Which circuit for Bath outlet?

pgproject | Posted in General Discussion on April 3, 2007 08:52am

OK, we’re redoing a small bathroom. There is a small (6×5) room which will contain the toilet and the tub/shower. Immediately outside the door to this room is a large dressing/ exercise area with a big walk-in closet, so we’re putting the vanity and lavy there. I know code requires a GFCI -protected outlet on a dedicated 20a circuit in the bathroom. I plan to put this ‘dedicated circuit’ outlet near the lavy (though it’s not technically ‘in the bathroom’), as I assume it’s intended for high-draw items (hair dryer) which would usually be used near the sink. So far, so good.

Now, in the ‘bath room’ (remember, toilet and bath only in here), I’m installing an electric towel warmer (90 watts) which stays plugged in and on all the time. Obviously, this outlet will need to be GFCI protected, but should it be on the same circuit as the lavy outlet, or should I run it from a general purpose (lighting/outlets) circuit? I can’t easily get another dedicated circuit from the panel, so it’s one or the other.

Thanks

Reply

Replies

  1. JohnSprung | Apr 03, 2007 05:32pm | #1

    I'd put it on the bath circuit.  Since they're in different rooms, I'd pigtail and put a GFCI receptacle in each location, instead of using one to protect the other downstream.  A little extra money now can save a whole bunch of head scratching and confusion a few years in the future. 

     

     

    -- J.S.

     

  2. User avater
    BillHartmann | Apr 03, 2007 06:08pm | #2

    I am not going to search the code and I don't know if it is there are not, but I have seen this discussed in some electrical forums.

    This is not uncommon arrangement. Specially in motels.

    A bathroom consists of all 3 fixtures. So it encompasses the whole area.

    The towel bar does not require a dedicated circuit any place and could be taped in any general purpose circuit.

    A dedicated 20 amp bathroom circuit serves all the receptacles in the bathroom. And it can also service receptacles in other bathrooms or in that one bathroom also the lights and fan.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
  3. User avater
    BillHartmann | Apr 03, 2007 11:27pm | #3

    I have the 2005 NEC Code with handbook open and saw this.

    "A bathroom is defined in Article 100 as ``an area including a basin with one or more of
    the following: a toilet, a tub, or a shower.'' The term applies to the entire area, whether
    or not a separating door, as illustrated in Exhibit 210.9, is present. Note that 210.52(D)
    requires that a receptacle be located on the wall or partition adjacent to each basin
    location or in the side or face of the basin cabinet. However, if the basins are adjacent
    and in close proximity, then one receptacle outlet may satisfy the requirement, as
    shown in Exhibit 210.9 (top)."

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
    1. pgproject | Apr 03, 2007 11:59pm | #4

      Thanks for the code reference- I don't see a specific answer to my question there, but I'm leaning toward putting the WC/Tub area receptacle on the same (dedicated) circuit as the lavy outlet. The constant 90 watt draw of the towel warmer doesn't seem like it will cause any problems with capacity for the sink outlet.Thanks again- what a great resource this forum is!

  4. rpait | Apr 04, 2007 02:37am | #5

    put all the outlets on one gfci circuit using a gfci breaker in the box, then your covered.

    1. pgproject | Apr 04, 2007 02:44am | #6

      It's cheaper to buy 2 CFCI outlets.

    2. grpphoto | Apr 04, 2007 03:01am | #7

      I've seen articles that recommend putting all outlets on a GFCI breaker, arguing that the breaker is less subject to false trips. I've seen just as many articles arguing that the GFCI outlets are less subject to false trips. The convincing argument to me is the fact that, when a GFCI outlet trips, it's right there and the problem is pretty obvious. When the breaker trips, someone is standing in the bathroom wondering why the hairdryer doesn't work.As a handyman, I make my living off these people. Put it on the breaker. :-)George Patterson, Patterson Handyman Service

    3. JohnSprung | Apr 06, 2007 03:50am | #17

      When you're wet and wearing a towel, would you rather push a button on the wall, or schlep on down to the breaker panel?  GFCI's should always be in the same room with everything they control. 

      Overcurrent breakers, OTOH, need to be in the central panel where the branch circuit originates, 'cause that's the only way they can protect all the wire on their circuits.  It's a necessary inconvenience.   

       

      -- J.S.

       

      1. rpait | Apr 06, 2007 04:59pm | #18

        either way, I am drying off first worrying about a tripped gfci second

  5. bezgrp | Apr 04, 2007 04:27am | #8

    ALL BATH GFCIS SHOULD BE ON ONE 20AMP BREAKER , TIE THE WARMER IN WITH OTHERS IN THE HOUSE .

    1. pgproject | Apr 04, 2007 04:50am | #9

      done- thanks

    2. jja28 | Apr 04, 2007 05:09am | #10

      Is that 1 20 amp breaker...total....for the house... no matter how many bathrooms (2, 3, 4, etc)? Or 1 20 am breaker per bathroom?

    3. User avater
      BillHartmann | Apr 04, 2007 07:28am | #11

      "ALL BATH GFCIS SHOULD BE ON ONE 20AMP BREAKER , TIE THE WARMER IN WITH OTHERS IN THE HOUSE ."NO. All bath GFCI's should not be on one 20 amp circuit. But they CAN be, if there is NOTHING ELSE on the circuit.Or you can run a 20 amp circuit to ONE bathroom and also put lights and fan on it.But the receptacle for the towel warner is a BATHROOM RECEPTACLE and thus must be on the 20 amp bathroom receptacle..
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      1. john7g | Apr 04, 2007 02:10pm | #12

        >Or you can run a 20 amp circuit to ONE bathroom and also put lights and fan on it.<

        Of the group above, do they all need to be GFCI protected or just the outlets need GFCI protection?  I'm thinking outlets only but I'm no electrician.

        1. User avater
          BillHartmann | Apr 04, 2007 03:30pm | #13

          ">Or you can run a 20 amp circuit to ONE bathroom and also put lights and fan on it.<Of the group above, do they all need to be GFCI protected or just the outlets need GFCI protection? I'm thinking outlets only but I'm no electrician."All of those are OUTLETS.In codish an outlet is anyplace where electrical power is utilized. It include both receptacles and permantely connected equipement such as the lights and fan.Code requires 2 things in this area.Receptectles to be GFCI protected.Manufacutres instructions to be followed. Often if fans are installed in wet areas, ie over showers or tubs, instructions require that they be GFCI protected..
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          1. pgproject | Apr 05, 2007 09:06pm | #14

            The fan/heat/light unit I have requires it's own dedicated circuit, and the instructions don't say anything about it having to be GFCI protected. The last three bathrooms I've done have been like this: GFCI outlets on 1 20a dedicated circuit; Fan/Heat/Light on one dedicated 20a circuit, lighting tied in to existing lighting circuit from the closest room. All have passed inspection. I was under the impression that lighting is NOT to be connected to the outlet circuit.

          2. User avater
            BillHartmann | Apr 05, 2007 09:18pm | #15

            "I was under the impression that lighting is NOT to be connected to the outlet circuit."Nope. The lights can be on a bathroom receptacle circuit as long as the circuit only supplies that one bathroom.BTW, you can't have any lights on the kitchen small appliance circuits."The fan/heat/light unit I have requires it's own dedicated circuit, and the instructions don't say anything about it having to be GFCI protected."Yes the heater part of it draws enough power that it would require a dedicated circuit.I am curious does the instructions allow for the unit to be installed over a shower or tub?.
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          3. pgproject | Apr 05, 2007 10:34pm | #16

            "I am curious does the instructions allow for the unit to be installed over a shower or tub?"Doesn't mention.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Critical Details for Ductless Heat Pumps

Trouble-free performance begins with properly installed line sets that pass rigorous testing for leaks.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast 550: PRO TALK With Carpentry Program Instructor Sandy Thistle and Graduate David Abreu
  • Podcast 549: Energy Upgrades, Chimney Inspections, and Questions About a Home You Might Buy
  • Podcast 549: Members-only Aftershow—Patios vs. Decks
  • Podcast 548: PRO TALK With Design/Build Operations Manager Jessica Bishop-Smyser

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • Pretty Good House
    Buy Now
  • 2023 Tool Guide
    Buy Now
  • 2022 Fine Homebuilding Archive
    Buy Now
  • Code Check Building 4th Edition
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 314 - April/May 2023
    • 7 Options for Countertops
    • Tool Test: Wood-Boring Bits
    • Critical Details for Ductless Heat Pumps
  • Issue 313 - Feb/March 2023
    • Practical System for a Seismic Retrofit
    • Fine Homebuilding Issue #313 Online Highlights
    • Practical System for a Seismic Retrofit
  • Issue 312 - Dec 2022/Jan 2023
    • Tool Test: Cordless Tablesaws
    • Gray-Water System for a Sustainable Home
    • Insulate a Cape Roof to Avoid Ice Dams
  • Issue 311 - November 2022
    • 7 Steps to a Perfect Exterior Paint Job
    • Options for Smarter Home-Energy Tracking
    • The Fine Homebuilding Interview: James Metoyer
  • Issue 310 - October 2022
    • Choosing a Tile-Leveling System
    • Choosing Between HRVs and ERVs
    • Custom Built-in Cabinets Made Easy

Fine Homebuilding

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in