My stepfather just returned from the UK where he picked up a Triton instant hot water heater with shower head etc. The data sheet is here:
http://www.parex.co.nz/triton/i/Triton%20T80xr_data_sheet.pdf
I’ve seen these types of heaters everywhere but in the US. Can they be legally installed here?
Also, I believe it calls for 240v 40A circuit but it is wired to accept just one hot and one neutral lead.
Please let me know what you all think.
Replies
In terms of legally electric it probaly is, BUT!
From the 2005 NEC.
"422.47 Water Heater Controls
All storage or instantaneous-type water heaters shall be equipped with a temperaturelimiting
means in addition to its control thermostat to disconnect all ungrounded
conductors. Such means shall comply with both of the following:
(1) Installed to sense maximum water temperature.
(2) Be either a trip-free, manually reset type or a type having a replacement element.
Such water heaters shall be marked to require the installation of a temperature and
pressure relief valve.
Exception No. 1: Storage water heaters that are identified as being suitable for use with
supply water temperature of 82░C (180░F) or above and a capacity of 60 kW or above.
Exception No. 2: Instantaneous-type water heaters that are identified as being suitable
for such use, with a capacity of 4 L (1 gal) or less.
FPN: See ANSI Z21.22-1999/CSA 4.4-M99, Relief Valves for Hot Water Supply Systems."
Now I see that the unit does have a MCB (circuit breaker). But does not have or does the flyer indicate the need for a RCD (GFCI). But they do require a disconnect switch which the US would also.
I don't have the exact wording, but the NEC talks about using appropriate and approved materials and processes. And the approval being by indepent groups.
They don't say it, but it is understood that generally means UL, but there are a few others such as Factory Mutal.
Now this has a number of approvals, but not by US groups or under US standards. So an inspector is very likely to question it, if this is inspected.
As to the power, the US 240 is withing the range for 230 equipment. In fact the 230 is a hormionized number to match up with old European/UK standards that ranged from 220 to 240.
And In the UK there are several different grounding standards and they are being changed and I don't know the details.
Bascially the hot and neutral for equipment like this are just the name for 2 terminals. In the US for COMMON RESIDENTIAL service you have split phase with a centertapped transformer that is the neutral (the grounded conductor) so that the hot (to neutral) is 120 and the difference between the 2 hot legs is 240.
In places where 230 is common and there is no 120 there is no centertap on the transformer and one terminal is bonded to the ground and is the neutral and the other terminal is the 230 to the neutral.
I notice that they require a 2 pole disconnect so from that standpoint it does not matter which type if system it is connected to.
You need to make an electrical inspection verify tht the neutral connection is isolated from any of the metal parts and that there is (or can be added) a place for a ground (earth connection).
BTW, I did not convert the pressure and flow charts to see how usable this unit is.
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
I would think that there would be a problem because it's not a "listed" device.
Corporation: n. An ingenious device for obtaining individual profit without individual responsibility. --Ambrose Bierce
"90.4 Enforcement
This Code is intended to be suitable for mandatory application by governmental bodies
that exercise legal jurisdiction over electrical installations, including signaling and
communications systems, and for use by insurance inspectors. The authority having
jurisdiction for enforcement of the Code has the responsibility for making interpretations
of the rules, for deciding on the approval of equipment and materials, and for granting the
special permission contemplated in a number of the rules.By special permission, the authority having jurisdiction may waive specific requirements
in this Code or permit alternative methods where it is assured that equivalent objectives
can be achieved by establishing and maintaining effective safety.This Code may require new products, constructions, or materials that may not yet be
available at the time the Code is adopted. In such event, the authority having jurisdiction
may permit the use of the products, constructions, or materials that comply with the most
recent previous edition of this Code adopted by the jurisdiction."From the commentary in the Handbook for this section."Some localities do not adopt the NEC, but even in those localities, installations that
comply with the current Code are prima facie evidence that the electrical installation is
safe.
Section 90.4 advises that all materials and equipment used under the requirements of
the Code are subject to the approval of the authority having jurisdiction. The text of
90.7, 110.2, and 110.3, along with the definitions of the terms approved, identified (as
applied to equipment), labeled, and listed, is intended to provide a basis for the
authority having jurisdiction to make the judgments that fall within that particular area
of responsibility.
The phrase ``including signaling and communication systems'' was added to the 2002
Code to emphasize that, indeed, these systems are also subject to enforcement.It is the responsibility of the authority having jurisdiction to interpret the specific rules
of the Code. This paragraph empowers the authority having jurisdiction, using special
permission (written consent), to permit alternative methods where specific rules are not
established in the Code. For example, the authority having jurisdiction may waive
specific requirements in industrial occupancies, research and testing laboratories, and
other occupancies where the specific type of installation is not covered in the Code.This paragraph of 90.4 permits the authority having jurisdiction to waive a new Code
requirement during the interim period between acceptance of a new edition of the NEC
and the availability of a new product, construction, or material redesigned to comply
with the increased safety required by the latest edition. It is difficult to establish a
viable future effective date in each section of the NEC because the time needed to
change existing products and standards, as well as to develop new materials and test
methods, usually is not known at the time the latest edition of the Code is adopted.""90.7 Examination of Equipment for Safety
For specific items of equipment and materials referred to in this Code, examinations for
safety made under standard conditions provide a basis for approval where the record is
made generally available through promulgation by organizations properly equipped and
qualified for experimental testing, inspections of the run of goods at factories, and
service-value determination through field inspections. This avoids the necessity for
repetition of examinations by different examiners, frequently with inadequate facilities
for such work, and the confusion that would result from conflicting reports on the
suitability of devices and materials examined for a given purpose.
It is the intent of this Code that factory-installed internal wiring or the construction of
equipment need not be inspected at the time of installation of the equipment, except to
detect alterations or damage, if the equipment has been listed by a qualified electrical
testing laboratory that is recognized as having the facilities described in the preceding
paragraph and that requires suitability for installation in accordance with this Code.
FPN No. 1: See requirements in 110.3.
FPN No. 2: Listed is defined in Article 100.
FPN No. 3: Annex A contains an informative list of product safety standards for electrical
equipment."Handbook:"Testing laboratories, inspection agencies, and other organizations concerned with
product evaluation publish lists of equipment and materials that have been tested and
meet nationally recognized standards or that have been found suitable for use in a
specified manner. The Code does not contain detailed information on equipment or
materials but refers to products as ``listed,'' ``labeled,'' or ``identified.'' See Article 100
for definitions of these terms.
NFPA does not approve, inspect, or certify any installations, procedures, equipment, or
materials, nor does it approve or evaluate testing laboratories. In determining the
acceptability of installations or procedures, equipment, or materials, the authority
having jurisdiction may base acceptance on compliance with NFPA or other
appropriate standards. In the absence of such standards, the authority may require
evidence of proper installation, procedures, or use. The authority having jurisdiction
may also refer to the listing or labeling practices of an organization concerned with
product evaluations that is able to determine compliance with appropriate standards for
the current production of listed items.
Annex A contains a list of product safety standards used for product listing. The list
includes only product safety standards for which a listing is required by the Code. For
example, 344.6 requires that rigid metal conduit, Type RMC, be listed. By using
Annex A, the user finds that the listing standard for rigid metal conduit is UL 6, Rigid
Metal Conduit. Because associated conduit fittings are required to be listed, UL 514B,
Fittings for Cable and Conduit, is found in Annex A also."100 Definitions;"Approved. Acceptable to the authority having jurisdiction.""Labeled. Equipment or materials to which has been attached a label, symbol, or other
identifying mark of an organization that is acceptable to the authority having jurisdiction
and concerned with product evaluation, that maintains periodic inspection of production
of labeled equipment or materials, and by whose labeling the manufacturer indicates
compliance with appropriate standards or performance in a specified manner.""Listed. Equipment, materials, or services included in a list published by an organization
that is acceptable to the authority having jurisdiction and concerned with evaluation of
products or services, that maintains periodic inspection of production of listed equipment
or materials or periodic evaluation of services, and whose listing states that the
equipment, material, or services either meets appropriate designated standards or has
been tested and found suitable for a specified purpose.
FPN: The means for identifying listed equipment may vary for each organization concerned with
product evaluation, some of which do not recognize equipment as listed unless it is also labeled.
Use of the system employed by the listing organization allows the authority having jurisdiction to
identify a listed product.""110.2 Approval
The conductors and equipment required or permitted by this Code shall be acceptable
only if approved.""110.3 Examination, Identification, Installation, and Use of Equipment
(A) Examination In judging equipment, considerations such as the following shall be
evaluated:
(1) Suitability for installation and use in conformity with the provisions of this Code
FPN: Suitability of equipment use may be identified by a description marked on or provided with
a product to identify the suitability of the product for a specific purpose, environment, or
application. Suitability of equipment may be evidenced by listing or labeling.
(2) Mechanical strength and durability, including, for parts designed to enclose and
protect other equipment, the adequacy of the protection thus provided
(3) Wire-bending and connection space
(4) Electrical insulation
(5) Heating effects under normal conditions of use and also under abnormal
conditions likely to arise in service
(6) Arcing effects
(7) Classification by type, size, voltage, current capacity, and specific use
(8) Other factors that contribute to the practical safeguarding of persons using or
likely to come in contact with the equipment.(B) Installation and Use Listed or labeled equipment shall be installed and used in
accordance with any instructions included in the listing or labeling."Handbook:"Manufacturers usually supply installation instructions with equipment for use by
general contractors, erectors, electrical contractors, electrical inspectors, and others
concerned with an installation. It is important to follow the listing or labeling
installation instructions. For example, 210.52, second paragraph, permits permanently
installed electric baseboard heaters to be equipped with receptacle outlets that meet the
requirements for the wall space utilized by such heaters. The installation instructions
for such permanent baseboard heaters indicate that the heaters should not be mounted
beneath a receptacle. In dwelling units, it is common to use low-density heating units
that measure in excess of 12 ft in length. Therefore, to meet the provisions of
210.52(A) and also the installation instructions, a receptacle must either be part of the
heating unit or be installed in the floor close to the wall but not above the heating unit.
(See 210.52, FPN, and Exhibit 210.23 for more specific details.)
In itself, 110.3 does not require listing or labeling of equipment. It does, however,
require considerable evaluation of equipment. Section 110.2 requires that equipment be
acceptable only if approved. The term approved is defined in Article 100 as acceptable
to the authority having jurisdiction (AHJ). Before issuing approval, the authority
having jurisdiction may require evidence of compliance with 110.3(A). The most
common form of evidence considered acceptable by authorities having jurisdiction is a
listing or labeling by a third party.
Some sections in the Code require listed or labeled equipment. For example, 250.8
includes the phrase ``listed pressure connectors, listed clamps, or other listed means.''"First of all I could not find any specific thing in the NEC that requires water heaters to be LISTED. But listing is one way of satifying the inspector that the equipment is suitable for the application.And while I have not tried determining the exact requirements I see a number of approvals listed on the spec sheet and suspect that the unit is in fact LISTED.But the NEC is open enough for an inspector to not allow this, but another to allow allow someone to take a UL list coffee cup insertion and use UL listed foil (duct) tape and tape in on the end of a shower head and plug it into a UL listed entension cord that is plugged into a UL liste GFCI..
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
Thanks for the responses. I guess the unit is viable.