings, but much less likely, specially the cheap ones.What you need to do is to go the other switch (I think that there was just another 3-way on it and not a 4-way) and ID the wires there and also ID the wires at the light.You will probably end up pulling all of the connections loose to help ID them. But don't do that yet and make a record of what you see at those 2 locations.BTW, do you have access to a tone generator/detector? Now needed by handy for IDing the wires.Here is a link showing all of the combination of ways that a 3-way circuit might be wired.http://www.selfhelpandmore.com/switchoutlet/3way/index.htm

  2. User avater
    SamT | May 08, 2005 04:34pm | #4

    Pertz,

    I would make a testing device from an outlet. Break of the connecting tab on the power side of the duplex outlet, wire one outlet to the hot side of the switch and the other to the switched side. Plug two lamps in.

    Make a truth table:

    Switch 1 Other Switch Hot Lamp Switched Lamp Controlled Fixture
    ON OFF ON OFF ON OFF ON OFF ON OFF
    X   X   ? ? ? ? ? ?
    X     X            
      X X              
      X   X            

    When filled in, circuit should be obvious to the most discerning mind.

    SamT

     

  3. DanH | May 08, 2005 04:43pm | #5

    The low voltages probably represent capacitive pickup. Even with a cheap analog meter you can still get some capacitive pickup, especially when a live black wire is fed in the same jacket as the wire you're metering.

    However, they could represent leakage due to a bad connection somewhere.

    The wiring of that switch is (potentially) legit, if odd. Basically it's a switch leg, but whoever wired it (if this was old work I'd suspect a college professor) used 3-wire cable so as to maintain a true neutral, even though code doesn't require that.

    There is a part that is slightly illegit, though -- the wiring of the neutral to the other neutrals in the box. This is generally bad practice, though I don't think it's necessarily a violation of code.

    1. Pertz | May 10, 2005 06:40am | #6

      Just got me curious, but why would connecting all the neutrals in the box (assuming, as in this case, its the same circuit) be a no-no? and how would it otherwise be done?

      1. User avater
        BillHartmann | May 10, 2005 10:37am | #7

        "(assuming, as in this case, its the same circuit) be a no-no? "That is the basic policy making sure that they are all on the same circuit.When you have a large gang box, with a combination of circuits with switch legs and others with power feed to the switch. Then throw in a couple of 3 or 4-ways and the only way to make sure that circuits are not crossed is to keep the neutrals separate.

        1. Pertz | May 10, 2005 03:29pm | #8

          Sorry, I'm being really thick here: if there are two circuits in the box, ok, you nut together the neutrals for the separate circuits. how do you separate beyond that? Or are we talking about not using white wires for switch legs?

          1. User avater
            BillHartmann | May 10, 2005 04:41pm | #10

            "Or are we talking about not using white wires for switch legs?"Who said that we have switch legs?In one 3 gange box you might have one single pole switch leg, one 3 way with the with power at that switch and with a cable that extends it along with the netural and traveler to the other end where the light connection is made, and another 3 way where both power and lights are connected at that end.And each of those 3 different switches might be feed from 3 different circuits.And if I counted right you have 7 different "white" wires, 2 of which should be remarked hots, but often arent'.

          2. Pertz | May 11, 2005 04:36am | #11

            gotcha, thanks. the white/hot program is a real problem...

      2. DanH | May 10, 2005 04:25pm | #9

        As a general rule, for EMI reduction, load calculations, etc, the net current flow in any piece of romex should be zero. That is, as much current should be coming back as goes out. If you tie neutrals together then neutral current can end up flowing back a different way from the way the "black" current is flowing, upsetting the balance in the cable. Among other things this can create fairly strong electromagnetic fields that can cause radio interference, and which are not generally considered good for humans.Also, if you tie neutrals together it can make troubleshooting a confused circuit like the one discussed even more difficult.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Two Ways to Test Windows

New devices showcased at the Builders' Show make it easy to measure glass performance, u-factor, SHGC, window thickness, and more.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast Episode 695: Saving Bricks, Cut-and-Cobble Insulation, and Waterproofing Foundations
  • FHB Podcast Segment: Waterproofing Below-Grade Foundation Walls
  • Midcentury Home for a Modern Family
  • The New Old Colonial

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 333 - August/September 2025
    • A Practical Perfect Wall
    • Landscape Lighting Essentials
    • Repairing a Modern Window Sash
  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data