24" O.C. for commercial interior non load bearing partitions.
ML
Thanks. What about for res.?
I believe Residential is 16" On Center, not 100% certain.ML
If you use a powder actuated fastener, one pin every 36" for interior non-load bearing walls, one pin every 18" for interior load bearing walls.
You can check an ICC-ES report for this information from any one of the powder actuated companies ICC report.
Thanks PLUM. I'll check it out.