Anchor Bolts 9″ o.c. !!!

EJCinc | Posted in General Discussion on March 2, 2007 10:46am

IRC2006  says that in my area of PA I have to place anchor bolts in my 12 course 10″ concrete block basement walls 9″ o.c. and I have to anchor EVERY joist to an anchor bolt with a 1/4″ steel angle bolted to the joist.

Is anyone else running into this?  It was all rumor here until a code official confirmed it early this week at a conference updating us on the new code.  He said that if we could get an architect or engineer to say our basements meet ACI318 or ACI 332 then we should be ok to place bolts at 4′-6′ o.c. which is what we had been doing.  I can’t find much helpful info about either of those ACI and the arch i talked to didn’t know much about it either.

Supposedly they are working on getting this repealed but who knows how long that will take. 

I can’t believe I haven’t heard anything about this on here.  This must be affecting somebody else!  Anyone??

Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

Reply

Replies

  1. Danno | Mar 03, 2007 12:25am | #1

    Wow. Are they expecting earhtquakes or hurricanes in PA? Seems like Michigan code is more like 6' o.c..

  2. User avater
    SamT | Mar 03, 2007 12:37am | #2

    Hey! Can we help it that you live in the middle of a swamp, subject to Richter 9 earthquakes, force 10 hurricanes, monster tornadoes, and 90 mph, 100 feet deep floods, with occasional visits by King Kong, Godzilla, and BunBun?

    (|;>)

    9" hunh? Does that mean your joists have to be 9", 18", or 27" OC? Gonna have to cut 6" off all your sheathing to keep it on 9" layout, yahno?

    What does it say about rafters? I betcha gotta use 6 each 4"x1/2" lags thru all the shingles too.

     

    SamT

    Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

  3. EJCinc | Mar 03, 2007 12:51am | #3

    Haha, it's easy to laugh when you don't have to worry about it isn't it? lol

    So what code are you guys working with that this doesn't affect you?

     

    Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

    1. User avater
      SamT | Mar 03, 2007 06:09pm | #22

      No, I'm not laughing any more. I thought it was just PA.

      And I'll be stuck with the 9" limit also due to soil types here.

      I'm thinking to try real hard to get a "Strike Plate" prescribed.

      A length or 1/4" or 3/8' plate with anchors, set to sit 1 1/2" above the TOC on the side of the wall. Tie wire in place, pour, pull the wire. Butt mudsill to the plate. Outer face of Strike Plate flush with face of wall.

      Cost a little more $teel, save hour$.

       

      Y'all realise that this is in response to bad construction techniques, doancha?

      Order 3500# mud, add water so's it'll work easier, don't vibrate, "Ain't gonna be no bee holes in that soup," strip the next day so thay can backfill 'cuz ya gotta gitter done so's the framers can get the floor laid so's I can get my draw, and we got anudder 100 of these to do knock out in this tract, no ya idiot helper, don't waste time knocking the snap ties off, they' be covered up an' nobody's gonna see 'em anyway, throw a socked drain that goes nowhere around the foot, whaddaya mean I gota put gravel over it? that's gonna take hours, where's that backhoe? I told him 9 o'clock he's fired, I found a smuck who'll do it cheaper. . . . .

      Faster faster cheaper cheaper.

      So now everybody has to do the things designed to make the idiots do OK work and we all know the hacks and Wally World companies will find some way to screw this up too.SamT

      Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

      1. MikeSmith | Mar 03, 2007 06:12pm | #23

        sam.. it looks like it's just for CMU walls.. i don't think poured concrete walls got the same treatment.... or am i just not  reading it right ?

        BTW.. those links that bil hartman provided lead to another link that is very informative

        http://www.toolsofthetrade.net/articles/showarticle.asp?articleID=2399&position=0&type=article

        Mike Smith Rhode Island : Design / Build / Repair / Restore

        Edited 3/3/2007 10:18 am ET by MikeSmith

        1. User avater
          SamT | Mar 03, 2007 06:41pm | #24

          Noooo, I think it applies to solid concrete also.

          I noticed in the pdf table attached above that the maximum wall height is 9'. Somebody said the slab bottom has to be 18" above the footing. does that mean the the maximum basement ceiling height is 7'? (|;>

          It kinda looks like I may not be able to play in the mud ever again.   Mommeeee!

          Won't know for sure for a while.

          But this situation would just mean more money in my pocket, because I was building the biz around the statement "My concrete won't crack" (with a few AOG contingencies) and always doing it better than standard. That's a premium service and costs premium dollars.

          I want to build for the "If you have to ask, you can't afford it" crowd, because they are a lot easier to sell to than the "But, it's my life savings" bunch.

          And I HATE being forced to do less than the best.SamT

          Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

        2. User avater
          jonblakemore | Mar 04, 2007 01:54am | #25

          I think Sam's right about the code applying to CMU & CC.I looked over the section attached in a little more depth, this is a big thing. I'm hoping that VA will adopt new provisions in their UBC to loosen things up. If not, I think we'll have some major changes in the way we build. 

          Jon Blakemore RappahannockINC.com Fredericksburg, VA

          1. MikeSmith | Mar 04, 2007 02:07am | #26

            those are requirements to prevent the wall from collapsing  due to unbalanced fill

            we already have the requirement of  foundation bolts 4' OC and  12" from each corner.. that's for wind uplift

            that link that i posted talked about poured concrete walls  being treated differently than  CMU...

             and the soil designation is going to have a lot to do  with itMike Smith Rhode Island : Design / Build / Repair / Restore

          2. User avater
            jonblakemore | Mar 04, 2007 02:56am | #27

            I just read the link talking about the ACI document. It looks I have yet another book to buy when we have a basement coming up. 

            Jon Blakemore RappahannockINC.com Fredericksburg, VA

          3. brownbagg | Mar 04, 2007 03:05am | #29

            the aci book is $500 and it has nothing to do with this.

          4. User avater
            jonblakemore | Mar 04, 2007 03:33am | #31

            The link posted to the Tools of the Trade site said that ACI 332 was written for residential concrete. ACI 332 is referenced in R404.1 of the IRC 2006 as being the standard. 

            Jon Blakemore RappahannockINC.com Fredericksburg, VA

          5. brownbagg | Mar 04, 2007 03:41am | #33

            aci 332 is 38 pages long, what do you need to know, i have it right herechapter 1 intro
            2 requirement for residental concrete
            3 material
            4 proportioning
            5 formwork
            6 reinforcement
            7 joints and embedded item
            8 footing and walls
            9 concrete slab
            10 curing
            11 repair of surface defects
            12 references pick your flavor

          6. EJCinc | Mar 04, 2007 04:25pm | #40

            Hey hey hey don't fight guys. 

            ACI332 and ACI318 are both mentioned in the code as acceptable alternatives.

            ACI332 = Poured concrete foundations

            ACI318 = Masonry

            I've found very little about ACI318 so far.

            It involves poured as much as masonry unfortuneatley.Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

          7. brownbagg | Mar 04, 2007 08:50pm | #43

            aci 318 there is nothing about masonary in 318. 318 is 443 pages longaci 318- Building code requirement for structutal concrete.mainly 318 is a design for footing, slabs, poured wall and roof,Its mainly load factors.

          8. ryding | Mar 05, 2007 12:50pm | #46

            I'm not up on all the codes here in seattle, but I believe every house we build has to be engineered due to sheer requirements relating to earthquake risk. Every sheer wall on the plan can have a different detail, from the amoun of rebar to to the spacing on the sheeting of the walls.

            I mostly frame and it's not on common to be pointing out missing bolts. I almost never see 1/2" bolts, almost exclusively 5/8" with 3" galvi. washers which fits your regs pretty close for my experience of tighest spacing, that being 12". I'm not sure I've even seen 6' spacing except out in the boonies maybe.

            Usually between 16" and 4', it is also common to have A35 [simpson clip] plate to rim every 32" down to every 6". Let's not overlook all the hurricane straps poured into the foundation walls in a very liberal manner, to be continued between floors with more staps attaching upper walls and lower walls together. 

            Did I mention the nailing patterns down to 2 rows of 2"spacing around the parimeter of sheeting, the result of which is the common practice of calling out 3x material for all plywood breaks. i.e. every 4', bottom plates, and two sided sheer walls require the insid sheet to fall on a different stud making two of the three studs in said wall 3xs. You can imagine the number of nails that go int these sheer walls what with nail patterns, hold downs, clips,etc. I spend more time pointing out these almost indecipherable details to my crews than any other aspect of the job I think.

            For your sake I hope you guys have it easier and that isn't changing soon.  

          9. dovetail97128 | Mar 05, 2007 08:32pm | #47

            ryding,
            Situation is the same here in Oregon.

          10. User avater
            jonblakemore | Jun 01, 2007 11:55pm | #48

            ---Update---

            The ICC meeting determined that the rules would be relaxed a little for the next round of codes. I think we will have to deal with the increased requirements while under IRC 2006, but it looks like there is a light at the end of the tunnel. 

            Jon Blakemore RappahannockINC.com Fredericksburg, VA

          11. Snort | Jun 02, 2007 01:11am | #49

            Whoa, that's a lotta nuts<G>What's with the 6' thing? We've got to go a foot from corners then 60"...and stick one near each joint...still a whole lotta crankin" I ain't gonna work for Maggie's ma no more.

            No, I ain't gonna work for Maggie's ma no more.

            Well, she talks to all the servants

            About man and God and law.

            Everybody says

            She's the brains behind pa.

            She's sixty-eight, but she says she's twenty-four.

            I ain't gonna work for Maggie's ma no more.

          12. User avater
            SamT | Mar 04, 2007 03:00am | #28

            One of the links bb? posted to a BI forum way up above is a long thread and the discussion makes it clear that this applys to poured walls.

            Only poured walls, CMUs are exempt!

            Some engineer in WA/OR  figured worst case for his state, and those specs were accidentally adopted for the whole nation!?!?!?

            They reckon it'll get changed at the next adoption meeting. . . in three years!

            I guess PA is just the first state to adopt the 2007 codes, cuz the PA reps are raising. . .well you know.SamT

            Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

          13. User avater
            BillHartmann | Mar 04, 2007 03:20am | #30

            "One of the links bb? posted to a BI forum way up above is a long thread and the discussion makes it clear that this applys to poured walls.Only poured walls, CMUs are exempt!"You have it backwards.R404 covers both CMU and concrete foundations.And it says that you either have to meet the requiresments of tables in 404 OR the design standards in the ACI references.Now I have not seen or know anything about the ACI, but based the comments in the BI thread the ACI manual for concrete foundations has design standards that allow the more common spacing of the bolts.And that there is apparently no similar standard for CMU foundations..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          14. User avater
            SamT | Mar 04, 2007 03:37am | #32

            You have it backwards.

            Not my fault, they said it, not me.

            Several times.

            According to them, CMUs still fall under the 2003 code.

            You wanna argue, you gotta find someone with an opinion.SamT

            Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

          15. User avater
            BillHartmann | Mar 04, 2007 03:56am | #34

            You did not link to any specific message, only the thread. In fact I can't find a way to link to a given message.But here is one section.JC Littlefield
            Contributor - posted 12-08-2006 04:24 PM Profile for JC Littlefield Send New Private Message Edit/Delete Post The 2006 IRC allows residential concrete foundations to be designed with ACI 332 without an engineer's stamp. It is prescriptive and even easier to use than the old IRC provisions but more importantly, it contains a lot more practical information. Of course, you have to buy it.http://www.toolsofthetrade.net/articles/showarticle.asp?articleID=2399&position=0&type=article[ 12-08-2006, 04:25 PM: Message edited by: JC Littlefield ] Posts: 70 | From: New England | Registered: Apr 2006 | IP: Logged | Report this post to a Moderator
            homebild
            Frequent Contributor - posted 12-09-2006 04:25 AM Profile for homebild Send New Private Message Edit/Delete Post Does ACI 332-04 apply only to poured concrete walls, or does it apply to concrete block walls as well? Posts: 302 | From: Pennsylvania | Registered: Jul 2004 | IP: Logged | Report this post to a Moderator
            JC Littlefield
            Contributor - posted 12-09-2006 04:53 AM Profile for JC Littlefield Send New Private Message Edit/Delete Post ACI 332 is only for poured-in-place concrete residential footings, foundation walls and slabs. Posts: 70 | From: New England | Registered: Apr 2006 | IP: Logged | Report this post to a Moderator
            homebild
            Frequent Contributor - posted 12-09-2006 07:08 AM Profile for homebild Send New Private Message Edit/Delete Post Thanks JC.That's what I thought.For regions like mine where the norm is to see concrete block construction, there does not appear to be any option for the construction of a block foundation other than to use the extremely burdensome prescriptive requirements of the 2006 or have an architect/engineer design and stamp an alternative, and likely, simpler foundation plan....
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          16. User avater
            SamT | Mar 04, 2007 12:10pm | #39

            You did not link to any specific message, only the thread. In fact I can't find a way to link to a given message.

            Me neither.

            Here's the main menu; http://www.iccsafe.org/cgi-bin/ultimatebb.cgi

            Here's the category Building and Residential Codes --Structural Issues

            Here's another link to that thread 2006 changes for anchor bolts Pages: 1 2  SamT

            Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

      2. dovetail97128 | Mar 04, 2007 04:45am | #35

        Sam,
        Just this morning I talked to a "Dinger" (tract) concrete foundation guy. Told me his company runs 3 crews and poured 1500 foundations last yr. Think they might be having it a bit tougher this coming yr.
        These new requirments are gonna be tough .

        1. User avater
          SamT | Mar 04, 2007 11:27am | #38

          3 crews and poured 1500 foundations last yr

          2 foundations per day per crew.

          Do you think any of those 1500 chunks of concrete had the time to cure properly before the backfill hit?

          I was on a power plant job where the crew I was on did better than 2 pours a day some days but every one of our pours wore forms and wet burlap for a week after the pour.

          Years before I got there, the GC had to rip out a couple hundred yard pour because it cure cracked. We did it right or never did it again for him and this was a 6-9 month job every year or two.SamT

          Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

          1. dovetail97128 | Mar 04, 2007 08:12pm | #42

            Sam,
            Not a chance, they strip early morning after a pour, move on, set up and pour again that afternoon.
            Very simple tract foundations, self leveling wet mud, mono pours for an inverted "T" foundation, not even using footing forms, they just "tack" a few pieces of 1/2 ply to the box form stakes and if it leaks just let it slop out etc. etc.
            No wish to compete against them on my part. I own all the stuff to do it, have it sitting on the truck ready to go , but why bother.

          2. brownbagg | Mar 04, 2007 08:52pm | #44

            they just "tack" a few pieces of 1/2 ply to the box form stakes and if it leaks just let it slop out etc. etc. They do it here too. but use a 2x4 as top screen and brick ledge. they might spill out four yards under the 2x

          3. brownbagg | Mar 05, 2007 08:06am | #45

            The past couple days ther have been talk of aci. Every year I have to buy the complete set of aci. it doesnt change much. Aci is about concrete, not masonary, not framing but concrete. It basically a very boring book. on how to pour, onhow to design, on how to mix.I keep a copy at home and a copy at work.so if anybody has any question on aci, let me know.

  4. brownbagg | Mar 03, 2007 01:04am | #4

    ACI is the American Concrete Institute,. 318 is a very big section that talks about everything. Now ACI is not a code book. Aci is a guideline for concrete construction, Its more on the design of concrete mixes.. But I have the complete set at the office and at home.

    1. EJCinc | Mar 03, 2007 01:41am | #6

      I've looked online and can't find anything specific to anchor bolts from either of those ACI sections.  I do know ACI 332 deals with concrete and ACI 318 deals with masonry.  We do all masonry.

      After my last discussion with our usual building inspector he's telling me that if I can get an architect or engineer to put a stamp on section 2308.6 from the 2003 IRC he will accept that.  I emailed that to the architect I've talking to about this and i'm awaiting his reply.  I can't really see him just throwing his stamp on that and calling it good though.  Seems like there would be some liability on his part.  But we'll see.Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

      1. GHR | Mar 03, 2007 03:12am | #9

        Your problem is you don't understand the building code.In general ...Ahe building code makes worst case engineering assumptions and prescribes a solution.An engineer takes the existing situation and determines if the construction will bear the loads.An engineer will always give you a more liberal solution than the code.

        1. User avater
          jonblakemore | Mar 03, 2007 03:19am | #10

          "An engineer will always give you a more liberal solution than the code."I've not always found this to be the case. Some guys seem to be more interested in protecting their stamp than being efficient. 

          Jon Blakemore RappahannockINC.com Fredericksburg, VA

        2. EJCinc | Mar 03, 2007 03:40am | #12

          Well do you know what it's going to do to the cost of a new home if we have to get an engineer involved with every one?  Up until now we have not had to have plans engineered or stamped.  There goes the entry level housing market in this area then!Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

        3. bobtim | Mar 03, 2007 04:21am | #14

          An engineer will always give you a more liberal solution than the code.

          That statement is simply incorrect.

          The "code" has a prescriptive method of doing something. Usually that is the most cost effective way to get the job done. I have never seen an "engineered" solution that was "easier"  than the prescriptive method.  Granted there are many situations where an engineer is simply the only way to get the job done.

          Sorry to take issue with your blanket statement, but Ijust don't buy it.

          PS  I have a lot of respect for engineers and don't bash them like it seems to be kinda popular on a lot of job sites.

  5. GHR | Mar 03, 2007 01:04am | #5

    Finding an engineer should be easy enough to do.

  6. User avater
    jonblakemore | Mar 03, 2007 02:13am | #7

    Here's a copy of the table from my 2006 IRC. You're right about th 9", that really does seem to be quite a jump from what we're used to.

    I would have a talk with the Chief Building Official in your locale.

     

    Jon Blakemore

    RappahannockINC.com Fredericksburg, VA

    1. DanH | Mar 03, 2007 02:34am | #8

      Note that that document is specifying how many bolts must be present to support the foundation walls against soil pressure, not how many must be present to keep the house in place.Presumably some other scheme such as a steel angle along the top of the wall could be used instead.Curious, though, that they don't specify (in that chart, at least) the construction of the wall -- would make a difference if block, reenforced block, poured concrete, etc. Nor do they make any statement about the structure on top and its ability to resist thrust.
      So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

  7. Shoeman | Mar 03, 2007 03:25am | #11

    They mentioned this and several other unbelievable things with foundations at my continuing ed class this year.

    I don't do any new construction, just minor remodeling - so I didn't pay real close attention, but, I do recall it was huge change from current code.

    Seem to remember something about lots of blocking being required. 

    Another one was that they wanted the poured concrete floor to be like 18" or something above the footer.

    Radical stuff, will have to see if I can find some of the info they gave me and post it here.

    1. brownbagg | Mar 03, 2007 04:18am | #13

      that 18 inches above natural gound so when it rains the water runs away from the slab instead of toward it. that is a very common code item

      1. Shoeman | Mar 03, 2007 04:37pm | #19

        not sure we are talking about the same thing.

        Looked up the informatin from class.  It states that "Top of footing shall be 16" below the bottom of the concrete floor slab minimum."

        Seems to me that the basement slabs around here are currently just poured on top of the footing.

        1. brownbagg | Mar 03, 2007 05:56pm | #21

          yes what they are saying is, the footing needs to be in natural soil, but the slab needs 18 inches above natural soil because of rain water. so you get around this by building a soil pad 18 above natural and then pouring a monolithic slab. that where the footer be turned down, But.... if you dont do a mono. then the footer have to be deep with a stem wall. three course of block.The point I was making is, the 18 is nothing new, its very common. It has some to do with freeze thaw too. In the south it never freezes at all but we still have a 18 inch footing deep

  8. woodroe | Mar 03, 2007 04:26am | #15

    What is the definiton of a "Supported Foundation Wall"?

    What is holding all the courses of block together? In my area we have to core fill with 1 #8 rebar every 6 feet. Anchor bolts within 12" of every corner and no more that 6' apart for the rest. With a whole lot less bolts than that the top course of block would crack loose.

    1. EJCinc | Mar 03, 2007 03:54pm | #18

      It sounds like your building to the 2003 code which is how we had been doing it. 

      We actually put #5 rebar, concrete, and an anchor bolt every 4' o.c.  and then yes we had to make sure that each sill plate had two bolts in it, within 12" from the ends, etc...Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

  9. User avater
    Matt | Mar 03, 2007 06:00am | #16

    What I have to wonder is if this is really going to be enforced, or was it just some guy who recently read the book and had to make a big showing for his audience.  If they are going to enforce it and similar stuff, it sounds like PA has done a 180.  Is it not true that PA had no state wide code as little as 8 years ago?  Sounds like they are having some growing pains.   Or maybe little Hitler is in charge at your county/city/whatever?  There is a town near here that had a guy like that, and builders would routinely have an upcharge for building in that jurisdiction.  Since then he has left and another BI told me "Oh him.... He wasn't very well liked" :-)

    Most states modify model codes into something that is a bit more reasonable for the specific location and building environment.  Here, builders as well as engineers, architects (and maybe even politicians and lawyers) sit on the code board.  I notice that even when we get a new code, a lot of the old amendments are retained.  These modifications take time though.  They are still trying to get the IRC 2003 ratified. :-)

    1. EJCinc | Mar 03, 2007 03:52pm | #17

      In most of the townships we build in we can use any inspector we want.  So of course we stay with the same guy.  So I called him and asked him about this and at he said he had never heard of this and had to check with his boss.  He checked and got back to me saying that yes it went through and unfortuneately they had to enforce it.  I can understand that from liability reasons.  They can't pick and choose what parts of the code to enforce and not enforce.  So yes it is going to be enforced until 1. it gets repealed or 2. we get our basements stamped by engineers.

      Your right we never had a code in PA until I believe it was 02-03 somewhere in there.  And this is the first problem I've had with any of it.Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

      1. User avater
        BillHartmann | Mar 03, 2007 05:35pm | #20

        This is a forum on on the codes.http://www.iccsafe.org/cgi-bin/ultimatebb.cgiThis issue is being discussed inhttp://www.iccsafe.org/cgi-bin/ultimatebb.cgi?ubb=get_topic;f=10;t=001535http://www.iccsafe.org/cgi-bin/ultimatebb.cgi?ubb=get_topic;f=10;t=001658.
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  10. User avater
    PeteDraganic | Mar 04, 2007 05:12am | #36

    I am simply blown away by this change... wow!

    When you're this good, EVERYONE wants a crack at you!

    http://www.petedraganic.com/

  11. User avater
    txlandlord | Mar 04, 2007 06:07am | #37

    Texas Windstorm Code for Zone 1 on the water is 4' O.C. and no further that 18" from a corner. Monolithic slab / 5/8" galvinized anchor bolts in concrete / 2" washer / galvinized nut

     

    1. EJCinc | Mar 04, 2007 04:27pm | #41

      Another good reason to move to TX then!Legal Disclaimer: The preceeding comments are for entertainment purposes only and are in no way to be construed as professional advice. The reader of these comments agrees to hold harmless the poster, EJCinc, from any and all claims that EJCinc offered professional advice, ideas, or comments to the reader that may or may not have resulted in the damage, injury, or death to the readers property or person.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Podcast Episode 685: Patching Drywall, Adding Air Barriers, and Rotted Walls

Listeners write in about running a profitable contracting business and ask questions about patching drywall, adding air barriers, and fixing a patio poured against the house.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • The Trump Administration Wants to Eliminate the Energy Star Program
  • Podcast Episode 685: Patching Drywall, Adding Air Barriers, and Rotted Walls
  • FHB Podcast Segment: Patching Drywall Near a Shower
  • The Unabashed Maximalist

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in