I am doing some light remodeling on a 10 year old home and find that a dimmer switch will not work in some parts of the home. Called the manuf., of the rheostat, who walked me through some possible problems and concluded that I must have a imbalance ( in current ?) , in the home. What is it and how to correct it? Sez the rheostat won’t work with a imbalanced load. Thanks
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story

DeWalt's hydraulic impact driver makes less noise without sacrificing power.
Featured Video
How to Install Cable Rail Around Wood-Post CornersHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
Are they line voltage or are they low-voltage dimmers? In other words, is there a neutral connection to the dimmers themselves?
I can't picture what the guy is talking about unless it is somehow related to the neutral(s) in the circuit(s).
Ed
No neutral connected to the dimmer.
What are the symptoms? No light at all? No dimming capability?
I ask because I've just never heard of such a thing (dysfunctional dimmers due to load imbalance) in all the years I've been doing electrical work.
Edited 6/5/2007 9:12 pm ET by edlee
I have 120v in to the dimmer and nothing out. I put a normal switch in place of the dimmer and it works perfect. I even took an identical dimmer from elsewhere in the house(it worked fine in it's original place) and same problem. Keep thinking!
is the power off when you are connecting the dimmers ?
.
.
.
., wer ist jetzt der Idiot ?
They aren't rheostates. They are electronic switches that quickly turn the voltage on and off, every 1/2 cycle.What is the brand and model of the dimmer?What kind of light are you trying to control?.
.
A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
I am trying to control incandecent can lights with a Lutron DV-600 preset dimmer. It is a 600 watt dimmer.............I just thought of something. Since it is 600 watt and I have 9 cans ( not my idea) and who know what bulbs we have in them, I may be putting too much load on the 600 watt dimmer. Tomorrow I'll check watts and eliminate some as a trial. Well ..DUH.. maybe thats the problem. Thanks
Yeah, 9 cans at 60 watts would be 540W, and I never like to load a 600W dimmer with more than about 450W if it can be avoided.
So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin
"Imbalanced load" is pretty meaningless. You're not trying to dim fluorescent or low-voltage lights, are you?
So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin