Kitchen Backsplash & Elec. Codes et al

Nuke | Posted in General Discussion on March 11, 2006 03:11am

Morning All! And no, I don’t sleep.

After reading about another poster’s project of installing a stainless steel backsplash behind the cooktop, I got wondering about the electrical codes for the kitchen. I know someone (or two or three) provided a handy reference on the frequency and type of outlets needed in a kitchen per the NEC, but I was wondering about if these outlets had to be in the wall vs. being surface-mounted.

Any able to shed some light on this aspect?

Reply

Replies

  1. User avater
    BillHartmann | Mar 11, 2006 03:56pm | #1

    They can be surface mounted. Or even tombstone and mounted on the countertop. But that is not very atractive.

    But I can't think of any surface mount that you would do in a kitchen except PlugMold. That is unless you wanted the commercial look and mounted metal boxes and exposed conduit.

    1. User avater
      Nuke | Mar 11, 2006 04:23pm | #2

      I guess the reason why I wondered about surface-mounting was due to the difficult and premium of getting custom laser-cut (factory custom) holes. Unless someone isn't looking for that commercial/industrial-look then why SS in the first place? :)

      1. 30ALL | Mar 11, 2006 05:52pm | #3

        If SS is installed only behind stove or range area like many people do, you don't need to have an elec outlet. Only if you want to use SS behind counter top, then you need to meet the codes, small appliance outlets every 4' behind counter top. I'm sure that can be done with metal fabricator to cut the holes at extact spots of your elect outlets.

      2. booch | Mar 11, 2006 07:41pm | #5

        I agree SS is kind of a sterile look but the price shouldn't be the issue.

        Laser cutting is getting pretty common. In the Milwaukee area I can name 5 places that do that kind of work. I'm sure it is common throughout the nation. Laser cutting isn't just for the James bond movies. In industrial metal working it is the primary fabrication method for sheet stock.

        In our use as a cosmetic backsplash, setup is the cost problem. No one wants to create a drawing from a napkin sketch then lase' it only to have the buyer say it doesn't meet the need 'cause it is "off". Nor do they want you to walk in to the shop and yammer on for an hour. In this environment time is money and often the difference from bankruptcy. Drafter, laser operator, etc all cost a lot when you compute in overhead.

        So.. make it simple for them & cheaper for you. If you want to laser cut steel or SS the best way is to create your own cad drawing (a dxf or dwg is the format needed) and take the file (better to e-mail after the relationship is struck) to a laser shop. Lead time is a week or two and it will cost you a minimum of 150 bucks. Now material cost gets factored in the larger it is etc. Also the more hands that touch it the pricier too.

        Match that to setting tile and it it could come out the same. Then again the previous thread I chimed in to say cleaning is more of an issue. And it all rests on cosmetics. What does your customer wish to see.Jack of all trades and master of none - you got a problem with that?

      3. User avater
        BillHartmann | Mar 12, 2006 02:55am | #7

        PlugMold (a strip of recpetacles in a metal chanel spaced every 6-18") would be ideal for that kind of situation.Mount it on a cant strip just under the bottom of the upper cabinets.

        1. User avater
          Nuke | Mar 12, 2006 03:20am | #8

          Actually, since 'faceplates' for electrical outlets can be SS (right?), why can't the SS backsplash also be the outlet faceplate, too? Does the GFCI reset button have to be on the outlet vs. the circuit breaker on the main panel?

          1. User avater
            maddog3 | Mar 12, 2006 03:41am | #9

            do you mean just cut out the backsplash for the GFI face?there is no access to the wiring then.
            .
            .
            " Wer hat den Idioten jetzt? "

          2. DanH | Mar 12, 2006 04:00am | #10

            But kinda neat option would be a larger opening with a matching access panel cut for the outlet. Would ease the problem of getting dead-on accuracy for the outlet locations -- just leave a stub in approximately the right place and install the box afterwards. Or the backsplash could be fabbed with a channel bent into it, and a strip cover installed after wiring through the channel.I hafta believe that this is a general enough problem that solutions are available.

            If ignorance is bliss why aren't more people

            happy?

          3. User avater
            maddog3 | Mar 12, 2006 04:23am | #11

            that channel idea sounds similar to commercial restaurant equipment.. primarily work tables, where some mfrs weld a j-box to an opening....and the box is usually the smallest one they can find...
            .
            .
            " Wer hat den Idioten jetzt? "

  2. notDusty | Mar 11, 2006 07:36pm | #4

    Hi Nuke ,

                    Check your local codes , here in Oregon believe it or not an out let must be located within 2 feet from the center of the sink . This can create a challenge in some applications . The surface mounted receptacle would be a nice place for water to go .

             dusty

    1. plumbbill | Mar 11, 2006 09:11pm | #6

      I'm not an electrician but I have to deal with their codes on my plumbing placement on many occasions.

      Here in WA state not 100% positive, but I'm pretty sure any countertop 18" or wider needs an outlet, & anything within 5' of a water source needs to be GFCI.

      1. FrankDuVal | Mar 12, 2006 06:45am | #13

        Close, try any counter 12" wide needs a receptacle and all kitchen 120 volt receptacles , not just within 6' of sink, need GFCI protection (with a few exceptions for stationary equipment). This is residential NEC.Frank DuVal You can never make something foolproof because fools are so ingenious.

  3. User avater
    JeffBuck | Mar 12, 2006 04:35am | #12

    do a layout where the boxes fall between studs ...

    get the cut outs sized and placed exact ...

    leave the wires hanging loose ...

     

    bust out big holes in the drywall ...

     

    and pop in some remodeling boxes from the front.

    Jeff

        Buck Construction

     Artistry In Carpentry

         Pittsburgh Pa

  4. renosteinke | Mar 12, 2006 08:49pm | #14

    I've recently dealt with this issue. Let me tell you what my solutions were.

    The holes I put in the sheet metal were not particularily neat; I used a drill and a saber saw, with LOTS of masking tape on the saw baseplate. The hole did not need to be "perfect" as I still needed to place a cover plate on the receptacle. The ones I used were also of brushed stainless steel.

    If you re-do your kitchen, you should bring it up to current code. I'd like to sum up the NEC requirements. Keep in mind that the NEC is but a "safety minimun," and is not intended to tell you how to design you place!

    A kitchen requires at least two "small appliance circuits." These must be 20 amp, and have GFI protection. These are the circuits that are intended to serve the counter-top receptacles.
    It is very common for a kitchen to have additional circuits, that are often not GFI protected. For example, refrigerators, dishwashers, trash disposals, compactors, and large microwaves are often on circuits separate from the two required circuitc. So are the lights.
    If you are intending to power the range hood with a fan that plugs in (as opposed to hard-wires), then this must be it's own 20 amp circuit. (The code guys figure that someday there will be a microwave over in that space).

    The dishwasher and trash disposal typically share a circuit. Here, it is common to have a "split" receptacle under the sink, with one part controlled by a switch (the disposal plug in here). Check your local rules- some places want these appliances 'hard wired.' This circuit is usually not GFI protected....a fine detail of the code is that counter receptalces need GFI protection, but switches do not.

    In most cases, receptacle placement is determined by measuring the counter along the wall. Every counter space over 12" wide needs a receptacle, and every point along the wall must be within 2 ft. of a receptacle. Areas behind sinks, stoves, etc., are not included in this, and need no receptacles.
    The receptacles may be on the wall, mounted on the backsplash, mounted on the counter top using a "tombstone" (you're not allowed to put them in facing up), in the face of the cabinets (within 6" of the top), under the lip of the counter, or even on the bottom of the cabinets above (so long as the face of the receptacle is not more than 18" above the counter). I suppose that you could also drop a cord from the ceiling!

    Plugmold can be a good solution, with one caution: the receptacles need GFI protection! For a 'clean' install, this may mean your using GFI breakers, rather than a GFI recepracle. And- you still need two circuits.

    Where the counter forms a peninsula, or there is an island....well, there are some code provisions specific to them- and this post is long enough already! :-)

    1. User avater
      BillHartmann | Mar 12, 2006 10:23pm | #15

      Here is a summary of all of the requirements.http://www.codecheck.com/pg27_28electrical.html#rough

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Tool Test: You Need a Drywall Sander

We tried out a range of rotary and random-orbit sanders to compare their dust collection, quality of finish, and user fatigue after hours of sanding.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Podcast Episode 684: Masonry Heaters, Whole-House Ventilation, and Porch Flooring
  • FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity
  • Tools and Gear for the Moms Who Get it Done
  • An Easier Method for Mitered Head Casings

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 81%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in