cutterhead | Posted in Energy, Heating & Insulation on June 18, 2006 08:18am

Just today one of the light switches in my place started acting strangely.  There are two lights wired to the switch and when the switch is turned “on” one light turns on and the other off.  When the switch is turned “off” they reverse.  So, one light is always on.  The place is just a few months old, so the wiring is obviously new too. 

Any ideas???

Reply

Replies

  1. 4Lorn1 | Jun 18, 2006 12:39pm | #1

    Sounds vaguely to me like they have wired the switch to control the neutral and the second light has a ground fault. Flipped one way the current returns through the switch. Switch off the current finds its way through he ground fault and lights the second fixture.

    Sounds like a multiple fault issue. Definitely a fault in the wiring. The details are not clear without doing some testing.

    Odds are that when you say the one fixture is off it is still getting some voltage but not enough to light the bulb enough to notice.

    New house, call the electricians back. Their fault and their problem. No need to tell them squat. If need be give the inspector a call. He or she might want to know what sort of wiring these folks are doing so their jobs can be surveyed more closely.

    People who don't know what they are doing need to stay the hell away from the electrical work. Usually it is just an inconvenience but simple electrical problems can and do cause fires and get people injured or killed.

    Get it taken care of ASAP. If all else fails call your own electrician and back charge the original contractor. Electrical problems don't normally heal themselves or get better on their own. The symptoms may go away but they always come back. Often with a vengeance.

    1. peteduffy | Jun 18, 2006 05:20pm | #2

      People who don't know what they are doing need to stay the hell away from the electrical work. Usually it is just an inconvenience but simple electrical problems can and do cause fires and get people injured or killed.

       

      You are right on there.  Not to hijack this thread, but I went to install a few cabinets for a guy, and a previous "handyman" had tapped into an outlet to add 2 outlets higher up.  I was to cover the outlet he tapped into, since it would be behind the cabinets.  I of course cut an access hole in the back of the cabinets, but in disconnecting the original outlet, I noticed that the previous hack had used 14 gauge wire connected to the original 12 gauge wire.  The new outlets he installed were 20 amp receptacles.  I checked the breaker, and yep, you guessed it, 20 amp breaker. 

      So he had 20 amp receptacles connected with 14 gauge wire to a 20 amp breaker.

      I told the homeowner that this is a problem, and what could possibly happen.

      Boy was he pi$$ed!  He called the original handyman, and chewed him a new one.  Not real happy that this hack put the homeowner, his wife, grandkids, and house in jeopardy.

      Turns out this homeowner is the wrong guy to have mad at you.  Not only is his son an attorney, but he (the son) was head of some association with 40,000 attorneys!

      I fixed it all up for him and made it safe, and he was happy.  He couldn't thank me enough for bringing it to his attention.  He said I didn't have to do that, that I could have just installed the cabinets and been on my way.  I told him I have to sleep at night.  No way would I just walk away form a problem like that.

      That's my quality control with electrical.  Can I sleep at night knowing what is there?

      Problem is, like you said, some people don't know enough to know that it is wrong, and I'm sure they sleep fine.  They should practice electrical in their own home; that way Darwin will weed them out so they don't kill any innocent people.Pete Duffy, Handyman

      1. cutterhead | Jun 18, 2006 06:33pm | #3

        Thanks guys.  I figured it was going to be a call back for the electrician but was hoping that maybe it was an obvious fix that wasn't obvious to me. 

        The problem with the area the house is in is that there's so much new housing going up that the Darwin effect doesn't weed out the lousy subs - there's more than enough work for even the bad ones. 

        1. pm22 | Jun 18, 2006 09:00pm | #4

          Another possibility is that a3 way switch was installed. 3 way switches do not have do not have "FFO" and "NO" molded in the switch lever.

          ~Peter

          Only 12 days left for the great Seattle-Tacoma earthquake

          1. 4Lorn1 | Jun 19, 2006 03:53am | #5

            Re:"Another possibility is that a3 way switch was installed."I hadn't considered the possibility of a three-way switch. With a single switch if both switch-leg cables were driopped into the box a three way would be easy for a hack to miswire. Hook the feed to the common and the switched-legs onto the other two terminals. Make up all the whites together and all the grounds together. It would function as he described.If there were two three ways and the travelers were in either light boxes with the feed it could also be screwed essentially the same way. One light hooked to each traveler in the middle and the hot feeding both switches from the middle. In this arrangement you could control either fixture alternately and have one or both on by working both switches. The one thing you couldn't do would be to turn both off. Why anyone would run the cables that way remains to be seen. There are a lot of ways you can run the cables in each case to get either situation, one switch or two, to work. Some are simpler, use less cable or wire, distribute box fill more evenly and/or are more transparent as to how to hook up later without taking notes. In each configuration of cables there is pretty much only one correct way to make connections. Problem is there are many ways of screwing it up even if the cables are run correctly. All of this speculation. It would be interesting to find out. It is hard to overestimate how bass ackwards people can do things when they don't know better and/or don't care enough to find out or, at the very least, check their work.

          2. User avater
            BillHartmann | Jun 19, 2006 06:55am | #6

            I had started to respond with a suggested of a 3-way switch, but noticed the details."Just today one of the light switches in my place started acting strangely."JUST TODAY.So unless he just installed bulbs in one of the fixtures then a 3-way switch problem would have been noticed from the begining.And I hope that he does come back with what the problem was.

          3. cutterhead | Jun 19, 2006 07:54am | #7

            Yes, that's the kicker, it just started.   I've done enough wiring to do basic stuff, but I don't know enough to diagnose this type of thing.  So, tomorrow I call the builder.  If I find out what the problem is I'll post it here.

          4. JohnSprung | Jul 08, 2006 03:06am | #11

            > It is hard to overestimate how bass ackwards people can do things when they don't know better and/or don't care ....

            Very true.  I've found some splices in our valley house where the original electrician stripped a whopping 3/16" of insulation before cramming the wires in the wire nuts. 

            Given that the OP has an original craftsmanship problem, it may be a better idea to do a whole-system tuneup than to try to troubleshoot individual defects.  Turn everything off, open all the boxes, check/tighten/replace as needed, document where things run, and what breakers they're on. 

             

            -- J.S.

             

  2. Bolts | Jun 19, 2006 12:41pm | #8

    Go and get an electrician its that simple

    You can make it fool proof but not idiot proof 

  3. HammerHarry | Jun 19, 2006 03:28pm | #9

    Are these lights hard wired, or plugged into switched outlets?

    If this started "just today", then something has changed.  If they're plugged into switched outlets, then maybe they've been plugged into the other half of the outlets, and maybe half the outlet is normally on, the other half normally off, but I can't imagine why.  It would take a 3 way switch wired creatively to do this, anyway.  Pull the switch out and look at how it's wired.  That may give you a clue.

    No matter what, you have a strange wiring problem.  First step is to find out what else is on that circuit (or circuits), and unplug / isolate them.  Something has changed, and you have to work backward to find out what.  Think, and ask everyone in the house - what did they do yesterday, that might affect that circuit.  Did someone plug in a radio in the garage?  Something has happened to cause a change.  Find the change, and you'll be close to finding the problem.

    I once lived in a house that had what seemed to be a three way on  a basement light, but it was in reality just two normal switches.  Sure, you could turn the light on from either side, but you could only turn it off by using whatever switch you turned it on with.  It took me a while to find out what the problem was, simply because when I pulled out the switch, it didn't twig that neither of them was a three way. 

    1. cutterhead | Jun 21, 2006 08:57pm | #10

      The builder spoke with my wife after looking at the problem and said it was orginally supposed to be wired with two switches for the two lights - and that the electrician had wired both into one switch.  Said it was buggered up and that he would fix it.  Doesn't explain why it would suddenly start acting the way it did months after the wiring was done.  I'm not getting a warm fuzzy here.

  4. Jer | Jul 08, 2006 05:46am | #12

    My first guess was that it was three way wired wrong, but if this just started happening...I'm not so sure.  Any way you look at it something's wired wrong and it needs to be corrected.  Good luck.

  5. DanH | Jul 08, 2006 06:55am | #13

    Yeah, demand (politely) that the builder send an electrician to fix this. Something is fairly badly messed up.

    If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Solar Shingles in Austin

A Tesla roof powers this five-bedroom Texas home and then transfers extra energy to the power grid.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Podcast 549: Energy Upgrades, Chimney Inspections, and Questions About a Home You Might Buy
  • Podcast 549: Members-only Aftershow—Patios vs. Decks
  • Podcast 548: PRO TALK With Design/Build Operations Manager Jessica Bishop-Smyser
  • Strategies for Venting a Roof Valley

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • 2023 Tool Guide
    Buy Now
  • Code Check Building 4th Edition
    Buy Now
  • 2022 Fine Homebuilding Archive
    Buy Now
  • Pretty Good House
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 314 - April/May 2023
    • 7 Options for Countertops
    • Tool Test: Wood-Boring Bits
    • Critical Details for Ductless Heat Pumps
  • Issue 313 - Feb/March 2023
    • Practical System for a Seismic Retrofit
    • Fine Homebuilding Issue #313 Online Highlights
    • Practical System for a Seismic Retrofit
  • Issue 312 - Dec 2022/Jan 2023
    • Tool Test: Cordless Tablesaws
    • Gray-Water System for a Sustainable Home
    • Insulate a Cape Roof to Avoid Ice Dams
  • Issue 311 - November 2022
    • 7 Steps to a Perfect Exterior Paint Job
    • Options for Smarter Home-Energy Tracking
    • The Fine Homebuilding Interview: James Metoyer
  • Issue 310 - October 2022
    • Choosing a Tile-Leveling System
    • Choosing Between HRVs and ERVs
    • Custom Built-in Cabinets Made Easy

Fine Homebuilding

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in