Am I right that a chart which gives AWG size, say for 2/0 CU, as 10 mm, means the diameter of the wire itself, and not the wire and insulation?
Youth and Enthusiasm Are No Match For Age and Treachery
Am I right that a chart which gives AWG size, say for 2/0 CU, as 10 mm, means the diameter of the wire itself, and not the wire and insulation?
Youth and Enthusiasm Are No Match For Age and Treachery
Discover a concrete-free foundation option that doesn't require any digging.
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Get home building tips, offers, and expert advice in your inbox
Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.
Start Free Trial NowGet instant access to the latest developments in green building, research, and reports from the field.
Start Free Trial NowDig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.
Start Free Trial NowGet instant access to the latest developments in green building, research, and reports from the field.
Start Free Trial Now© 2025 Active Interest Media. All rights reserved.
Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.
Get home building tips, offers, and expert advice in your inbox
Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.
Start Your Free TrialGet complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.
Already a member? Log in
We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.
Replies
Yes, AWG is the size of the bare wire.
But also note that when calculating conduit fill that you need to both AWG and the type of insulation. As conducit fill is based on the OD which and different types of insulation have different thicknesses.
Isn't heat also a factor in conduit fill? Insulation rated for lower temps requires looser fill so as not to get too hot?
-- J.S.
NoThe conduit fill is simply a percentage of area. That is to allow for pulling wires without damage.Heat derating is a completely different subject.Depending on the number of equivalent current carrying conductors in a conduit or for cable bundled together then the ampacity of the wire is derated.*Equivalent current carry conductors. For single phase circuits you have two, the hot and neutral. For multiwire circuits you have the 2 (or 3 for 3 phase) hots. The neutral is not counted as it only carries the difference.
Ah, yes. I'm starting to remember now. By staying below the point where derating kicks in, you pretty much always stay below the conduit fill limit, right?
-- J.S.
No.For different size wires you need to calculate it, but for all the same size there are table of conduit fill.For 1/2" EMT with #12 THHN you can have 9 wires.In most cases that means derating.
My code books are packed up for the move next weekend, but I think we're saying the same thing. You can have nine THHN #12's in a 1/2" with derating, that's the fill limit. There's a lower number than nine where you don't have to derate. By staying below that lower number, you're cool -- as it were -- for both fill and thermal derating.
-- J.S.
Don't forget that derating starts from the 90º column so actually it works out.
~Peter
"Don't forget that derating starts from the 90º column so actually it works out."Depending on the insulation.But in general most is, but not all.
This is a handy page for calculating conduit fill, provided you don't have too many different types:
http://www.systemswestengineers.com/fill.htm
I also have an Excel spreadsheet I got somewhere, for more complicated situations.
Thanks,Yesterday I ran across a box with 200 A breaker and unmarked copper feeds that just didn't look like the right size. (I get so used to seeing stuff sized properly, that when I see something like this, I tend to hesitate when the wire isn't marked.)I was able to pick up an unsecured wireless network and check the AWG sizes, and called it out as too small (the wires w/ insulation were 10mm)Just wanted to be sure.