OK…..This seems like a stupid question, but here goes.
What is the IBC, or BOCA method for sistering a floor joist? I know what I want to see when I do this, but what will the inspector want?
Thanks
OK…..This seems like a stupid question, but here goes.
What is the IBC, or BOCA method for sistering a floor joist? I know what I want to see when I do this, but what will the inspector want?
Thanks
Learn more about the benefits and compliance details for the DOE's new water heater energy-efficiency standards.
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Get home building tips, offers, and expert advice in your inbox
Fine Homebuilding
Get home building tips, offers, and expert advice in your inbox
© 2024 Active Interest Media. All rights reserved.
Get home building tips, offers, and expert advice in your inbox
Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.
Start Your Free TrialStart your subscription today and save up to 70%
SubscribeGet complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.
Already a member? Log in
Replies
The new joists need to meet the support requirements of the code usually 1-1/2 min bearing.
The nailing needs to be sufficient to transfer the full load to the other joist. (In general 16d nails will carry about 100#. Most joists carry 66#/ft so 16" nail spacing works out.)
Here it's two rows of 16d nails, one near each edge of the joist, 16" OC but staggered so you have a top edge nail, then 8" horizontally along the joist to a bottom edge nail, etc.
I glued mine together with yellow wood glue, it makes absolutely sure there won't be squeaks between the sisters in the future.
1 1/2" bearing may be acceptable in many cases, but for long spans it's worth doing the math to see how many psi you're putting on that area.
-- J.S.
I think the question was what an inspector looks for.
What I stated was what I as an inspector would accept. In all cases it is sufficient. I.E. The nails are sufficient to transfer the total load from one member to the other. The bearing is sufficient for dimensional lumber loaded to failure.
Now you are free to follow the perscriptive code. You are free to use glue if you wish. You can even bolt the whole thing together. But I am not going to require a structure to be overbuilt.