what would cause a GFI to catch fire

WillieWonka | Posted in General Discussion on November 18, 2006 05:54am

I replaced a receptacle for someone last night. It was a GFCI. The face place was completely charred, the buttons were completely melted and fused into a molten mess. The outlet into which a heater was plugged had one of the prong slots completely melted and the other prong slot was pretty much on its way to being melted. The other outlet at the top of the duplex, while charred somewhat was for the most part ok, recognizable, and looked like it would’ve still been usable. Upon removal of the GFCI the back of the unit looked brand new, no signs of damage at all, or on the sides of the unit. Only the front had this damage. The plug of the heater that was plugged into it was nonexistent, it had just melted in the “fire” and unusable.

Obviously there was something wrong the heater that caused the fire. But the GFI never tripped. The wire was 12ga feeding the receptacle and was in excellent shape.

Should a GFI tripped in this case?

If at first you don’t succeed, try using a hammer next time…everything needs some extra persuasion from time to time.  -ME
Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    MarkH | Nov 18, 2006 05:56pm | #1

    No, it wont trip in that case.  I think the GFI may have had an electronic failure.

  2. USAnigel | Nov 18, 2006 06:10pm | #2

    This sounds like a bad connection between plug and socket. This will generate heat! With a heater pluged in you are running near the suggested max of that socket. I suggest you replace the heater plug too.

  3. User avater
    maddog3 | Nov 18, 2006 06:26pm | #3

    it would seem that the heater finally scorched the GFI.

    space heaters are a constant "forgotten" load...with large wattages, up to 1800 watts or more, and will overheat tinsel cord extensions and their cheap molded plugs .. large looking extension cords eventually have problems as well

    even the plugs on the heaters have been damaged...

    space heaters under desks in cubicles are a source of regular complaints in offices at this time of year, with units being left on over the weekends especially....

    .
    .
    .
    .Wer ist jetzt der Idiot
    ?



    Edited 11/18/2006 10:28 am by maddog3

    1. DaveRicheson | Nov 18, 2006 06:41pm | #6

      Sooo right!

      To the OP.

      GFCI recepticals trip on GROUND FAULTS, not circuit overloads or a dead short of hot to neutral.

      maddog3 gave you the most likely scenerio for the burn out.

      Our local AHJ issued an advisory in September recomending that electrician run dedicated circuits and AFCI breakers for retro work where space heaters will used.

      A lot of house fires get started from electric space heater usage.

       

      Dave

      1. User avater
        maddog3 | Nov 18, 2006 06:51pm | #7

        I have been reading where the mfrs.of the arc fault stuff, mainly SqD , are pushing the NEC for a WHOLE HOUSE requirement for ' 08gotta sell those things somehow I guess.

        .

        .

        .Wer ist jetzt der Idiot

        ?

        1. User avater
          BillHartmann | Nov 18, 2006 07:07pm | #8

          I have a copy of the proposed 08 and it does have a requirement COMBINATION type AFCI protection on all 120v 15 & 20 amp branch circuits in dwellings.Don't have any idea of the status of those proposal are.And I dont' know what a COMIBNATION AFCI is.The standards have defined several types. One of which adds serial arc detection. Another type is gives AFCI type of protection at the receptacle.As far as I know none of those other types are available yet.

          1. User avater
            maddog3 | Nov 18, 2006 07:21pm | #9

            Sq D started the whole AFCI craze IIRC, but no one seems to be able to manufacture a unit that does what was promised when this all started....I don't know what a "combination afci "....is either.it should significantly add to the cost of a new service however.

            .

            .

            .Wer ist jetzt der Idiot

            ?

          2. User avater
            BillHartmann | Nov 18, 2006 07:33pm | #10

            A number of localation have opted out of the AFCI requirement or modified them to only require it on bedroom receptacles.But I don't have any idea of what percentage homes that is.Also from some searching it seems that many CA cities (so it might be statewide) DOES NOT require AFCI's when doing a service/panel upgrade.

          3. Joe Sullivan | Nov 18, 2006 10:32pm | #11

            Would a combination unit be both AFCI and GFCI? I would imagine that would be VERY expensive. ALso, if ordinary AFCI breakers were required for the whole house in a panel upgrade, think of the number of GFCI breaker protected circuits that would have to be traced and rewired with GFCI recepticles.

          4. User avater
            BillHartmann | Nov 19, 2006 02:28am | #19

            I don't think that it a combination of AFCI and GFCI although I think that I have heard that someone makes such a device or has introduced one.

          5. User avater
            maddog3 | Nov 19, 2006 05:07pm | #28

            this is the UL definition of a "combination " AFCI......
            I found it about five minutes agoArc Fault Circuit Interrupters, Combination Type - An AFCI which complies with the requirements for both branch/feeder and outlet circuit AFCIs. It is intended to protect downstream branch circuit wiring and cord sets and power-supply cords.hope this cleared it up for ya....I'm still scratching my bean.

            .

            .

            .Wer ist jetzt der Idiot

            ?

          6. User avater
            BillHartmann | Nov 19, 2006 05:23pm | #29

            http://forums.taunton.com/n/mb/message.asp?webtag=tp-breaktime&msg=81702.1

            Edited 11/19/2006 10:06 am by BillHartmann

          7. User avater
            maddog3 | Nov 19, 2006 05:54pm | #30

            OMG.....!no,no, not that one.

            .

            .

            .Wer ist jetzt der Idiot

            ?

          8. User avater
            BillHartmann | Nov 19, 2006 06:07pm | #31

            I see that I had the correct like. Just 3 copies in a row and that confused the system and it reverted to the first thread.http://forums.taunton.com/n/mb/message.asp?webtag=tp-breaktime&msg=81702.1

          9. User avater
            maddog3 | Nov 19, 2006 12:04am | #13

            I know Wis. had NOT adopted it ....again.... for the '05 Code....." Also from some searching it seems that many CA cities (so it might be statewide) DOES NOT require AFCI's when doing a service/panel upgrade." yep,it would be impossible to use them for an upgrade if there are existing multi-wire circs.....unless those are run in conduit !!the things are a real PITA.....IMO.

            .

            .

            .Wer ist jetzt der Idiot

            ?

          10. User avater
            BillHartmann | Nov 19, 2006 02:37am | #21

            Cutler Hammer does make a two pole AFCI that could be used on multi-wire curcuits. I think that I have heard that they are the only one, but not sure.But I don't see that as such a big stumbling block.While this might vary by region and by electrican I don't think that many circuits that feed bedrooms are multi-wire.But they could require the AFCI's and just except EXISTING multiwire circuits from that requirement.

          11. User avater
            BillHartmann | Nov 19, 2006 04:10am | #22

            I have figured out the AFCI and am starting a new thread.

          12. USAnigel | Nov 19, 2006 01:15am | #17

            I was not aware that "arc faults" were such a problem!! All this fancy stuff and we still can't get people to replace the batterys in the smoke dectector.

          13. DanH | Nov 19, 2006 02:16am | #18

            The vast majority of "electrical fires" start with a bad connection that overheats. In most cases of an overheated connection the result is just like this one -- eventually the connection gets hot enough to melt down the connectors involved, and then the connection is broken and damage is minimal. But in a few cases either the overheating directly starts a fire, or the wiring insulation melts and produces an electric arc of sorts that can really get things burning.But it all starts with the bad connection.
            People never lie so much as before an election, during a war, or after a hunt. --Otto von Bismarck

    2. Frankie | Nov 18, 2006 11:39pm | #12

      Might it be that the outlet was rated for 15 amps and the circuit was rated for 20? Feed wires would have stayed cool enough while the internal contacts of the outlet would have started to heat up.Just a thought,Frankie

      Flay your Suffolk bought-this-morning sole with organic hand-cracked pepper and blasted salt.

      Thrill each side for four minutes at torchmark haut. Interrogate a lemon.

      Embarrass any tough roots from the samphire. Then bamboozle till it's al dente with that certain je ne sais quoi.

      Arabella Weir as Minty Marchmont - Posh Nosh

      1. DanH | Nov 19, 2006 12:23am | #15

        You can easily overheat the contacts with only 5-10 amps, if the contact resistance is high enough.
        People never lie so much as before an election, during a war, or after a hunt. --Otto von Bismarck

      2. User avater
        BillHartmann | Nov 19, 2006 02:34am | #20

        ALL 15 amp receptacles are rated for 20 amp feed through and can be used on 20 amp circuits. And GFCI's are also rated for 20 amp feedthrough to the load terminals.If you are on a 20 amp circuit you are suppose to be able to safely draw 20 amps at that receptacle. Such as 2 10 amp loads or a 15 and 5.And with one exception I have never seen anything with a 15 amp plug that will draw more than 15 amps.That exception being stationary power tools. Specially imported ones. Many of them have 1 1/2 hp motors with labeled full load currents of 15-18 amps.

        1. WillieWonka | Nov 19, 2006 06:37am | #24

          The feed thru stuff I don't understand. In my posting that started this mess....the GFI was rated for 15A and a 20A feed thru. I"m not sure I understand what that means....does it mean the receptacle (GFI in this case) is rated for a load only up to 15A but that the feed thru (I assume this means a wire splice in the receptacle box to continue downstream elsewhere) can go to somethat that draws 20A?

          Does it mean the breaker can be a 20A brkr even though the receptacle is rated for 15A? It doesn't make sense to me if that is the case because you can't put 14ga wire on a 20A brkr and it sounds the same to me as if that's what you're doing...sorta. What does the "feed thru" mean really? If at first you don't succeed, try using a hammer next time...everything needs some extra persuasion from time to time.  -ME

          1. User avater
            BillHartmann | Nov 19, 2006 07:34am | #26

            In a 15 amp receptacle the wipers (contacts) in the receptacle and in the plug are designed to handle a max of 15 amps.The common duplex receptacle consists of TWO receptacles. Each set of contacts is designed to handle a max of 15 amps.But the connections (screw terminals or clamps) and the buss bar connection in the receptacle is designed to handle a maximum of 20 amps.Thus it can be connected to a 20 amp circuit. All of the parts that might be carrying 20 amps is rated for 20 amps.That would include the wire (#12), the screw terminals (or back clamps such as used on the GFCI's), the relay contacts in the GFCI, the bus bar straps on the side of the duplex receptacle are all designed to handle 20 amps. The only thing is limited to 15 amps is the each individual receptacle contacts and the matching plug.Thus you can have any combination of loads that adds up to 20 amps.It can be two 10 amp loads in this receptacle or example or maybe a 5 amp load in this recptacle and a downstream (freed through) receptacle that has a 10 and a 5 amp load. Anything that is in series is rated for 20 amps.Thus a 20 amp circuit is allowed to use 15 amp receptacles as long as you have more than one receptacle (and the duplex counts as two) on the circuit.Or the same receptacles and GFCI can be wired with #14 and connected to a 15 amp breaker.(Note if the back stab terminals are used on residential grade receptacles they are limited to #14 wire adn thus 15 amp circuits. But if the screw terminals are used the same ones can be used with #12 on a 20 amp circuit. The back stab are those with a hole that you poke the wire in and it is help with a spring. That is different from the back wire on GFCI receptacles that has a plate that hold the wire when the terminal is screwed down.)

          2. WillieWonka | Nov 19, 2006 07:52am | #27

            Thank you. AS for the backwired method, I'll NEVER do that. I've replaced a number of recepts where the backwiring caused some kind of issue.  I always use the screw terminal or the pressure-plate screw connection.If at first you don't succeed, try using a hammer next time...everything needs some extra persuasion from time to time.  -ME

  4. DanH | Nov 18, 2006 06:30pm | #4

    This is not unusual. Likely the connection between the heater plug and the GFI socket contacts was poor, resulting in heating which further compromised the connection. There is never an overload (in fact, current will go DOWN slightly as this occurs), and there is never a short to ground (at least not until the charring causes it), so a breaker or GFCI won't trip.

    Alternatively, the heater plug could have developed a bad internal connection, with essentially the same result.

    Presumably an arc-detecting breaker would have tripped.

    People never lie so much as before an election, during a war, or after a hunt. --Otto von Bismarck
    1. User avater
      maddog3 | Nov 18, 2006 06:39pm | #5

      don't think an AF breaker would trip either, unless there was a
      L-N arc..

      .

      .

      .Wer ist jetzt der Idiot

      ?

      1. DanH | Nov 19, 2006 12:21am | #14

        Hard to say for sure.  It's certainly more likely to trip than a regular breaker or a GFCI, both of which have essentially zero chance of tripping in this scenario.
        People never lie so much as before an election, during a war, or after a hunt. --Otto von Bismarck

        1. User avater
          maddog3 | Nov 19, 2006 01:10am | #16

          that's the beauty of 'em......they do one damn thing, besides, maybe the panel where this happened won't accept one.BTW, I just came home from Lowe's and both GE and Sq D are still within pennies of $35...is it any wonder they want these things to be used to fill up a panel.

          .

          .

          .Wer ist jetzt der Idiot

          ?

  5. RedfordHenry | Nov 19, 2006 05:36am | #23

    You say the face plate was melted?  Maybe the heater was pointed at the wall. 

    1. WillieWonka | Nov 19, 2006 06:38am | #25

      The recept was up above the sink. The space heater on the floor. Don't think it's likely the heater melted the face.If at first you don't succeed, try using a hammer next time...everything needs some extra persuasion from time to time.  -ME

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Outdoor Lighting

Lighting up an exterior isn't just about ambiance— it's also about code compliance. Here is what the code says about safety and efficiency when it comes to outdoor lighting.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Design and Build a Pergola
  • Podcast Episode 689: Basement Garages, Compact ERVs, and Safer Paint Stripper
  • FHB Podcast Segment: Are Single-Room ERVs the Answer?
  • Fire-Resistant Landscaping and Home Design Details

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data