Recessed Lights – How many on 15 amp

Shecky | Posted in General Discussion on February 16, 2006 04:26am
I am in the middle of a basement remodel. I have 18 recessed lights that I would like to split on two different switches.  Is this to much for one 15 amp circuit? If so and I break these lights into two circuits, can you have two different circuits in the same junction (switch) box to control the lights?

Thanks

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    maddog3 | Feb 16, 2006 05:01pm | #1

    why don't you use those two circuits........ no problem in the same box ........it will provide some lighting if one circuit should trip or need maintenance ?

    or some one doesn't try to turn you on while your working on them with a single circuit

  2. User avater
    G80104 | Feb 16, 2006 05:07pm | #2

      You could homerun a leg of 14/3 off the switch box back to the panel. This would give good results.

  3. DaveRicheson | Feb 16, 2006 05:23pm | #3

    You are good for 1440 watts on one 15A/120V circuit. Depending on your lamp size you could use just one circuit to the switch and split it to two switch legs.  I would not go over 75W bulbs with this method (1350W).

    Only one home run to make, and half the wire.

     

    Dave

  4. moltenmetal | Feb 16, 2006 09:42pm | #4

    Code rule up here in Canada is that you may have no more than 12 receptacles or fixtures or combinations thereof on a single circuit.  Switches don't count.  Don't know what your own rules are.  If it were my house, the 14 fixtures would be served with two different circuits.

    1. Shecky | Feb 16, 2006 10:27pm | #5

      It looks like I will divide the lights into two circuits.  Does anyone know if it is legal to have switches from two different circuits in the same gang box?  Potentially, you could open one breaker at the main panel and still have live wires in the box. Do the grounds get tied together or should they be separated by circuit?

      1. User avater
        maddog3 | Feb 16, 2006 10:52pm | #6

        ....yes you can have two circuits in one box...its a multi-wire circuit if you share the same Neutral...yes you tie the grounds together........yes there will be voltage present if you only turn off one breaker....

        1. User avater
          mfmalm | Nov 08, 2020 04:46pm | #26

          YOU SOULD KEEP THE NEUTRALS ISOLATED. A NEUTRAL CONDUCTOR SHOULD NOT SHARE CURENTS FROM ANY OTHER CIRCUIT. BARE GROUNDS SHOULD BE TIED TOGETHER. THEY ONLY CARRY FAULT CURENTS FOR SAFTEY.
          MARVIN F. MALM PE(ret)

      2. moltenmetal | Feb 16, 2006 11:43pm | #7

        Again, don't know your local rules, but here in Canada you can run a single piece of 3-wire to supply your 2-gang switch box, with the black supplying one switch, the red supplying the other, and the single neutral serving both circuits.  I presume you meant "neutral" when you said "ground", because you always tie the bare ground wires together! 

        Using a dual breaker with a tie bar between them to serve a three-wire cable is always a good idea, to minimize the risk of having one live and one dead circuit in the box as you've mentioned.  That said, I've checked with the local authority and up here the tie-bar connected dual breaker is not code required unless it serves split receptacles.  The advantage of doing it with separate breakers is that if you overload one side, you don't lose lights to your entire basement. 

        If you choose to use separate breakers, you must make sure that the two you use aren't supplied from the same phase (i.e. the same buss bar in the panel), otherwise you'll be overloading the single neutral in your three-wire supply cable!  If you don't know what I'm talking about, run two separate 2-wire feeds and keep the neutrals separate in your switchbox.  It's a little more work to pull 2 wires instead of one, a little more wasted copper for the extra neutral and ground wire, but given the price of 3 wire versus 2 wire cable it's pretty much exactly the same money.  Why that is so is a mystery to me- 3 wire should be cheaper than 2 pcs of 2 wire of the same length!

        1. Shecky | Feb 17, 2006 03:43pm | #8

          Thanks for all of your hellp.  I think I have a good understanding of what I need to do.

          1. User avater
            maddog3 | Feb 17, 2006 05:07pm | #10

            although.....you may want to use two separate boxes if you are considering dimmers...

          2. fingers | Feb 17, 2006 06:39pm | #16

            Don't forget, you can always decrease the amount of load on the circuit by using compact florescent bulbs.  That complicates things as far as dimmers go.  You can get CF bulbs that will work on dimmers but they are pricey.

            Using CF bulbs is good for other reasons too like increasing the amount of light without exceeding the limits for the wire, breaker, cans, etc.  not to mention the electricity used.

        2. User avater
          BillHartmann | Feb 17, 2006 04:32pm | #9

          "Again, don't know your local rules, but here in Canada you can run a single piece of 3-wire to supply your 2-gang switch box, with the black supplying one switch, the red supplying the other, and the single neutral serving both circuits. I presume you meant "neutral" when you said "ground", because you always tie the bare ground wires together! "What do you do in a box that has 3 or 4 3-way/4-way switches in it?You would have different "supply" cables for different switches and each might be on a different circuit.

          1. moltenmetal | Feb 17, 2006 05:54pm | #11

            Correct me if I'm wrong, Bill, but if you still had the supply cable(s) entering the switch box first, it makes no difference whether the switched circuits you're supplying are switched with ordinary, 2-way, 3-way or 4-way switches.  What changes is the wiring between the switches and the fixtures (and the other switches).   Which circuit each group of light fixtures is supplied by is determined at the supply end.  Obviously you need to stay clear of cross-connections between circuits if you have multiple 3- and 4-way switches sharing common boxes.   

            The point I was getting at is that here in Canada, the only place I even vaguely know the code rules, you are permitted to have circuits supplied by more than one breaker sharing a common box, unless that box is serving a split receptacle.  That's what the OP was concerned about when it was suggested he supply his 14 fixtures with 2 circuits rather than one.  Supplying more than 12 fixtures with a single circuit would be a code violation here in Canada regardless what the ratings of the fixtures were.

          2. User avater
            BillHartmann | Feb 17, 2006 06:23pm | #14

            "The point I was getting at is that here in Canada, the only place I even vaguely know the code rules, you are permitted to have circuits supplied by more than one breaker sharing a common box, unless that box is serving a split receptacle."I thought that is what you where saying.But you have a box with multiple way switches in then is very likely that you have circuits being feed from different breakers.In fact with the condition I described to Tim (based on a real house) you have maybe 8 different boxes, each with 2-4 switches that are all "common" in that one each box shares a circuit with one or more other of the eight. Way too many lights and to large any area to be on one circuit.I mapped out the breakers for that house, but don't remember the number, but I think that it was probably 4 different circuits.

          3. HeavyDuty | Feb 18, 2006 05:19am | #22

            "The point I was getting at is that here in Canada, the only place I even vaguely know the code rules, you are permitted to have circuits supplied by more than one breaker sharing a common box, unless that box is serving a split receptacle."

            He is talking about the Ontario Code and he's speaking Canadian hence the confusion. We speak the same language so I can tell you what he really meant was you could run two separate circuits in the same box so you didn't have to be concerned about

            What do you do in a box that has 3 or 4 3-way/4-way switches in it?

            I don't have to be concerned about the situation you outlined since I have a better solution, I always carry a flashlight with me.

          4. Mooney | Feb 17, 2006 05:57pm | #12

            here the whole thing would be turned down

            Tim

             

          5. User avater
            BillHartmann | Feb 17, 2006 06:15pm | #13

            "here the whole thing would be turned down"Why and based on what rules?You have an entrance hall and it in you have a box a the front door with which includes a 3-way for the hall area and 3-way for the stair lights. At the top of the stairs is the other 3-way along with another 3-way for ligths in an upper area office. The other 3-way is at another stairway into the area. And in both of those boxes in the upstairs there are switches for other lights in the area.Now back to the entracne hall it is also controlled by a 4-way at the door from the garage and another 4-way at the first floor hallway. And in that 2nd box is also a 3-way with a switch at the other end. And at the ot her end is switches for lights in that area.At back to the box with the switch for the stairs there is also a 3-way for the dining room lights. The other end of the 3-way at the door way from the kitchen.Are you saying that all of those lights have to be off one circuit or are you saying that in Arkansas that they just have one 100 watt bare bulb with a pull chain and hang in the middle of the house where it will shine in all rooms.

          6. Mooney | Feb 17, 2006 09:54pm | #18

            Are you saying that all of those lights have to be off one circuit or are you saying that in Arkansas that they just have one 100 watt bare bulb with a pull chain and hang in the middle of the house where it will shine in all rooms.

            LOL, thats funny right there .

            Only 12 gauge wire is approved for all living areas serving multiple devices. And you guessed it , 20 amp circuits.

            Existing circuits are ok but they cannot be added to without up grading .

            Tim

             

          7. User avater
            BillHartmann | Feb 18, 2006 03:45am | #21

            Moltenmetal implies that all of the circuits in a box have to be on the same circuit.I quested that. And mentioned when you have multiple ganged boxes with 3 and 4 way switches in them (indicate that part of that circuit will be in an other box) and when this applies to home with several different places where there are these multiple gang boxes with 3/4 way switches that you are going, end up with at least one box that is feed from several different branch circuits.Your reply was that it was illegal in Arkansas, without givin an details.So my coment was how can you guarantee that all of the interconnected lights will be on one circuit other than limiting the house to one light.

          8. Mooney | Feb 18, 2006 08:00am | #24

            Your reply was that it was illegal in Arkansas, without givin an details.

            So my coment was how can you guarantee that all of the interconnected lights will be on one circuit other than limiting the house to one light

            Its late and Im not going back to make sure what he said cause were not arguing anyway .

            I understod or have the understanding that hes going to be adding on to what he has now .

             

            The problem arose when I inspected a house with 15 amp circuits and they used 14 gauge wire. I started counting outlets and went to the book and found that it was non compliance .[I was self training on the job <G> }  Then I called it in and got the meetings and had the state inspector on the job the next morning . I was going to allow it if I could get comfortable with the number of outlets but the code didnt help me there. Neither did the state .

            Their reason was the homeowner doesnt know what he or she has and they could tie on to it like this author . Theres power , lets use it . I agreed with that . They could plug in an electric heater and I agreed with that too.

            The 14 gauge wire was  turned down.

            If you tie on to a circuit you must be responsible for the whole thing back to the box or what ever you add to it . Whoever does it needs to address the responsibility.

            I didnt go into all that because its probably a moot point , cause its not here. Only cause you asked .

            Tim

             

          9. moltenmetal | Feb 20, 2006 10:06pm | #25

            Sorry if I was unclear, and thanks to TomC for clarifying.  That was my point:  you are permitted, here at least, to have multiple circuits (i.e. supplied by multiple breakers) in a common box.

          10. User avater
            maddog3 | Feb 17, 2006 06:28pm | #15

            yah, why Tim?

    2. Scott | Feb 17, 2006 07:12pm | #17

      Actually, Canadian code, or at least the BC ammendements to the code, allows for the 1440 watt limit for entirely fixed loads like lights. For variable loads like plugs, or mixed loads with lights and plugs, you must stick to the 12 device limit. So if you're using fixtures that are clearly rated for a 100 watt limit you could have 14.

      Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

      1. moltenmetal | Feb 17, 2006 10:07pm | #19

        Thanks for pointing that out!  Does that apply to permanently-mounted fixtures like ceiling cans only? 

        I re-read the OP's post and he said 18 fixtures, so no different for him, but good to know for future.

        1. Scott | Feb 18, 2006 03:18am | #20

          >>>Thanks for pointing that out!  Does that apply to permanently-mounted fixtures like ceiling cans only?

          I forget the exact code excerpt, but I believe that the rule applies to any fixed load, like heating and lighting (no plugs).

          >>>I re-read the OP's post and he said 18 fixtures, so no different for him, but good to know for future.

          It would depend on the rating of the fixtures. 18 fixtures each rated at 50 watts would be allowed as long as there are no unfixed loads (plugs) in the circuit. I'll see if I can find a copy of the code this weekend and cite the rule. It's an interesting point that can save a lot of time and money.

          Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

      2. RalphWicklund | Feb 18, 2006 06:33am | #23

        Then the calculations are out the window if the OP wants to put all fixtures on a dimmer. The off the shelf dimmers, like Leviton, are rated at 600 watts so if he used 150w bulbs like I did he's limited to 4 fixtures per dimmer and 9 fixtures total on the circuit. That would be 3 dimmers needed per circuit.

        Then, if he hunted down the 1000w dimmers at the local supply house, he could reduce the total number of dimmers required but would have to change or add boxes because the heat sinks on those dimmers take up a lot of space. He'd be able to have 6 150w fixtures on one dimmer.

        But then he could be using the 95w quartz bulbs and get to put 6 fixtures on one regular dimmer and 15 on one circuit. Go to the 45 w quarts bulbs and he could have 13 fixtures per regular dimmer and 32 per circuit. Those bulbs are bright.

        Then during all this playing around he also has to chose the trim to go with the cans and the trim will determine the size of the bulb. And so on.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Fight House Fires Through Design

Smart construction decisions and material choices can significantly improve occupant safety and survival in the event of a fire in the home.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Ramon Martinez, Site Supervisor
  • What Size Nails?
  • Stop Ice Dams When Reroofing
  • Outdoor Lighting

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data