upnorthframer | Posted in Energy, Heating & Insulation on January 9, 2009 06:15am

In my new home I have a sealed combustion boiler, sealed combustion fireplace, air exchanger (zoned) for bathroom venting, and an electric range.  My inspector is insisting that I install a grill in the ceiling of my house with a pipe to the outside for make up air.  This seams odd to me as none of my appliances are using inside air for combustion air.  Only the dryer is blowing air out, but not combusting it.

In addition, in Wisconsin, the code reads:  “If your dwelling does nto ahve any open combustion appliances, then you do not have any combustion air requirements, and by code, can rely upon infiltration through building cracks for makeup air”

Inspector won’t specify with me, but is he considering the drying as using combustion air?  Is this correct? 

upnorthframer

Reply

Replies

  1. DanH | Jan 09, 2009 06:32pm | #1

    Is the "air exchanger" a true 2-way heat exchanger? If so, I'd suspect that the inlet duct has no positive closer arrangement to prevent it from drawing air in if there's negative pressure in the house. This should suffice to provide makeup air for the dryer.

    Doesn't code there require a whole-house exchanger or HRV, for humidity abatement in the winter?

    God is REAL, unless explicitly declared INTEGER
    1. upnorthframer | Jan 09, 2009 07:34pm | #3

      my air exchanger is an HRV.  It is zoned in the bathrooms however, thus meaning I can turn on air exchange in just one bathroom at a time.

      upnorthframer

      1. DanH | Jan 09, 2009 08:36pm | #4

        It PROBABLY provides sufficient "makeup air" for the dryer, even when not operating.
        God is REAL, unless explicitly declared INTEGER

  2. User avater
    BillHartmann | Jan 09, 2009 06:43pm | #2

    "but is he considering the drying as using combustion air? Is this correct? "

    Only if it is a gas dryer.

    Or if your dryer has and Instant Dry setting, ie less than 10 seconds. That might lead to combustion.

    .
    William the Geezer, the sequel to Billy the Kid - Shoe
  3. CramerSilkworth | Jan 09, 2009 08:52pm | #5

    I don't understand how the house is ventilated. Does the HRV supply & return only to the bathrooms, or do you supply to the bed/living areas and exhaust from bath & kitchen, all through the HRV? The tighter the house gets the more critical this issue becomes. Can the HRV be run unbalanced, ie supply more than its exhausting, if it senses a pressure drop when the dryer is running?

  4. Riversong | Jan 09, 2009 09:10pm | #6

    My inspector is insisting that I install a grill in the ceiling of my house with a pipe to the outside for make up air.  This seams odd to me as none of my appliances are using inside air for combustion air.  Only the dryer is blowing air out, but not combusting it.

    A dryer is a 200 cfm exhaust fan. Where is that volume of make-up air coming from? Is your house that leaky? Is this new construction?

    In addition, in Wisconsin, the code reads:  "If your dwelling does nto ahve any open combustion appliances, then you do not have any combustion air requirements, and by code, can rely upon infiltration through building cracks for makeup air"

    That might be adequate in a leaky house for combustion make-up air. But any new house built to IRC Energy Code standards is required to have a minimum of controlled mechanical 0.35 ACH.

    It sounds like your "air exchanger" is just a fancy bathroom exhaust fan. There should also be an outside-ducted range hood, even with an electric stove, to evacuate moisture at the source.

    In a tight house in a cold climate, moisture management becomes the dominant challenge in the heating season.

     

     
    Riversong HouseWright
    Design *  * Build *  * Renovate *  * Consult
    Solar & Super-Insulated Healthy Homes
    1. upnorthframer | Jan 09, 2009 10:19pm | #7

      My HRV is a greentek brand.  It is piped to all closets, bathrooms, kitchen, etc... and is hooked to a humidistat so it can exchange all of the air in the house when necissary.  However, there is a thrid supply duct ran specifically for my two main bathrooms and when the timers are turned on in those specific rooms, it only pulls air from those areas.  It pulls roughly 70 cfm from the bathrooms. 

      The house is brand new, 6" icynene in walls, 8" icynene in ceiling with 18" loose fill cellulose over that.  Microwave does not vent to the outside, I have an HRV vent nearby for excess moisture. 

      I just want to know if my inspector is right by saying my electric dryer is using inside air as combustion air?  Has anybody ever ran into this before?  It seems rather odd to me. 

      upnorthframer

      1. DanH | Jan 09, 2009 10:21pm | #8

        It's not combustion air, any more than the air pulled out by a range hood or bathroom fan is "combustion air". You do need a source of makeup air for it, though, as a practical matter. Doesn't need to be a hole in the ceiling, though.Like I said, I suspect that your HRV will fill that role, even when not operating.
        God is REAL, unless explicitly declared INTEGER

      2. Riversong | Jan 09, 2009 11:19pm | #9

        I just want to know if my inspector is right by saying my electric dryer is using inside air as combustion air? 

        If it's a gas dryer, then yes. 

        Riversong HouseWright

        Design *  * Build *  * Renovate *  * ConsultSolar & Super-Insulated Healthy Homes

      3. Riversong | Jan 09, 2009 11:24pm | #10

        My HRV is a greentek brand.  It is piped to all closets, bathrooms, kitchen, etc... and is hooked to a humidistat so it can exchange all of the air in the house when necissary.  However, there is a thrid supply duct ran specifically for my two main bathrooms and when the timers are turned on in those specific rooms, it only pulls air from those areas.  It pulls roughly 70 cfm from the bathrooms. 

        You're still not describing this system adequately.

        Where are the intake vents, and where are the return vents?

        70 cfm is adequate only for a small bathroom. The Home Ventilation Institute recommends intermittent bath ventilation of 8 ACH. 

        Riversong HouseWright

        Design *  * Build *  * Renovate *  * ConsultSolar & Super-Insulated Healthy Homes

  5. Clewless1 | Jan 12, 2009 04:01pm | #11

    On the surface, yes, the inspector is full of it. You're not missing anything there.

    However we are still missing a little. A HRV has two types of ports in the house ... air inlets for fresh air ... at the furnace or located in common living areas .... and outlets (exhaust) located at e.g. bathrooms or other areas that require exhaust.

    Maybe the BO is concerned that when you use the dryer the HRV is not necessarily on. But the code is what it is ... it doesn't require it. If he can explain himself well, you could make an informed decision. I suspect you should have your HRV running at least most of your waking and occupied hours, so this all may be a moot point ... hmmm I see you have it on a dehumidistat. Maybe switch to a timer? (just thinking out loud, now). Most HRVs are used w/ a timer, not a dehumidistat. The bath fan might use a dehumidistat ... you have bath fans AND a HRV? The bath fans separate from the HRV?

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding Hazardous Materials in a Fixer-Upper

Look closely at these common locations for hazardous materials in older homes.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Stud-Spacing Jig
  • Fine Homebuilding's Author Guidelines
  • Podcast Episode 693: Old-House Hazards, Building Larsen Trusses, AI in Construction
  • FHB Podcast Segment: Finding Hazardous Materials in a Fixer-Upper

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in