Hi Guys,We are getting ready to install a geothermal ground loop for our home.Some of our research points us to 500′ of trench per ton of heating/cooling.Local HVAC people have calculated our 3500 sq.ft. home at just over 5 tons of loading and their software called for only 1000′ of 3/4″tubing in 4/250′ trenches.Our info calls for double that size So we have decided a ground loop length of 2000′ using 11/4″ poly.We are here in northern Va. where ground temperatures are 55 degrees. We’ve been told that larger loops will short cycle but would rather error larger than smaller.Any input would be appreciated .Thanks,again,Tess |
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story

From building boxes and fitting face frames to installing doors and drawers, these techniques could be used for lots of cabinet projects.
Featured Video
How to Install Exterior Window TrimHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Fine Homebuilding Magazine
- Home Group
- Antique Trader
- Arts & Crafts Homes
- Bank Note Reporter
- Cabin Life
- Cuisine at Home
- Fine Gardening
- Fine Woodworking
- Green Building Advisor
- Garden Gate
- Horticulture
- Keep Craft Alive
- Log Home Living
- Military Trader/Vehicles
- Numismatic News
- Numismaster
- Old Cars Weekly
- Old House Journal
- Period Homes
- Popular Woodworking
- Script
- ShopNotes
- Sports Collectors Digest
- Threads
- Timber Home Living
- Traditional Building
- Woodsmith
- World Coin News
- Writer's Digest
Replies
Short cycling will cause premature compressor failure. The refrigerant carries the oil through the compressor to lubricate it. When the unit short cycles, not enough oil is move, and the compressor will burn up in five to seven years, based on usage.
Another problem with over sizing a unit and it short cycling is the lose of dehumidification. It may cool your house air but not run long enough to dehumidify the air. You will be cool and clammy.
Loop size is based on heat transfer of the particular type of ground it is placed in. My FIL system is a 5 ton with 5 vertical loops of 165' each.
Dave
How can oversizing the ground coils call short cycling?
To rapid heat exchange at the condenser will lower the head pressure and suction pressure. The compressor will shut down on the low suction limit. A throteling valve that operates off of the head pressure will probably work. Hope the installer is up on how to check superheat.
Honeywell makes a pressure valve that will work for this application. Next question is how it will affect the condenser circulating pump. The only time I have used this set up was on water cooled condensers for five ton Carrier units. One used our chilled water system for the condenser, and the other used domestic water. In neither case did we have to be concerned about causing to much head pressure for a pump.
Do you know how a single speed circulating pump would fare if you choked down the supply say to 80%, or stacked up 10 to 20% more head pressure than its' rating?
I don't have a clue, but am interested in how it might work.
Dave
"Do you know how a single speed circulating pump would fare if you choked down the supply say to 80%, or stacked up 10 to 20% more head pressure than its' rating?"
A common centrifical pump can be throttled down without any problems. And typically the power demands go down. In fact you can run it deadheaded, the only problem is if you have a big pump all of the curning of the water in the dead head pump will cause it to heat.
Actually this sound like a great application for a variable speed motor.
Go for a second or third opinion. I checked with the guy who did mine, and his off the top of the head guess is that for horizontal you'd need in the neighborhood of 800' of 1" pipe / ton. 5 parallel loops in a 200' trench 15' apart using about an acre of ground. He also said 1 1/4 pipe is not usually used in horizontal.
Note that http://www.geothermalheatpump.com/how.htm mentions 700' to 1000'/ton for a slinky tube arrangement and suggests that's better than horizontal.
My vertical installation in WNC is an 800' well (1700' of 1 1/4" tube) for a 4 ton pump.
Guys;we've heard of short cycling but feel that a valve plumbed into the feed or return line to throttle, if necessary,would avoid that problem.Water Furnace rep convinced us that slinky ground loop might be much to difficult to purge.Besides,our 11/4" poly is on its way;2000' of unbroken tubing. Tess!
Edited 8/11/2003 5:57:16 PM ET by tess
After you have it running, it should be interesting to see the performance. Based on temp differentials and flows, they should be able to tell the btu's it's producing. I hope you come back and tell us how it performs.
We hope to be with this heating system by October.Will let all know of performance.From several posts we are somewhat concerned about oversizing the loop and may make adjustments.Thanks for your imputs.Tess