GFCI puzzle

brucet9 | Posted in Energy, Heating & Insulation on February 19, 2010 09:37am

1970’s construction; steel boxes, wires in conduit, no separate ground wires.

Two outlet circuits in kitchen; circuit A with two outlets, one on each side of the sink; circuit B with one outlet 5′ from sink. They are on adjacent 20A breakers in the panel. Neither has a GFCI. Outlets are on pigtails. Both test properly wired using three-prong tester – two amber lights.

I installed a GFCI in circuit A with its dependent outlet on the load terminals; tested ok from both outlets.

I installed a GFCI in circuit B on the same pigtails as the old outlet; nothing on Load terminals. There are a hot, two lines branching out of the box into other conduits, and the pigtail all wire nutted together. The pigtail white and companion whites to the hot wires are wire nutted together. As soon as I turned the breaker back on, GFCI A tripped and could not be reset; GFCI B remained tripped and could not be reset. There was nothing plugged into either GFCI nor the dependent outlet on A.

When circuit breaker A is off, circuit B GFCI works normally. When breaker B is off, circuit A GFCI works normally.

All the outlets are Decora style, and there are GFCI’s in the bathrooms, so I’m guessing whoever upgraded from the original outlets found the same problem and couldn’t solve it so they just put standard outlets instead of GFCI’s in the Kitchen.

 Anyone have an idea what’s haunting these circuits? 

Reply

Replies

  1. BigBill | Feb 19, 2010 11:46pm | #1

    I think that they share the same neutral phase.  Do the two hots give you 220volts or nothing?

    You should get 220.  If you don't get 220 the hots are both feeding the neutral in the same phase and tripping each other.

    1. brucet9 | Feb 20, 2010 01:48pm | #2

      "If you don't get 220 the

      "If you don't get 220 the hots are both feeding the neutral in the same phase and tripping each other."

      I don't understand.  By that logic, shouldn't any two GFIs in the house, if they are on the same phase trip each other?  If there are more than two GFIs in the house, at least two of them must be on the same phase.

       

  2. gfretwell | Feb 20, 2010 09:58pm | #3

    I would start by disconnecting the wires on the load side of A. See if that helps.

    You are sure you are on the LINE side of the GFCI with the feed???

  3. User avater
    MarkH | Feb 21, 2010 07:35am | #4

    BigBill is partially correct.  The GFCI outlets won't work on a shared neutral.  One way that will usually indicate this is a red hot wire on one circuit.  GFCI outlets will trip when there is a very slight difference in the currents on the hot and neutral. 

    1. gfretwell | Feb 21, 2010 12:37pm | #6

      You can't share the neutral on the load side but it can't see the line side.

  4. gfretwell | Feb 21, 2010 10:03am | #5

    It really depends on how old the GFCIs are, whether they work when miswired and the new ones immediately trip. Isn't that the problem?

    1. brucet9 | Feb 21, 2010 03:15pm | #7

      I installed new GFIs and they both work correctly as long as the other one's breaker is off, but the first one trips as soon as the second breaker is turned on.

      That brings up another wrinkle to this.  New GFIs come out of the box in tripped condition - you have to reset them after installing.  When I installed GFI B, GFI A tripped as soon as I turned breaker B back on.  I had not yet reset GFI B and in fact GFI B could not be reset, not even for a fraction of a second as with GFI A.  It was as if GFI B reset button was stuck.

      I know it was not an out-of-box failure, because with circuit breaker A off, GFI B worked normally.

  5. DanH | Feb 23, 2010 09:17pm | #8

    My guess is that somewhere circuits A and B have their HOTS cross-wired, so that either breaker energizes the circuit.  GFCI B is downstream from GFCI A, but breaker B feeds into the link between the two.

    Trace the load wires coming out of GFCI A.  Likely they lead to some other outlet, and from there to GFCI B.

    1. brucet9 | Feb 23, 2010 09:37pm | #9

      "My guess is that somewhere

      "My guess is that somewhere circuits A and B have their HOTS cross-wired, so that either breaker energizes the circuit" 

      If that were the case, I could not have cut power to one or the other circuit to install the GFCIs.

       

      There is only one pair of load wires on GFCI A, a white/black pair exiting into a conduit at the bottom of the box and there is one white/black pair entering the bottom of the box of the dependent outlet and they go dead when GFCI A trips; that outlet is end-of-line, so there is nothing downstream from it.  Whatever connections there may be in other boxes, perhaps behind the hard-wired trash compacter, I don't know.  

      I've referred an electrician friend to the HO.  Perhaps I'll hear back one day just what was wrong with that wiring.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

The Fine Homebuilding Interview: Lloyd Alter

This author and architect discusses achieving carbon reduction in the home-building industry through radical sufficiency and using less.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Convert a Porch to a Mudroom
  • Podcast 599: Trees Moving Buildings, Epic Thermal Bypasses, and Supplemental Dehumidification
  • Podcast 599: Members-only Aftershow — Tools That Changed Residential Construction
  • Remodeling Done Right

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • Code Check Complete 3rd Edition
    Buy Now
  • Pretty Good House
    Buy Now
  • 2022 Fine Homebuilding Archive
    Buy Now
  • 2023 Tool Guide
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 318 - October 2023
    • Make Mudsills Square and Level
    • Turn Up the Heat With Induction Cooktops
    • The Fine Homebuilding Interview: Lloyd Alter
  • Issue 317 - Aug/Sept 2023
    • Finishing Drywall With Seamless Results
    • A Flat Roof in a Cold Climate
    • Compact Cordless Shop Vacs
  • Issue 316 - July 2023
    • Timber-Framed Solar Canopies
    • Build a Transom Above a Stock Door
    • Understanding Toilet Design and Efficiency
  • Issue 315 - June 2023
    • How to Craft a Copper Roof
    • 5 Lessons from Building in a Cold Climate
    • The Advantages of Cellular PVC Siding
  • Issue 314 - April/May 2023
    • 7 Options for Countertops
    • Tool Test: Wood-Boring Bits
    • Critical Details for Ductless Heat Pumps

Fine Homebuilding

Follow

  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok
  • twitter

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok
  • twitter

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in