I want to make a home run line of 1/4″ pex about 70′ from the hot water to the shower. Will that flow enough to run a shower? I want the smallest line so I don’t waste too much water purging the cold from the line.
Eric
I want to make a home run line of 1/4″ pex about 70′ from the hot water to the shower. Will that flow enough to run a shower? I want the smallest line so I don’t waste too much water purging the cold from the line.
Eric
Fine Homebuilding is excited to be the official media partner of the 2024 Building Science Symposium series! This event offers builders, tradesmen, architects, designers and suppliers to discuss topics ranging…
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Get home building tips, offers, and expert advice in your inbox
Fine Homebuilding
Get home building tips, offers, and expert advice in your inbox
© 2024 Active Interest Media. All rights reserved.
Get home building tips, offers, and expert advice in your inbox
Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.
Start Your Free TrialStart your subscription today and save up to 81%
SubscribeGet complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.
Already a member? Log in
Replies
As a roll of 1/4" pex costs
As a roll of 1/4" pex costs about $20, do this:
Buy a 250' roll. Attach one end to your supplies temporarily. Connect the other end to a cheap shower setup, with a mixing valve and shower head.
Turn it on and see how it works.
BTW, I think you are thinkin of 3/8" PEX which is 1/4ID.
Code Requirement is:
That, the line deliver 3-gpm at 20-psi.
You need to determine the minimum static pressure, and do the pressure loss calcs for 3-gpm over the 70-foot run length.
A quick look at an online table shows a drop of 0.39psi/ft of length. So you would drop 27.3 psi in your 70-ft run.
Which means you would need at least 60-psi as an inlet pressure to provide a bit of a margin of safety.
Just checked the Zurn site. They are listing a pressure drop of 52.4-psi/100-ft at 3-gpm. So, that would mean a drop of 36.7-psi in 70-ft. This is for straight runs, any fittings or bends will increase the loss. They also indicate the velocity is at 9.9-fps, and some local codes are limited to 8-fps maximum.