Gas and meter sizing help please

madmadscientist | Posted in Energy, Heating & Insulation on April 20, 2008 11:39am

Hello All,

I’m in the process of trying to get the local gas company PG&E to upgrade my meter but I’m running into a few bumps and wanted to get a reality check from y’all.

First off here’s the nameplate BTU requirements of the equipment I am planning to install.

  1. Wolf-highzoot range 120,000 BTU
  2. Tankless WH 200,000 BTU
  3. Boiler for rad heating 200,000 BTU
  4. BBQ 100,000 BTU
  5. Gas dryer 22,000

For a grand total of 642,000 BTU. 

This neighborhood is all on a low pressure supply which I believe is 1/2″WC.  The meter has no regulator it just flows and meters the low pressure gas from the main in the street.  The meters nameplate says its a model 250 and has this spec 275CFH@1/2″WC-I don’t know what that means. 

The hardline from the street is 1.25″ which necks down to 1″ for a run of about 20′ to the meter where it is necked down again to 3/4″ thru the meter and on into the house. 

Here’s what PG&E is saying.  That if they replace the 1″ flex line with 2″ flex line and replace the meter with a larger unit that I will get the flow I need and will not have less than a .5PSI drop in pressure.  Not changing the 1.25″ hardline from the street seems like B.S. to me?

Does this sound okay to anyone?

Daniel Neumansky

Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

Oakland CA 

Crazy Homeowner-Victorian Restorer

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    madmadscientist | Apr 20, 2008 11:51pm | #1

    Oops the title should say Gas line and meter sizing help please.

    I've got another problem with PG&E on this.  They say they won't 'authorize' putting the new meter in the nice hidden little cubby hole that the original one is in.

    View Image

    Its not apparently an issue of the new meter fitting they just don't appear to want to install the new one where the old one is?  When pressed the rep said it 'would'nt be up to code' if it was installed the box.  I asked her what code was that exactly and of course she could'nt tell me... She is referring the matter up to her supervisor..

    What they want to do is put the new meter on the wall to the right of the box 12" in from the edge of the vertical stair bit.

    View Image

    I say that the meter is going to 1. be ugly as sin right up there in front of the house.  2. Going to make this Victorian house look very un Victorian. and 3. Going to obstruct the path to the stairs to get in that door...

    We'll see how it goes...maybe I'll have to go to all elec here...

    Daniel Neumansky

    Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

    Oakland CA 

    Crazy Homeowner-Victorian Restorer


    Edited 4/20/2008 4:52 pm by madmadscientist



    Edited 4/20/2008 4:52 pm by madmadscientist

    1. Karl | Apr 21, 2008 12:13am | #2

      Daniel, Have them put the new meter in however they are inclined to and after the fact pipe it into the cubby yourself. The meter reader is accustomed to reading it in the cubby so he/she probably won't even notice you moved it unless you wait a month or two to replumb it in the new /original location).I think the saying goes, "it is easier to ask forgiveness than permission"That flex line looks very unorthodox and vulnerable to me. I would definitely hard pipe it if you do relocate the new meter yourself.I too get gas from PG&E and have relocated a meter before without anyone taking any notice. Just do a clean workmanlike job of plumbing it and finish off with a nice coat of gray rustoleum paint over the meter and all the pipe fittings, valves, etc. PGE comes out every ten years or so and gives our meter and exposed pipes a fresh coat of paint. If you paint all your new plumbing work yourself I would say your meter wont attract a second glance.
      Karl

      1. User avater
        madmadscientist | Apr 21, 2008 01:11am | #3

        Well I hadn't thought about just moving it.  I might of already made to big of a stink for them to forget about it...

        It seemed to me like the rep was saying that they just didn't want to go thru the extra work of plumbing in the new 2" line to the cubby.  I told her that I'd do it and she nearly had a fit. 'EVERYTHING from the street to the valve on the meter is property of PG&E, you are not allowed to touch it..blah blah blah...'

        That janky yellow flex line from the riser to the meter is just temp the foundation guys plumber put it on so they could lift-level the house.  I have not changed it cause I'm waiting to get the new meter.

        Any idea of my BTU requirements will work with the plan they have outlined?

        Daniel Neumansky

        Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

        Oakland CA 

        Crazy Homeowner-Victorian Restorer

        1. Karl | Apr 21, 2008 01:48am | #5

          PGE would never agree to you touching the plumbing prior to the meter. Like I said it is easier to ask forgiveness than permission. As long as you follow standard practices and plumbing conventions no one will ever notice you moved things. I am assuming it is obvious that one would never want to touch the plumbing upstream of the main pge shut off valve. The guy who comes out and installs your meter will likely never return. If you think/know they are coming out again then wait til they have made their final visit and then relocate the meter.I don't know about the flow restrictions in your main supply pipe and meter but I would just get the biggest one they will install and try it out. I like the previous suggestion of a combination boiler hot water heater rather than two separate units. It is hard to imagine a single family residence routinely requiring the kind of btu consumption you have outlined? Maybe so, but it sounds like a lot of gas for one family.In California I have generally concluded elec is more expensive a heat source than gas but if you are able to add solar panels to your roof and have sufficient sun exposure it might be a better system than gas over the long haul. The system where pge buys back your surplus solar (runs meter backwards) seems to work really well for countless pge customers down here in santa cruz.Karl

    2. JohnCujie | Apr 21, 2008 02:07am | #6

      PG&E's green book does have a spec for a meter cabinet. Or at least it used to. You may have to modify yours to comply. If you want to follow the rules.John

    3. peteshlagor | Apr 21, 2008 02:05pm | #9

      The spot I gussied up down in San Juan Capo similarly had the meter right there for everyone to see.  I, too, had it swapped out for a bigger one, but in the same spot.

      The landscape designer solved the problem with a nice bush.

       

    4. User avater
      popawheelie | Apr 21, 2008 04:45pm | #10

      I just had to move a meter because of a storage shed I built around it. They don't want the meter in any kind of structure. They want it exposed to the open air so if there is any leakage the gas has no way of accumulating.

      I'm not positive but my city inspector and my wife who works in the energy industry said the oversight for this stuff has changed. Believe it or not it is because of Homeland security. The potential for anything blowing up was looked at and they thought it best to put all of it under the energy companies.

      The feds put jurisdiction under the energy companies.

      You could just hide with a bush afterwards.

      1. User avater
        madmadscientist | Apr 22, 2008 12:26am | #13

        That makes sense except for places like here in SF where all the neighborhoods with row houses have the meters in the garages.  This is basically outside its just in a cubby under the stair landing.

        I was just told that nat gas is lighter than air so as long as the cubby is vented at the top and bottom (I would think it would be fine).

        Yea hiding it with a bush is an idea but its still going to be directly in the way of the stairs down to the bottom floor of the house.

        Daniel Neumansky

        Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

        Oakland CA 

        Crazy Homeowner-Victorian Restorer

        1. User avater
          popawheelie | Apr 22, 2008 02:07am | #14

          I understand the pita it is but I had no choice. I offered to ventalate the room but they just wouldn't listen. They wanted it outside. Period. At my cost.

          In the end I let it go. If there is even the slightest chance of it being dangerous I'll comply. But at first it made me angry. It just took a while to get used to the idea.

          The crew that moved it was a nice bunch of guys. A made them two batches of cookies.

  2. plumbbill | Apr 21, 2008 01:27am | #4

    1 cubic foot = 1,031 btu's or 1 therm

    275cfh = 275 cubic feet per hour

    275 cubic feet = 283525 btu's

    In other words it will run about 1/2 of your full demand

    Normally you won't use all of those at the same time----- kicker------ water heater & boiler will run at the same time in the winter.

    If you had a combo boiler/water heater under 300K you would be fine.

    Yours is the first low pressure distribution system that I have seen.

    “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

    1. User avater
      madmadscientist | Apr 21, 2008 02:27am | #7

      My radiant expert is pushing me towards a combo boiler-WH.

      If I did that do you mean that the existing meter would handle it and the existing 1" pipe?

      It would be cheapest for me if the 1" pipe would handle it and they could just pump the hardline up to 1" and put a bigger meter in the cabinet.  I plan on running a 1" line from the meter to the rest of the house with 3/4" branches running to the appliances.

       

      Daniel Neumansky

      Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

      Oakland CA 

      Crazy Homeowner-Victorian Restorer

      1. plumbbill | Apr 21, 2008 02:31am | #8

        Here's a good rule of thumb for sizing. This is in CFH, but these numbers are figured from a meter that has a regulator.

                      Length in Feet

        Pipe Size

        10

        20

        30

        40

        50

        60

        70

        80

        90

        100

        1/2

        174

        119

        96

        82

        73

        66

        61

        56

        53

        50

        3/4

        363

        249

        200

        171

        152

        135

        127

        118

        111

        104

        1

        684

        470

        377

        323

        286

        259

        239

        222

        206

        197

        1-1/4

        1404

        955

        775

        663

        588

        532

        490

        456

        428

        404

        1-1/2

        2103

        1445

        1161

        993

        880

        795

        734

        688

        641

        605

        2

        4050

        2784

        2235

        1913

        1696

        1538

        1413

        1315

        1234

        1165

        2-1/2

        6455

        4437

        3503

        3049

        2703

        2449

        2253

        2096

        1966

        1857

        3

        11412

        7843

        6299

        5391

        4778

        4329

        3983

        3705

        3476

        3284

        Pipe Size

        125

        150

        200

        250

        300

        350

        400

        450

        500

        550

        1/2

        44

        40

        34

        30

        28

        25

        24

        22

        21

        20

        3/4

        93

        84

        72

        64

        58

        53

        49

        46

        44

        42

        1

        174

        158

        136

        120

        109

        100

        93

        87

        82

        78

        1-1/4

        358

        324

        278

        246

        223

        205

        191

        179

        169

        161

        1-1/2

        536

        486

        416

        369

        334

        307

        296

        268

        253

        241

        2

        1033

        936

        801

        710

        643

        592

        551

        517

        488

        463

        2-1/2

        1646

        1492

        1277

        1131

        1025

        943

        877

        823

        778

        739

        3

        2910

        2537

        2257

        2000

        1812

        1667

        1551

        1455

        1375

        1306

        “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

        1. User avater
          madmadscientist | Apr 22, 2008 12:22am | #12

          Hi Bill and thanks for the table,

          So my math says that I need ~622CFH for all the BTU's.

          Is that table from the meter into the house?  Or from the street to the meter?

          If those are low pressure #'s then dang I will need at least a 1.25" pipe for the 20' run from the street to the meter.  Then after the meter my 1" pipe idea isn't going to be big enough..Wow, I don't think I've ever seen residential gas lines bigger than 1" inside a house...

          Of course if that table is only for higher pressure gas then all bets are off and I'll need even bigger lines...yowza

           

          Daniel Neumansky

          Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

          Oakland CA 

          Crazy Homeowner-Victorian Restorer

          1. plumbbill | Apr 22, 2008 02:55am | #15

            Table is low pressure from the regulator.

            My house has a 1.25" main cause my furnace is at the opposite end of the meter.

            When I did a friends I had to install a 1.5" main----- same reason.

            “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

          2. User avater
            madmadscientist | Apr 22, 2008 03:32am | #16

            Okay that makes sense so I can consider everything to be 'after the regulator' because the entire system is at .5"WC

            Now PG&E says the line from their main to my prop line is 1.25" and this line is about 20' long.  That gives me 955CFH at that point.  Then they want to switch to a 2" line from there for the ~20' to my meter. Does that make sense to you?

            From the meter its about 60' to the farthest away appliance-gas bbq.  To be safe should I do 1.5" from the meter thru the house?

             

            Daniel Neumansky

            Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

            Oakland CA 

            Crazy Homeowner-Victorian Restorer

          3. caseyr | Apr 22, 2008 04:31am | #17

            As long as you are installing a new meter, you might consider also installing an excess flow valve. I believe these are required in Alameda County whenever there is a sufficient amount of remodeling is done. In Contra Costa County, an earthquake shutoff valve for the whole house is required when the building is sold or remodeled - along with excess flow valves on each appliance. Thus it is likely that the requirements will be tightened over time in your county. Besides, additional shutoff protection is probably a good idea in any event. It will probably be a lot cheaper to install a shutoff valve when a new meter is being installed than it would later on when the meter is in place. (Last I heard, the going price for having a plumber work on the gas meter was in excess of $120/hr.) I think an excess flow valve runs around $100 or so, the earthquake shutoff valve is probably $20 to $30 more. Having both excess flow and earthquake shutoffs, like is the requirement in Contra Costa County, is probably overkill.

          4. plumbbill | Apr 22, 2008 07:54am | #18

            >>>>>Now PG&E says the line from their main to my prop line is 1.25" and this line is about 20' long.  That gives me 955CFH at that point.  Then they want to switch to a 2" line from there for the ~20' to my meter. Does that make sense to you?<<<<<<<

            Yeah it makes sense, we size gas lines from the furthest point to the source.

            “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

        2. Gabriel24 | Apr 23, 2008 08:37am | #19

          This has been a very interesting topic. As usual, the message starts at the very practical, and ends up at the very scientific. I am referring to the chart. Uniform Plumbing Code says : For a maximum of 50 feet and a maximun of 466 CFH  the pipe size is Half inch. Just one observation, the code says 3/4 of an inch for all freestanding appliances, and I am referring to the BBQ. Also, some pipes before the tee connection gather the BTU of the other appliances and therefore require a larger size. Again, I  admire the chart, it is educational. If I get too scientific, I apologize.

          1. plumbbill | Apr 23, 2008 02:48pm | #20

            I'm not sure I'm following you.

            What code says that at 50' of 1/2" you can 466 CFH?

            “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

          2. User avater
            madmadscientist | Apr 24, 2008 12:52am | #21

            I think he's reading the chart wrong.  50' of 1/2" pipe according to the chart is only good for 73CFH. 

            Had the PG&E rep and her boss out to the house this am.  Turns out the meter with the cap I need is a commercial meter and won't physically fit in the space.  The biggest residential that will fit in the space is rated at 350CFH so I either gotta  cut way down or go with a commercial meter.

            He did suggest an alternate spot for the meter that will be a lot less  obvious from the street and not screw with the Victorian looks of the house.

            I can't believe what they are going to charge me though...If I uncover the existing gas line/valve and dig a trench all the way to the new meter spot ~10' I have to go under the driveway curb and SWMBO is going to have to pry up some of those bricks she laid-boy am I glad we listened to you guys and did them in sand not mortar-and I have the house line brought to the area of the new meter they are going to charge me...~$3500!!! 

            $3500 is highway robbery for what they are doing.  I have to pay thru the nose for the privilege of buying much more of their product....where's the logic in that?

            Daniel Neumansky

            Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

            Oakland CA 

            Crazy Homeowner-Victorian Restorer

          3. Gabriel24 | Apr 24, 2008 08:36am | #25

            The code is Uniform Plumbing Code . Plumbing a House by Peter Hemp page 170 Taunton Press. The table reads Natural Gas Maximum Capacity of pipe CFH Feet 50  CHF 466 pipe size 1/2 inch.

          4. plumbbill | Apr 24, 2008 02:52pm | #27

            That's strange, I wonder what year that book came out.

            UPC doesn't cover gas pipe anymore, now covered by the UMC.

            My 1994 UPC book has gas sizing, I'll dig it out & see what the charts in have to say.

            “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

          5. rich1 | Apr 26, 2008 01:29am | #28

            B149 gives me 95,000 btuh at 50 feet at 7"-14" w.c. based on a 1" pressure drop.

          6. User avater
            madmadscientist | Apr 24, 2008 12:58am | #22

            Can you explain a bit more about the pipes before the T gathering the btu's of the other appliances? 

            I am planning on running a 1.25" main line into the house and then branching off from that with short runs of 3/4" line to the appliances.  Will a setup like that solve this issue?

            All my big gas appliances spec a 3/4" gas line.  But then the biggest I could find a flex line is 5/8" id?  The guy at the real hardware store looked at me like I was crazy for asking for anything bigger?  I've got a 200,000BTU tankless heater that has to suck gas thru a 5/8" line?  Does that make any sense??

            Daniel Neumansky

            Restoring our second Victorian home this time in Alamdea CA.  Check out the blog http://www.chezneumansky.blogspot.com/ 

            Oakland CA 

            Crazy Homeowner-Victorian Restorer

          7. JohnSprungX | Apr 24, 2008 02:21am | #23

            Take a look at Taunton's "Code Check: Plumbing" book.  It has the tables and an explanation of how to use them to size gas pipes to multiple appliances. 

             

            -- J.S.

             

          8. Howard_Burt | Apr 24, 2008 02:33am | #24

            Take a look at these for your tankless connections.

            http://www.dormont.com/dmc/uploadedfiles/res/ResourceCenter/tankless-gass-connect-spec.pdf

          9. Gabriel24 | Apr 24, 2008 08:49am | #26

            Example: The farthest appliance from the meter is 75 feet . Another appliance branches off at 50 feet. This branching off is caused by putting a tee. So now you have 75 feet + 50 feet. That is a total of 135 feet. The pipe between the tee and the meter must be larger than 1/2 inche because it is going to supply two appliances. If you look at the chart under 135 feet and the combined CFHof the two appliances, it will give you the size of the pipe. Chances are that 5/8 (like you say) is o.k. From a practical point of view, we install pipes just a tiny larger if in the future they decide to have additional appliances.

    2. roger g | Apr 21, 2008 04:55pm | #11

      I too had never heard of such a thing until a couple of years ago when I was offered a job (didn't take) of running a gas line crew in downtown Vancouver BC. They were replacing all the low pressure gas lines in that part of the city. The steel pipes were about 6 inches in diameter and they were running the new high pressure lines inside the old pipe. In the front of each house the old pipe was broken out (about 4 feet) and the house connection was made and torpedoed to the new meter which now had a reg.
      Roger

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding the Right Fixer-Upper

Get expert guidance on finding a fixer-upper that's worth the effort.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data